Just because u have no rocks doesnt mean people in other areas dont. Thats bad advice to be giving because youre basing it on what u have!
No, You're thinking on that is wrong. Distance doesnt limit breaker size. He could still use a 90a breaker even over a long run. U dont lower a breaker size to compensate for distance! Instead, u increase your wire size....
At 150' and full load of 90a(which he will probably never hit) his voltage drop will be about 8.6v or 3.5%....he will be fine!
Read above...the wire youre using is max 90a ampacity in the application youre using it at...
[/b]
No, conduit makes it so much easier when needing to replace the wire. Also, Any wire used underground should be rated for wet location. Sweeps are used all the time without issue. Not using a sweep is a HORRIBLE idea

: and one that will cause ample frustration when pulling wire. It will be very hard to do so! What is your alternative idea? Im all ears!
No dont do that! Horrible idea!! Even with drainage holes water will still stay in the conduit due to condensation, etc... MHF is rated for water so u dont even need to worry about this!