Wiring for 220 size, length & ground question.

ybnormal70

Well-known member
Joined
Jan 8, 2010
Messages
931
Location
Conway, SC
I have a few questions for the electricians out there.

I have a 60' wall that has my circuit panel at the very beginning. I am wanting to put 3 Nema 6-50r on the wall. The first will be a dedicated circuit a few feet from the box. The other 2 I would like to run on a single circuit. I am using 3/4" emt. That limits me from running 2 separate circuits because of fill % since I am planning on using #6 thhn for the hots and I need to know what size ground would work for this? Should I go down to #8 and just run 2 circuits or what?

The max length of the longest run would be about 40-45'. This work will be inspected and we go by the 2012 IRC code. I've tried getting a hold of one of the inspectors but only get a voicemail and no return calls.

Thanks,

Kevin
 
To avoid these ads, REGISTER NOW!

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,596
Location
Fullerton, CA
#8 is rated for 50 amps when installed in conduit (as opposed to Romex)

If you decide to run the ground, it only needs to a #10 (up to 60 amps). The EMT is technically allowed to serve as the ground without a ground wire.
 
OP
Y

ybnormal70

Well-known member
Joined
Jan 8, 2010
Messages
931
Location
Conway, SC
Ok thanks. So I can run 4 #8 thhn hots and 1 #10 thhn ground in my 3/4" emt and only be at 31% of my max 40% fill.

Thanks,

Kevin
 
OP
Y

ybnormal70

Well-known member
Joined
Jan 8, 2010
Messages
931
Location
Conway, SC
Progress so far. I have only installed 1 220 outlet at this point.

Kevin
 

Attachments

  • Garage Outlet Installation Finished & Waiting Inspection (1).jpg
    Garage Outlet Installation Finished & Waiting Inspection (1).jpg
    100.1 KB · Views: 80
  • Garage Outlet Installation Finished & Waiting Inspection (2).jpg
    Garage Outlet Installation Finished & Waiting Inspection (2).jpg
    101.9 KB · Views: 76
  • Garage Outlet Installation (6).jpg
    Garage Outlet Installation (6).jpg
    64.8 KB · Views: 48
  • Garage Outlet Installation (28).jpg
    Garage Outlet Installation (28).jpg
    75.2 KB · Views: 54
  • Garage Outlet Installation (38).jpg
    Garage Outlet Installation (38).jpg
    85.6 KB · Views: 48
OP
Y

ybnormal70

Well-known member
Joined
Jan 8, 2010
Messages
931
Location
Conway, SC
Considering that I have never done anything like this before, I think I am doing very well. I have bent all the conduit myself and installed everything except for the fuse panel and the first outlet, 1 light and switch. Here are some of the before shots and some pics of the tools I'm using. Also a pic of my rolling wire cart that I made.

Kevin
 

Attachments

  • Garage Outlet Installation (35).jpg
    Garage Outlet Installation (35).jpg
    89.5 KB · Views: 50
  • Garage Outlet Installation (30).jpg
    Garage Outlet Installation (30).jpg
    90.9 KB · Views: 45
  • Garage Outlet Installation (29).jpg
    Garage Outlet Installation (29).jpg
    137.5 KB · Views: 51
  • Garage Wiring (13).jpg
    Garage Wiring (13).jpg
    98.8 KB · Views: 57
  • Garage Wiring (17).jpg
    Garage Wiring (17).jpg
    146 KB · Views: 58
  • Garage Wiring (14).jpg
    Garage Wiring (14).jpg
    103.1 KB · Views: 94
  • Garage Service Install (1).jpg
    Garage Service Install (1).jpg
    71.6 KB · Views: 46

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
Where is your grounding electrode conductor? This is the wire that runs to your ground rods, or a water pipe, rebar, etc.

Also, ditch the white wire on the breaker. Use black #8 instead.

I can't tell in the pics, but you need a grounding pigtail connected to the back of each of those receptacle boxes.
 
OP
Y

ybnormal70

Well-known member
Joined
Jan 8, 2010
Messages
931
Location
Conway, SC
All of the boxes have a ground attached to them. Not sure where the ground from outside goes, but it is attached to the rebar in the foundation and to 2 grounding rods. Can I leave the white and just label the ends with red tape? Or is relabeling white this way not allowed?

Anything else I should check on?

Thanks,

Kevin
 

Attachments

  • Garage Wiring (5).jpg
    Garage Wiring (5).jpg
    97.4 KB · Views: 43
  • Garage Service Install (4).jpg
    Garage Service Install (4).jpg
    114.1 KB · Views: 40
  • Garage Service Install (5).jpg
    Garage Service Install (5).jpg
    56.3 KB · Views: 48
  • Garage Service Install (6).jpg
    Garage Service Install (6).jpg
    71.7 KB · Views: 34

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,596
Location
Fullerton, CA
That's a good job. I've had 4th year apprentices that wouldn't do near that.
(The grounding jumper in the box should be #10 as well)
 
OP
Y

ybnormal70

Well-known member
Joined
Jan 8, 2010
Messages
931
Location
Conway, SC
#10 for the ground? Everything is #12 for the 20 amp circuits. Is this not correct?

Thanks,

Kevin

P.S. Thanks very much for the compliment!!!
 
To avoid these ads, REGISTER NOW!

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,596
Location
Fullerton, CA
That's correct, with the 50amp circuits, the grounds need to be #10 all the way.
With the 20amp circuits, a #12 grounding conductor is fine.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Technically with individual wires the wire should be the correct color. Labeling a white as an ungrounded conductor it allowed if part a cable such as NM.

All of the boxes have a ground attached to them. Not sure where the ground from outside goes, but it is attached to the rebar in the foundation and to 2 grounding rods. Can I leave the white and just label the ends with red tape? Or is relabeling white this way not allowed?

Anything else I should check on?

Thanks,

Kevin
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
All of the boxes have a ground attached to them. Not sure where the ground from outside goes, but it is attached to the rebar in the foundation and to 2 grounding rods. Can I leave the white and just label the ends with red tape? Or is relabeling white this way not allowed?

Anything else I should check on?

Thanks,

Kevin

The ground in your meterbase is fine. I'm used to bringing into the panel only, but it's because our power companies over here don't want any grounds in the meterbase, but it's a local thing, not an NEC code.

Also, you can't relabel that white wire. You need to use some other color besides white, gray, or green.
 
OP
Y

ybnormal70

Well-known member
Joined
Jan 8, 2010
Messages
931
Location
Conway, SC
Ok thanks. I will fix that.

Just wanted to make sure. Anyone else have any idea on the ground question I was asked earlier about the ground coming into the building? (I see Aceman just answered this).

Thanks,

Kevin
 
OP
Y

ybnormal70

Well-known member
Joined
Jan 8, 2010
Messages
931
Location
Conway, SC
I am planning on running my 220 circuit right above my 110 circuit down the wall. Is there any regulation to the spacing between the boxes from the separate circuits? Do they have to be connected, is touching ok or is there a certain distance they need to be spaced? I am planning on mounting the new boxes directly over/touching the existing boxes.

Thanks again,

Kevin
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
You can mount the boxes as close together as you want. Just remember the raised covers overhang a little bit so you probably want at least a 1/4" gap between them.
 