Hey guys, ready to hook up my stove, and needing some info and pics of an install in a metal building! I want to go through the roof. Thanks a lot, Jp
1e202cc722fecfdeb9cf1b344d295cd2.jpg
d8ceebf7a3243a2a66b6ad52d56c50ff.jpg



Sent from my iPhone using Tapatalk
 
To avoid these ads, REGISTER NOW!
OP
B

Bigpee733

Well-known member
Joined
Jun 17, 2013
Messages
86
And yes, the stove will be pulled out from the wall some! Lol


Sent from my iPhone using Tapatalk
 

930dreamer

Super Moderator
Staff member
Joined
Oct 7, 2009
Messages
22,954
Location
Amarillo,TX and Stinnett,TX
This is what I did;
1/2" Hardieboard for a non-combustible backing, Dura Plus brand ceiling support box with triple wall up and through my metal roof, single wall pipe from the bottom of the support box into the stove.
 

Attachments

  • 100_1280.jpg
    100_1280.jpg
    74.4 KB · Views: 162
  • 100_1289.jpg
    100_1289.jpg
    55.5 KB · Views: 165
  • 100_1309.jpg
    100_1309.jpg
    98 KB · Views: 152

Fyrme

Well-known member
Joined
Nov 28, 2012
Messages
2,231
Location
Green country, Oklahoma
I would get you a fairly thick piece of sheet metal, 3/16"-1/4" would be perfect. Take it to a metal shop and bend a 45˚ on either side and put a few inches behind the stove, and a few inches off the wall. It will greatly help radiate the heat out into the center of the shop, rather than behind and straight up. Also use a single wall flue until you get to the roof penetration, then use a minimum double wall. You didn't say how big your shop is, but those two suggestions will help get that heat where it needs to go. If your shop is very big, that little guy will need all the help it can get. Insulation on those walls will help a ton as well.
 
OP
B

Bigpee733

Well-known member
Joined
Jun 17, 2013
Messages
86
So your triple wall goes from the top of the box, all the way up to the vent cap? And also, I've seen these pipe boots that are very cheap, and are supposed to seal the roof up very well, what did you use to seal up your roof? Thanks for the info and pics!


Sent from my iPhone using Tapatalk
 
OP
B

Bigpee733

Well-known member
Joined
Jun 17, 2013
Messages
86
It's a 30x40, my dad has the same stove in his 25x30 garage, also uninsulated, and it definitely puts out some heat, but his is stick built.


Sent from my iPhone using Tapatalk
 

Fyrme

Well-known member
Joined
Nov 28, 2012
Messages
2,231
Location
Green country, Oklahoma
Another option is a short block wall behind the stove. The idea is protecting the wall, AND getting something close to the stove that will retain and radiate heat.
 
OP
B

Bigpee733

Well-known member
Joined
Jun 17, 2013
Messages
86
I like the reflector idea to bounce the heat outward!


Sent from my iPhone using Tapatalk
 

Fyrme

Well-known member
Joined
Nov 28, 2012
Messages
2,231
Location
Green country, Oklahoma
So your triple wall goes from the top of the box, all the way up to the vent cap? And also, I've seen these pipe boots that are very cheap, and are supposed to seal the roof up very well, what did you use to seal up your roof? Thanks for the info and pics!


Sent from my iPhone using Tapatalk

I hope that's not what he means. That is a waste of heat and money if so. :scared:
 
OP
B

Bigpee733

Well-known member
Joined
Jun 17, 2013
Messages
86
I hope that's not what he means. That is a waste of heat and money if so. :scared:


So how much insulated pipe do you think I would need? Just a couple feet where it goes through the boot?


Sent from my iPhone using Tapatalk
 

930dreamer

Super Moderator
Staff member
Joined
Oct 7, 2009
Messages
22,954
Location
Amarillo,TX and Stinnett,TX
So your triple wall goes from the top of the box, all the way up to the vent cap? And also, I've seen these pipe boots that are very cheap, and are supposed to seal the roof up very well, what did you use to seal up your roof? Thanks for the info and pics!


