Sub panel installed. How does it look?

poorboy87

Well-known member
Joined
Apr 13, 2014
Messages
132
Location
Southern Indiana
Got everything connected today and got power to my garage.
Just curious if my connections are ok. I don't have to have it inspected but I'd like another opinion. New wire comes in on the bottom left
It's 2-2-2-4 MHF on a 90A breaker

nadu2u3u.jpg

Main panel

ze3uqa7u.jpg


9a6ehuhe.jpg

Sub panel in the garage. I've got two ground rods outside about 6ft apart


Sent from my iPhone using Tapatalk
 
Last edited:
To avoid these ads, REGISTER NOW!

Premium08

Well-known member
Joined
Jun 6, 2014
Messages
362
Location
Littleton, NC
I dont know my code that well but I think the two ground rods should be connected together with a continuous wire, how I was taught anyway.

Sent from my SCH-I535 using Tapatalk
 
OP
P

poorboy87

Well-known member
Joined
Apr 13, 2014
Messages
132
Location
Southern Indiana
I had thought about doing that but it seemed excessive. I can still add that. Is having them both bonded to the panel not enough?


Sent from my iPhone using Tapatalk
 

CoopVA

Well-known member
Joined
Jan 20, 2014
Messages
2,144
Location
Virginia
You only needed one wire. One wire connected to both rods is the proper way to do it. The wire starts at one rod, connects to the next rod and then to the panel.


Sent from my iPad using Tapatalk
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,006
Location
Modesto, CA
Yeah if the 2 bare cu wires go to separate groud rods, then thats incorrect! It should be one continous wire from panel to the last rod.


I had thought about doing that but it seemed excessive. I can still add that. Is having them both bonded to the panel not enough?


Sent from my iPhone using Tapatalk

The reason for bonding them together is so u have one low impedance path to earth. Bonding both rods together ensures one path to earth.
 
Last edited:
OP
P

poorboy87

Well-known member
Joined
Apr 13, 2014
Messages
132
Location
Southern Indiana
Do I have to have one solid wire between the two or can I just connect the one ground rod to the other then to the panel?



Sent from my iPhone using Tapatalk
 

Premium08

Well-known member
Joined
Jun 6, 2014
Messages
362
Location
Littleton, NC
One wire from farthest rod , through second rod up to panel. No breaks or splices

Sent from my SCH-I535 using Tapatalk
 
OP
P

poorboy87

Well-known member
Joined
Apr 13, 2014
Messages
132
Location
Southern Indiana
We'll that *****... Guess I'll go buy another spool. It's cut and won't reach now.

Can I bury the cable between the two rods so it isn't sticking above ground?

Thanks for all the help!

Sent from my iPhone using Tapatalk
 
Last edited:

Premium08

Well-known member
Joined
Jun 6, 2014
Messages
362
Location
Littleton, NC
Depending on how you placed your rods in relation to the panel you should be able to use the wire from the farthest rod and loop it through the other rod then back up to the panel. Yes burry the wire

Sent from my SCH-I535 using Tapatalk
 
OP
P

poorboy87

Well-known member
Joined
Apr 13, 2014
Messages
132
Location
Southern Indiana
One cable goes up and over into the panel the other goes up the block wall and into the shop follows the wall to the panel then down and in.

I'll see if I can make it work


Sent from my iPhone using Tapatalk
 

Premium08

Well-known member
Joined
Jun 6, 2014
Messages
362
Location
Littleton, NC
If they are 6ft apart why does the wire take such a different route, just curious

Sent from my SCH-I535 using Tapatalk
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,754
Yeah if the 2 bare cu wires go to separate groud rods, then thats incorrect! It should be one continous wire from panel to the last rod.




The reason is so u have one low impedance path to earth. The goal is to have 25 ohms or less of impedance to earth.

No, if you can prove 25 Ohms of resistance or less then you need to only drive one rod.
 
OP
P

poorboy87

Well-known member
Joined
Apr 13, 2014
Messages
132
Location
Southern Indiana
I don't know. Seemed like a good way to route it.
Learning as I go

I did two ground rods just because. I don't know if I actually needed to but I did it anyway
 
Last edited:

APEowner

Well-known member
Joined
Oct 2, 2009
Messages
4,164
Location
Sunny, New Mexico
You need to check local code on the ground. In some places it's 2 rods and one continuous cable that runs from panel to rod to rod and back to the panel. The idea being that the cable can be damaged in any one spot and you'll still have a ground
 
Last edited:

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,006
Location
Modesto, CA
No, if you can prove 25 Ohms of resistance or less then you need to only drive one rod.

