I have 1/2 emt (i know, a little small) run for my compressor, my question is, would you run solid or stranded 10 gauge, 50 feet 270 degrees of bends. if stranded, how would i go about bonding the box that the compressor whip will come into, crimp connector?
 
To avoid these ads, REGISTER NOW!

Labradorian

Well-known member
Joined
Nov 5, 2013
Messages
315
Location
Pembroke, ON
I have 1/2 emt (i know, a little small) run for my compressor, my question is, would you run solid or stranded 10 gauge, 50 feet 270 degrees of bends. if stranded, how would i go about bonding the box that the compressor whip will come into, crimp connector?

You can use either, no code restriction. It is just easier to pull stranded through the conduit.

A crimp type connector works best on stranded wire, crimping connectors wouldn't bite onto a solid wire very well. I wouldn't use crimp connectors on solid wire.

cheers
 

teamextreme

Well-known member
Joined
Aug 10, 2013
Messages
867
Location
Lakewood, CO
I would avoid solid #10 like the plague. Pain in the *** to work with and pulling in conduit, especially 1/2", will be a high risk for knicking the wire. With 270 degrees of bends, you'll be much happier with stranded. BTW, code says you can pull 6 THHN's in a 1/2", but I can't imagine stuffing that many in there. For the 2 wires you'll need, 1/2" is fine.
 

cagullett1

Well-known member
Joined
Sep 29, 2013
Messages
2,203
Location
North Texas
After recently wiring a 5kw 240V heater.... I HATE 10G solid wire. The flexibility of the stranded is necessary to run in those sharp bends.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,580
Location
Fullerton, CA
you can buy prefab bonding pig tails with the screws attached, then you just wire nut them together.

The bonding pigtails only have #12 wire. In this case it would need to be #10.
____________________________________________________________

#10 Solid will leave you cussing, and swearing not to make that mistake again, especially with 270° of bend.
As others have said, go with Stranded
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
The bonding pigtails only have #12 wire. In this case it would need to be #10.

Why? #12 is fine as a ground on a 20A up to 60A circuit. Wrong

Edit: Ground does need to be #10. My brain was not working when I typed my reply. I'm just going to blame it on a senior moment.



*
 
Last edited:

600SL

Well-known member
Joined
Apr 26, 2012
Messages
1,794
Location
Connecticut
I would avoid solid #10 like the plague. Pain in the *** to work with and pulling in conduit, especially 1/2", will be a high risk for knicking the wire. With 270 degrees of bends, you'll be much happier with stranded. BTW, code says you can pull 6 THHN's in a 1/2", but I can't imagine stuffing that many in there. For the 2 wires you'll need, 1/2" is fine.

I disagree.

Me and my wife just pulled 7 THHN #10 through about 90 ft of 3/4 EMT with over 400° of bend. It was 3/4" but there were 7 #10 stranded. I also did 7 #12 of solid in 3/4" EMT ~ 270° and 50'. I did that one dry. I did use plenty of lube. 2 #10 in 1/2" solid or stranded would be fine very very easy.
 
Last edited:

zmaxmotorsports

Well-known member
Joined
Jan 11, 2013
Messages
11,948
Location
South of omaha
I disagree.

Me and my wife just pulled 7 THHN #10 through about 90 ft of 3/4 EMT with over 400° of bend. It was 3/4" but there were 7 #10 stranded. I also did 7 #12 of solid in 3/4" EMT ~ 270° and 50'. I did that one dry. I did use plenty of lube. 2 #10 in 1/2" solid or stranded would be fine very very easy.
:eyecrazy::eyecrazy::eyecrazy::eyecrazy::eyecrazy::lol:
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,580
Location
Fullerton, CA
Why? #12 is fine as a ground on a 20A up to 60A circuit.


Huh?

Table 250.122 Minimum Size Equipment Grounding
Conductors for Grounding Raceway and Equipment


(Amperes)
Size---------------------Copper-----Aluminum or Copper-Clad Aluminum
15-------------------------14---------------------12
20-------------------------12---------------------10
60-------------------------10---------------------8
100------------------------8----------------------6
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Huh?

Table 250.122 Minimum Size Equipment Grounding
Conductors for Grounding Raceway and Equipment


(Amperes)
Size---------------------Copper-----Aluminum or Copper-Clad Aluminum
15-------------------------14---------------------12
20-------------------------12---------------------10
60-------------------------10---------------------8
100------------------------8----------------------6

You're right, I had a brain block. #12 is up to 20A and #10 is up to 60A. I don't know why I said that, I knew better.
 
Last edited:

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,021
Location
Modesto, CA
I disagree.

Me and my wife just pulled 7 THHN #10 through about 90 ft of 3/4 EMT with over 400° of bend. It was 3/4" but there were 7 #10 stranded. I also did 7 #12 of solid in 3/4" EMT ~ 270° and 50'. I did that one dry. I did use plenty of lube. 2 #10 in 1/2" solid or stranded would be fine very very easy.

U forgot an LB or pull box...cant have more than 360* worth of bends before u need a pull point...
 
To avoid these ads, REGISTER NOW!

teamextreme

Well-known member
Joined
Aug 10, 2013
Messages
867
Location
Lakewood, CO
I disagree.