Sent from my iPhone using Tapatalk

I bought a metal roof flashing with the malleable base from Mueller's steel buildings and used a generic metal storm cover over that.
 
Last edited:

930dreamer

Super Moderator
Staff member
Joined
Oct 7, 2009
Messages
22,954
Location
Amarillo,TX and Stinnett,TX
So how much insulated pipe do you think I would need? Just a couple feet where it goes through the boot?


Sent from my iPhone using Tapatalk

Triple wall gives you a 2" minimum clearance, so enough pipe to go from the top of the support box (fits flush to the inside of the ceiling), out the roof and 2.5' above the building peak. triple wall was $125 for a 36" piece plus you will need a triple wall cap $70.
 
Last edited:
OP
B

Bigpee733

Well-known member
Joined
Jun 17, 2013
Messages
86
I bought a metal roof flashing with the malleable base from Mueller's steel buildings and used a generic metal cover over that.


Have any pics of the roof side? That sounds about like what I'm thinking of doing.


Sent from my iPhone using Tapatalk
 

930dreamer

Super Moderator
Staff member
Joined
Oct 7, 2009
Messages
22,954
Location
Amarillo,TX and Stinnett,TX
Have any pics of the roof side? That sounds about like what I'm thinking of doing.


Sent from my iPhone using Tapatalk

It was bad enough having to climb up the ladder, I forgot to get any topside pics. If I can get my Sherpa to go on the roof again I'll get some. I can jump out of a plane but I don't like heights.:willy_nil

The ceiling support box by dura vent has a built in 2" clearance to combustible already.
 
Last edited:

Fyrme

Well-known member
Joined
Nov 28, 2012
Messages
2,231
Location
Green country, Oklahoma
Any reason you have to go out the roof? Could you go out the side up by the eave or top of the wall? Roof penetrations on metal buildings scare me. Especially if you have vinyl backed insulation under the roof metal. If it leaks, you may never know it because it will just run down the vinyl til it gets to the fascia and rot it out. If no insulation, you would catch a leak.
 
OP
B

Bigpee733

Well-known member
Joined
Jun 17, 2013
Messages
86
Any reason you have to go out the roof? Could you go out the side up by the eave or top of the wall? Roof penetrations on metal buildings scare me. Especially if you have vinyl backed insulation under the roof metal. If it leaks, you may never know it because it will just run down the vinyl til it gets to the fascia and rot it out. If no insulation, you would catch a leak.


I thought about through the wall, but for one, I don't want the all the 90 degree bends in the pipe, for 2, I don't want 20 feet of pipe on the side of my building, and for 3, it seems like that's a lot of wasted heat! I don't have any insulation, so any leaks would be found pretty quick.


Sent from my iPhone using Tapatalk
 
OP
B

Bigpee733

Well-known member
Joined
Jun 17, 2013
Messages
86
Also, I don't have a ceiling in the building either, so I could probably just make some kind of support for the insulated pipe. So I would probably need about 3 sections of the insulated pipe! Jesus, there is just no good way to do this cheap is there? Lol


Sent from my iPhone using Tapatalk
 

readhead

Well-known member
Joined
Dec 8, 2012
Messages
6,177
Location
Durango, Co.
No insulation, metal roof, I think I would run the single wall through the roof. Check the code requirements because you will need to stay a good distance from the wood purlins.
Remember to run the laps down so you don't get condensation coming out of the joints.
 

Fyrme

Well-known member
Joined
Nov 28, 2012
Messages
2,231
Location
Green country, Oklahoma
I thought about through the wall, but for one, I don't want the all the 90 degree bends in the pipe, for 2, I don't want 20 feet of pipe on the side of my building, and for 3, it seems like that's a lot of wasted heat! I don't have any insulation, so any leaks would be found pretty quick.


