I have a few questions for the electricians out there.
I have a 60' wall that has my circuit panel at the very beginning. I am wanting to put 3 Nema 6-50r on the wall. The first will be a dedicated circuit a few feet from the box. The other 2 I would like to run on a single circuit. I am using 3/4" emt. That limits me from running 2 separate circuits because of fill % since I am planning on using #6 thhn for the hots and I need to know what size ground would work for this? Should I go down to #8 and just run 2 circuits or what?
The max length of the longest run would be about 40-45'. This work will be inspected and we go by the 2012 IRC code. I've tried getting a hold of one of the inspectors but only get a voicemail and no return calls.
Thanks,
Kevin
I have a 60' wall that has my circuit panel at the very beginning. I am wanting to put 3 Nema 6-50r on the wall. The first will be a dedicated circuit a few feet from the box. The other 2 I would like to run on a single circuit. I am using 3/4" emt. That limits me from running 2 separate circuits because of fill % since I am planning on using #6 thhn for the hots and I need to know what size ground would work for this? Should I go down to #8 and just run 2 circuits or what?