electrical question
ronpurdy
Parish, NY
Hi everyone,
At work, we had some electrical work done and I wanted to know if it is OK to use a smaller neutral conductor than the hot conductor. We have a 30 amp 120 volt circuit that is wired with a 10 awg hot and a 12 awg neutral. It is a dedicated circuit for a packaging line equipment with a 21 amp max draw. Is that acceptable? They did have 5 duplex 20 amp receptacles pigtailed on to this circuit but we had them change it.
Thanks for any help!
Ron
R
ronpurdy
Parish, NY
Hi everyone,
Ron
Aceman
Eastern Oregon
No, it is not acceptable to have a #12 neutral conductor on your 30 amp circuit. You need #10. You also need a #10 ground wire, if they pulled one in the conduit.
wyliesdiesels
Modesto, CA
Hi everyone,
Ron
Wow talk about hack work. Whos doing the work? A licensed C-10?
If the circuit has outlets on it then its not dedicated.
And the 20a receptacles on a 30a breaker is another red flag. Good thing u had them change it...
Stuart in MN
Minneapolis
A reduced size neutral wire can be used in some circumstances with three phase circuits, but not on a single phase circuit.
R
ronpurdy
Parish, NY
Thanks everyone. It is a single phase circuit. They ran a 10awg neutral conductor from the receptacle and from the breaker, but its is wire-nutted to a 12awg in the middle of the circuit, between two junction boxes. There are actually two 30 amp circuits wired like this. There are the two 10awg conductors ran down from above the drop ceiling to the outlet, but connected to 12 gauge above the ceiling. It seemed strange to me, although I am not a certified electrician. I also understand that it will not be inspected. Not sure why that is.