Sent from my iPhone using Tapatalk

You didn't understand me completely. 90% of the pipe which is single wall stays in the shop. You don't exit until you get to the top of the wall. Then you have one single wall elbow, into a double wall out the wall, (no insulation or wood on the walls so you can get away with it) far enough to clear your eave, if you have one, then another elbow, piece of pipe and a cap.

I know it is more components than going straight up, but it would be cheaper I'd think.
 

Attachments

  • wood stove1.jpg
    wood stove1.jpg
    53.7 KB · Views: 114
To avoid these ads, REGISTER NOW!
OP
B

Bigpee733

Well-known member
Joined
Jun 17, 2013
Messages
86
Yeah, I guess I could go up and then exit, but my stove has a rear exit for pipe, so I'd be looking a 3 90 elbows, just seems like a lot bends, and a pain to clean!


Sent from my iPhone using Tapatalk
 

NUTTSGT

Super Moderator
Staff member
Joined
Sep 14, 2009
Messages
50,923
Location
Northern Central Ohio
Also, I don't have a ceiling in the building either, so I could probably just make some kind of support for the insulated pipe. So I would probably need about 3 sections of the insulated pipe! Jesus, there is just no good way to do this cheap is there? Lol

Use single wall black pipe until you get the ceiling, or where the ceiling will be. As long as you maintain, the correct distance from combustibles, you should be alright.

The single wall pipe will radiate heat into the shop unlike the insulated pipe.
 

Fyrme

Well-known member
Joined
Nov 28, 2012
Messages
2,231
Location
Green country, Oklahoma
Yeah, I guess I could go up and then exit, but my stove has a rear exit for pipe, so I'd be looking a 3 90 elbows, just seems like a lot bends, and a pain to clean!


Sent from my iPhone using Tapatalk

Well in that case, through the roof might be the best option. I'd start by stopping by a fireplace supply and ask them what the correct materials would be necessary to make a roof penetration and go from there. I've seen some hack jobs on roofs that look awful, probably leak, and have rust streaks running down the roof surface.

This one on the other hand.....
I'd almost be willing to poke that right through the roof on the front of my shop. Thing is **** as hell.
chimneyflash.jpg
 

Crfdell

Well-known member
Joined
Dec 22, 2012
Messages
103
Location
Cambridge Ontario Canada
Depending on where you live codes are slighlty different if the unit is not a certified appliance min clearance from combustible materials is 48" you can reduce clearances by adding a heat sheild but it must be of a correct size and have the proper spacing from the wall if you provide specifics i can give you more detail. In a shop the stove must be 18" off the floor as well as protected from accidentally being run into.

What does your insurance co require?
 
OP
B

Bigpee733

Well-known member
Joined
Jun 17, 2013
Messages
86
I've read about all the codes a what not, but I'm gonna say right now, my dad had been burning a stove in his gas and oil and brake cleaner filled garage since I was 2 (I'm 34 now) and it's too close to the wall, with no backer, and sits right on the floor, and there has never been anything close to even a close call. As for the insurance, I'm too scared to call them! Lol


Sent from my iPhone using Tapatalk
 

AnthonyJ124

Well-known member
Joined
Nov 28, 2010
Messages
674
Location
Southeast
Well, IF something ever happens you'll probably call insurance- right? They can deny claims because you had a woodstove installed out of code. BUT I don't want to be THAT GUY. It's your space, do what you're comfortable with.

As far as installation ideas, the hearth.com forums are FULL of good info/people.
 
OP
B

Bigpee733

Well-known member
Joined
Jun 17, 2013
Messages
86
Yeah, I guess that would be a bridge I'd have to "burn" when I get there! For what it's worth, I was talking to my dad, he has a wood burner in his basement as well, insurance told him, we don't want to know about it. If something was to happen, we'd pay it, and then cancel you! Im sure that happens a lot. I'd be willing to bet a lot of people that put stoves in, probably don't even realize they are supposed to let their insurance company know.


