Anyone looking at generators need to check out Champion. Their prices are good (maybe not as good as HF) but they stock all of the parts in the US !
They sell a 3100 watt (peak, 2800 watt continuous) inverter generator at a fraction of what Honda and Yamaha sell their same size generators for.
The labels say,
Main (200 amp)
Generator (30 amp)
Pole barn (100 amp)
So can you explain how this series of breakers function ? Specifically what is the function of the breaker labeled "Main" and "Generator".
The main is the 200 amp disconnect from the pole. The generator 30 amp is what the generator is rated for. Turn the main off and generator on. Feeds the box in the house.
The Wizard must be napping, but I know where he was going...
You need an interlock on those breakers so you can not back feed to the grid. Your install is not up to code and if the power company discovers it they can (and will) disconnect you until it is corrected.
I brought this up and was told with the new breakers can not back feed. I see what you are saying. It needs to be idiot proof.
No I did not go through the building inspector.