Me and my wife just pulled 7 THHN #10 through about 90 ft of 3/4 EMT with over 400° of bend. It was 3/4" but there were 7 #10 stranded. I also did 7 #12 of solid in 3/4" EMT ~ 270° and 50'. I did that one dry. I did use plenty of lube. 2 #10 in 1/2" solid or stranded would be fine very very easy.

You disagree because you've pulled a completely different number of conductors through a completely different size conduit....uh huh. :dunno: Besides, I didn't say 2 #10's in a 1/2" would be an issue, quite the opposite, I also said 2 would be fine. And like Wylies said, 400 degrees of bends in a single pull is a code violation.
 
OP
M

Mike Honcho

Well-known member
Joined
Mar 17, 2009
Messages
163
Location
SE Michigan
Thanks guys,

as long as the crimp connectors are UL listed, they are good to go correct? theres no other nec code for these?
 

600SL

Well-known member
Joined
Apr 26, 2012
Messages
1,794
Location
Connecticut
U forgot an LB or pull box...cant have more than 360* worth of bends before u need a pull point...

I did not forget. I had boxes every 8 ft on that run. So at most I had no more than 90° of bend before another box. I just decided to run the pull to a point over 400°. I could have pushed it another 50' and 270° to complete the job but I elected to re-feed it from the last continuous wire.
 

600SL

Well-known member
Joined
Apr 26, 2012
Messages
1,794
Location
Connecticut
You disagree because you've pulled a completely different number of conductors through a completely different size conduit....uh huh. :dunno: Besides, I didn't say 2 #10's in a 1/2" would be an issue, quite the opposite, I also said 2 would be fine. And like Wylies said, 400 degrees of bends in a single pull is a code violation.

I gave you a comparison of two wire pulls with significantly higher fill ratios. No not exactly the same but both significantly more difficult pulls.

As far as the 360° rule, code only requires a pull box to be placed at 360° intervals. I doesn't restrict you from actually pulling under 360°.
 
OP
M

Mike Honcho

Well-known member
Joined
Mar 17, 2009
Messages
163
Location
SE Michigan
Correct. U/L listed and rated for the correct voltage and amperage....

Thanks,

any tips on wire nutting 4 of these wires together? once i have the switch, i will have pigtails from the box and the switch plus the 2 main ground wires. getting 3 in a wire nut was a pain enough, now i need to add one more.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,021
Location
Modesto, CA
Thanks,

any tips on wire nutting 4 of these wires together? once i have the switch, i will have pigtails from the box and the switch plus the 2 main ground wires. getting 3 in a wire nut was a pain enough, now i need to add one more.

What size wire? #12? And is the j box metal or plastic? If metal and the switch is self grou ding then u can elimnate the ground pigtail to the switch.

If plastic have u ever seen these:

http://m.homedepot.com/p/Ideal-Gree...rs-92-Green-100-per-Package-30-192P/202894282

Will take max 4 #12 plus has feed through hole so u can eliminate 1 wire, keep one of the remaining 3 long and continue it onto the switch...

Your other option is crimp sleeves...I dont like those as much...I prefer the wire nuts...

http://m.homedepot.com/p/Gardner-Bender-14-8-AWG-Copper-Crimp-Connectors-50-Pack-10-311C/202520223/
 

Attachments

  • 27631d1393809444-ground-wire-question-green-wire-nut.jpg
    27631d1393809444-ground-wire-question-green-wire-nut.jpg
    3.8 KB · Views: 2
  • TSBEu.jpg
    TSBEu.jpg
    3.1 KB · Views: 84
Last edited:
OP
M

Mike Honcho

Well-known member
Joined
Mar 17, 2009
Messages
163
Location
SE Michigan
What size wire? #12? And is the j box metal or plastic? If metal and the switch is self grou ding then u can elimnate the ground pigtail to the switch.

If plastic have u ever seen these:

http://m.homedepot.com/p/Ideal-Gree...rs-92-Green-100-per-Package-30-192P/202894282

Will take max 4 #12 plus has feed through hole so u can eliminate 1 wire, keep one of the remaining 3 long and continue it onto the switch...

Your other option is crimp sleeves...I dont like those as much...I prefer the wire nuts...

http://m.homedepot.com/p/Gardner-Bender-14-8-AWG-Copper-Crimp-Connectors-50-Pack-10-311C/202520223/


all 10 gauge in a metal box and this switch you recommended in the air compressor thread.

http://www.amazon.com/gp/aw/d/B002MPQ51O/ref=mp_s_a_1_1?qid=1417614330&sr=8-1

Thanks.
 

Banjorear

Well-known member
Joined
Jul 22, 2013
Messages
1,881
Location
Essex Co., NJ
I would avoid solid #10 like the plague. Pain in the *** to work with and pulling in conduit, especially 1/2", will be a high risk for knicking the wire. With 270 degrees of bends, you'll be much happier with stranded. BTW, code says you can pull 6 THHN's in a 1/2", but I can't imagine stuffing that many in there. For the 2 wires you'll need, 1/2" is fine.


I just did my garage using old 10/3 armor clad wire. It was a chore getting it into the duplexes even with deep boxes.
 