Yeah, i didnt word that right! I corrected it!

I don't know. Seemed like a good way to route it.
Learning as I go

I did two ground rods just because. I don't know if I actually needed to but I did it anyway

2 rods are required only if u cant show that u have 25 ohms or less of resistance to earth with one rod.

You need to check local code on the ground. In some places it's 2 rods and one continuous cable that runs from panel to rod to rod and back to the panel. The idea being that the cable Canberra damaged in any one spot and you'll still have a ground

Ive never heard of this. Must be a local requirement....
 
Last edited:

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
Can someone post the code article that requires you to use one wire to both rods and not individual wires to each rod?
 

JohnX14

Well-known member
Joined
Jun 2, 2014
Messages
557
Location
Boston 'burbs
Can someone post the code article that requires you to use one wire to both rods and not individual wires to each rod?

250.64(c)

A grounding electrode conductor can not be spliced (with exceptions) But the installation in OP is not a code violation. You can install the way he did. You can also run from panel to one ground rod. Then run a second wire from rod to rod. This is considered a bonding jumper. There are numerous publications explaining this. The Mike Holt site has some good illustrations. NEC 250.53(3)(C) discusses bonding jumpers.
 
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Ding Ding Ding.... we have a winner. This is how the NEC is written, but our local requirement is 2 rods placed on one continuous conductor.

A grounding electrode conductor can not be spliced (with exceptions) But the installation in OP is not a code violation. You can install the way he did. You can also run from panel to one ground rod. Then run a second wire from rod to rod. This is considered a bonding jumper. There are numerous publications explaining this. The Mike Holt site has some good illustrations. NEC 250.53(3)(C) discusses bonding jumpers.
 
Last edited:

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,580
Location
Fullerton, CA
If it's a detached garage, the conductors to the ground rods should be terminated to the neutral bar, not the ground bar.
 
Last edited:

JohnX14

Well-known member
Joined
Jun 2, 2014
Messages
557
Location
Boston 'burbs
Ding Ding Ding.... we have a winner. This is how the NEC is written, but our local requirement is 2 rods placed on one continuous conductor.

I neglected the local code disclaimer. Is that a state, town, or county regulation? Here in MA we do have a fair amount of front end amendments.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
It's a county thing here. At least the inspector always says "You need 2 rods on one continuous conductor". It's not worth arguing with him since it's such a minor thing.

I neglected the local code disclaimer. Is that a state, town, or county regulation? Here in MA we do have a fair amount of front end amendments.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,580
Location
Fullerton, CA
I had that backwards. I apologize for my mistake

I realized that the neutral is only supposed to be grounded in 1 location
 
Last edited:

Mech33

Well-known member
Joined
Feb 16, 2014
Messages
141
Big no no! DO NOT ATTACH THE GROUND TO THE NEUTRAL! The neutral in the sub panel must be isolated from the ground.


Sent from my iPad using Tapatalk

It looks like the neutral is currently bonded to EGC in the sub panel picture, so that should be disconnected.
 

JohnX14

Well-known member
Joined
Jun 2, 2014
Messages
557
Location
Boston 'burbs
It's a county thing here. At least the inspector always says "You need 2 rods on one continuous conductor". It's not worth arguing with him since it's such a minor thing.

I can't stand hearing that unless the inspector is correct. I agree that it's such a small detail it isn't worth arguing. I've been an electrical contractor for 25 years and an inspector for ten. As a contractor I'd do the install as the inspector wants but tell him why I disagree with his interpretation. As an inspector I'd want a contractor to tell me if he disagrees, then we can discuss.

All this is moot if there really is a local ordinance.

I just had to clear this up with one of my guys. I laid out a new service for one GEC to be installed from main disconnect to 2 ground rods. (passing through the first as it would be easier) And a second GEC to be run from the main disconnect to the copper water service. Then my other crew tried to tell the first crew it "has to be one conductor all the way from main disconnect/ through ground rods/ to water main. Just had to explain otherwise on Friday. It's a common misconception in this industry.
 

Mustang51js

Well-known member
Joined
Jan 24, 2014
Messages
1,734
Location
Haskell nj
Just noticed in your main panel you have grounds and nuetrals under the same screw,neutral has to be under it's own screw but you can put two grounds under one screw
 