#2/3 Romex by the foot?
kazlx
Tustin, CA
Anyone have a place to buy online? Seems most want to sell rolls. I need maybe 50-60ft. Haven't measured yet.
rockwithjason
Las Vegas
the price of buying by the foot will cost as much or more than a 100ft roll. the big box stores sell 25ft, 50ft, 100ft, and 250ft rolls.
Speedy Petey
NY State
Let's clarify. Do you really mean 2/3, or do you need 12/3 ???
12/3, just buy a roll. Less than 100' the per foot cost is outrageous.
If you do mean 2/3, try a real electrical supply house.
K
kazlx
Tustin, CA
I really do mean #2/3. It's for a 100A feed to a garage sub panel from a 200A main house panel. Supply houses want to sell a full roll which is usually around 125ft. I don't want to spend $800 on a roll that I probably need less than half of.
Speedy Petey
NY State
A supply house that will only sell full rolls of 2/3?? Wow. I can imagine how accommodating they are on everything else. They'd be out of business in a heartbeat around here.
Personally, I'd use AL #2SER and a 100A breaker (or 90A).
pattenp
Virginia - USA
Actually, 2/3 NM is carried at HD. my guess is that is or close to the max size of non-metallic sheathed cable though.
I was thinking 2 conductor, it comes up to #6. I see 3 conductor does go up to #2. Never used it so was not really aware NM came that large.
offroadsteve
Hampton, VA
That's pretty cool, Learn something new every day.
Way OT but I'm still blown away by the 0000/4 (yes that's four strands of 4/0) flexible "cord" we have at work. They use it for feeders for big portable A/C units and power distribution panels.
K
kazlx
Tustin, CA
That sounds like the plan. My buddy that's an electrician suggested the same thing.
pattenp
Virginia - USA
For your use #2 Al SER as a branch feed is to be overcurrent protected at no more than 90 amps @ 75C. I saw that Speedy said 100A breaker but that is only when the feeder is use as a service feed supplying the total load to a dwelling. Also if the #2 Al SER is run within insulation for a certain distance the amps drop to 75A @ 60C.
theoldwizard1
SE MI
I know you keep saying 100A, but if you are willing to limit your current to 60A you could use 2-2-2-4 MHF cable and save a lot of money !
You can still use a 100A sub-panel, you just have to feed it with a 60A breaker from your main.
K
kazlx
Tustin, CA
I don't want to save money....I want to make sure I have enough juice to run my equipment. I have a Powermax 85 CNC table and a Syncrowave 250 I need to run, on top of a 15hp RPC for my 3 phase stuff, not to mention the compressor and all the other small **** I have. Plus, I want to make sure I have space to add a CNC mill.
pattenp
Virginia - USA
Why do you keep saying #2 Al has to be breakered @ 60A? #2 Al is 75A @ 60C or 90A @ 75C.
pattenp
Virginia - USA