10 gauge wire
Mike Honcho
SE Michigan
I have 1/2 emt (i know, a little small) run for my compressor, my question is, would you run solid or stranded 10 gauge, 50 feet 270 degrees of bends. if stranded, how would i go about bonding the box that the compressor whip will come into, crimp connector?
Labradorian
Pembroke, ON
You can use either, no code restriction. It is just easier to pull stranded through the conduit.
A crimp type connector works best on stranded wire, crimping connectors wouldn't bite onto a solid wire very well. I wouldn't use crimp connectors on solid wire.
cheers
teamextreme
Lakewood, CO
I would avoid solid #10 like the plague. Pain in the *** to work with and pulling in conduit, especially 1/2", will be a high risk for knicking the wire. With 270 degrees of bends, you'll be much happier with stranded. BTW, code says you can pull 6 THHN's in a 1/2", but I can't imagine stuffing that many in there. For the 2 wires you'll need, 1/2" is fine.
cagullett1
North Texas
After recently wiring a 5kw 240V heater.... I HATE 10G solid wire. The flexibility of the stranded is necessary to run in those sharp bends.
alfredeneuman
Fullerton, CA
you can buy prefab bonding pig tails with the screws attached, then you just wire nut them together.
The bonding pigtails only have #12 wire. In this case it would need to be #10.
____________________________________________________________
#10 Solid will leave you cussing, and swearing not to make that mistake again, especially with 270° of bend.
As others have said, go with Stranded
pattenp
Virginia - USA
Why? #12 is fine as a ground on a 20A up to 60A circuit. Wrong
Edit: Ground does need to be #10. My brain was not working when I typed my reply. I'm just going to blame it on a senior moment.
600SL
Connecticut
I disagree.
Me and my wife just pulled 7 THHN #10 through about 90 ft of 3/4 EMT with over 400° of bend. It was 3/4" but there were 7 #10 stranded. I also did 7 #12 of solid in 3/4" EMT ~ 270° and 50'. I did that one dry. I did use plenty of lube. 2 #10 in 1/2" solid or stranded would be fine very very easy.
zmaxmotorsports
South of omaha
I disagree.
:eyecrazy::eyecrazy::eyecrazy::eyecrazy::eyecrazy::lol:
alfredeneuman
Fullerton, CA
Huh?
Table 250.122 Minimum Size Equipment Grounding
Conductors for Grounding Raceway and Equipment
(Amperes)
Size---------------------Copper-----Aluminum or Copper-Clad Aluminum
15-------------------------14---------------------12
20-------------------------12---------------------10
60-------------------------10---------------------8
100------------------------8----------------------6
pattenp
Virginia - USA
Huh?
(Amperes)
You're right, I had a brain block. #12 is up to 20A and #10 is up to 60A. I don't know why I said that, I knew better.
wyliesdiesels
Modesto, CA
I disagree.
U forgot an LB or pull box...cant have more than 360* worth of bends before u need a pull point...
teamextreme
Lakewood, CO
I disagree.
You disagree because you've pulled a completely different number of conductors through a completely different size conduit....uh huh. :dunno: Besides, I didn't say 2 #10's in a 1/2" would be an issue, quite the opposite, I also said 2 would be fine. And like Wylies said, 400 degrees of bends in a single pull is a code violation.
Mike Honcho
SE Michigan
Thanks guys,
as long as the crimp connectors are UL listed, they are good to go correct? theres no other nec code for these?
600SL
Connecticut
I did not forget. I had boxes every 8 ft on that run. So at most I had no more than 90° of bend before another box. I just decided to run the pull to a point over 400°. I could have pushed it another 50' and 270° to complete the job but I elected to re-feed it from the last continuous wire.
600SL
Connecticut
I gave you a comparison of two wire pulls with significantly higher fill ratios. No not exactly the same but both significantly more difficult pulls.
As far as the 360° rule, code only requires a pull box to be placed at 360° intervals. I doesn't restrict you from actually pulling under 360°.
Mike Honcho
SE Michigan
Correct. U/L listed and rated for the correct voltage and amperage....
Thanks,
any tips on wire nutting 4 of these wires together? once i have the switch, i will have pigtails from the box and the switch plus the 2 main ground wires. getting 3 in a wire nut was a pain enough, now i need to add one more.
wyliesdiesels
Modesto, CA
Thanks,
What size wire? #12? And is the j box metal or plastic? If metal and the switch is self grou ding then u can elimnate the ground pigtail to the switch.
If plastic have u ever seen these:
http://m.homedepot.com/p/Ideal-Gree...rs-92-Green-100-per-Package-30-192P/202894282
Will take max 4 #12 plus has feed through hole so u can eliminate 1 wire, keep one of the remaining 3 long and continue it onto the switch...
Your other option is crimp sleeves...I dont like those as much...I prefer the wire nuts...
http://m.homedepot.com/p/Gardner-Bender-14-8-AWG-Copper-Crimp-Connectors-50-Pack-10-311C/202520223/
Mike Honcho
SE Michigan
all 10 gauge in a metal box and this switch you recommended in the air compressor thread.
http://www.amazon.com/gp/aw/d/B002MPQ51O/ref=mp_s_a_1_1?qid=1417614330&sr=8-1
Thanks.
Banjorear
Essex Co., NJ
I just did my garage using old 10/3 armor clad wire. It was a chore getting it into the duplexes even with deep boxes.