Sent from my iPhone using Tapatalk
 

kelpaso1

MEMBER EMERITUS
Joined
Sep 28, 2009
Messages
3,962
Location
New Brunswick
Yeah, I guess I could go up and then exit, but my stove has a rear exit for pipe, so I'd be looking a 3 90 elbows, just seems like a lot bends, and a pain to clean!


Sent from my iPhone using Tapatalk

You are only allowed a maximum of 2 90 degree elbows in your chimney system. The less the better. also running most of the pipe indoor creates a better draft. I don't know why stove makers make them with a rear outlet as you have to start with a 90 right off the bat:willy_nil
 

Shop Specialties

Well-known member
Joined
Mar 16, 2012
Messages
530
Location
Grass Range, MT
Selkirk Ultra-Temp.
Starting from top to bottom.
Cap
Dektite - #9 fits 8 inch Ultra Temp perfect. #8 for 6 inch Ultra Temp.
4' (or less depending on roof) Ultra Temp
RSP - Roof Support Package. 18" piece of Ultra Temp with wings. Wings rest on top of roof supporting pipe.
DSAC - Dripless Stove Pipe Adapter with Coupler.
Single wall to stove as long as you maintain 18" from combustibles.
 
OP
B

Bigpee733

Well-known member
Joined
Jun 17, 2013
Messages
86
I went out today and bought a dura vent through the ceiling kit, 14 feet of single wall stove pipe and 1 90 degree elbow for the inside of the building, and I also bought 4 ft of stainless steel insulated triple wall, for the support box up. All I need now is a boot for the roof, and I'll be good to go! Might as well do it right, but my God that stuff is high!


Sent from my iPhone using Tapatalk
 
OP
B

Bigpee733

Well-known member
Joined
Jun 17, 2013
Messages
86
Can't wait! I found a #8 silicone pipe boot on eBay, and made an offer, I'll wait and see if they accept, if not, I'll order one from pipebootexpress, but it won't be long now!


Sent from my iPhone using Tapatalk
 

NUTTSGT

Super Moderator
Staff member
Joined
Sep 14, 2009
Messages
50,923
Location
Northern Central Ohio
That's good as the snow is starting to fly.

One thing you may also want to do is add a general location to your profile. When you ask questions like this, it helps other members answer your questions properly.
 
OP
B

Bigpee733

Well-known member
Joined
Jun 17, 2013
Messages
86
That's good as the snow is starting to fly.

One thing you may also want to do is add a general location to your profile. When you ask questions like this, it helps other members answer your questions properly.


Thanks for the heads up, I got my location changed! Also, the ebay guy came back with a counter offer, but it was still too high, so I declined and ordered one from the other place last night. I'll keep everybody posted!


Sent from my iPhone using Tapatalk
 

mhoss44

Well-known member
Joined
May 23, 2014
Messages
92
Location
Morrison, Oklahoma
@930dreamer.....I am an old Paratrooper and hate climbing on roofs. Especially slick metal. Hahahaha


Sent from my iPad using Tapatalk
 

fireguy

Well-known member
Joined
May 25, 2008
Messages
530
20 years on the truck, every fire we went to, the owner was totally surprised when their woodstove caught the building on fire. Every one had a wood stove that was not installed as per code. Most were caused by lack of clearance. But, hey it is your house, so you get to burn it down if you want.
 

klogan121

Well-known member
Joined
Jan 23, 2010
Messages
113
Location
Linden, MI
20 years on the truck, every fire we went to, the owner was totally surprised when their woodstove caught the building on fire. Every one had a wood stove that was not installed as per code. Most were caused by lack of clearance. But, hey it is your house, so you get to burn it down if you want.

The guy wants to install this thing as safely as possible! That is why he is asking a lot of questions! You think he wants to burn it down?? :eek7:
 
OP
B

Bigpee733

Well-known member
Joined
Jun 17, 2013
Messages
86
Got the stove plumbed in today, I'll post some more pics tomorrow!