Hi everyone,

At work, we had some electrical work done and I wanted to know if it is OK to use a smaller neutral conductor than the hot conductor. We have a 30 amp 120 volt circuit that is wired with a 10 awg hot and a 12 awg neutral. It is a dedicated circuit for a packaging line equipment with a 21 amp max draw. Is that acceptable? They did have 5 duplex 20 amp receptacles pigtailed on to this circuit but we had them change it.

Thanks for any help!

Ron
 
To avoid these ads, REGISTER NOW!
OP
R

ronpurdy

Member
Joined
Mar 31, 2015
Messages
10
Location
Parish, NY
Hi everyone,

At work, we had some electrical work done and I wanted to know if it is OK to use a smaller neutral conductor than the hot conductor. We have a 30 amp 120 volt circuit that is wired with a 10 awg hot and a 12 awg neutral. It is a dedicated circuit for a packaging line equipment with a 21 amp max draw. Is that acceptable? They did have 5 duplex 20 amp receptacles pigtailed on to this circuit but we had them change it.

Thanks for any help!

Ron
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
No, it is not acceptable to have a #12 neutral conductor on your 30 amp circuit. You need #10. You also need a #10 ground wire, if they pulled one in the conduit.
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,073
Location
Modesto, CA
Hi everyone,

At work, we had some electrical work done and I wanted to know if it is OK to use a smaller neutral conductor than the hot conductor. We have a 30 amp 120 volt circuit that is wired with a 10 awg hot and a 12 awg neutral. It is a dedicated circuit for a packaging line equipment with a 21 amp max draw. Is that acceptable? They did have 5 duplex 20 amp receptacles pigtailed on to this circuit but we had them change it.

Thanks for any help!

Ron

Wow talk about hack work. Whos doing the work? A licensed C-10?

If the circuit has outlets on it then its not dedicated.

And the 20a receptacles on a 30a breaker is another red flag. Good thing u had them change it...
 

Stuart in MN

Well-known member
Joined
Sep 8, 2005
Messages
23,179
Location
Minneapolis
A reduced size neutral wire can be used in some circumstances with three phase circuits, but not on a single phase circuit.
 
OP
R

ronpurdy

Member
Joined
Mar 31, 2015
Messages
10
Location
Parish, NY
A reduced size neutral wire can be used in some circumstances with three phase circuits, but not on a single phase circuit.

Thanks everyone. It is a single phase circuit. They ran a 10awg neutral conductor from the receptacle and from the breaker, but its is wire-nutted to a 12awg in the middle of the circuit, between two junction boxes. There are actually two 30 amp circuits wired like this. There are the two 10awg conductors ran down from above the drop ceiling to the outlet, but connected to 12 gauge above the ceiling. It seemed strange to me, although I am not a certified electrician. I also understand that it will not be inspected. Not sure why that is.
 