Absorbed Power
bczygan
DETROIT! Arsenal of Scrappers
I have a 230VAC 1PH welder with a listing of 5.4 kilowatts of absorbed power.
How does this relate to the required circuit size and breaker in amps, and wiring, both cord and circuit portions?
Bill
wyliesdiesels
Modesto, CA
What model welder?
What does the manufacturer call for?
What kind of cord and plug does the welder have?
Welder circuits are wired based on duty cycle and type of welder (transformer or motor driven)....
Without any of that info we would just be guessing...
bczygan
What model welder?
Doesn't call for anything.
#14, no plug.
HF #44568:
https://www.google.com/url?sa=t&rct=j&q=&esrc=s&source=web&cd=2&ved=0CCYQFjABahUKEwjj-uPU_-_GAhWBHR4KHbf0AG4&url=http%3A%2F%2Fpdfstream.manualsonline.com%2F5%2F52e92f38-6fd7-43cc-9fb2-92937e3fd196.pdf&ei=YjWwVePBKYG7eLfpg_AG&usg=AFQjCNH9vDv6Uasxabb6WASVSaHXC_Kg2w&sig2=xlqKXF6MRj7td3oq8kSZDQ
Transformer type, I think.
AC/DC
10%@130AC 15%@100DC
Bill
Alchymist
Central PA
To be "technically correct" absorbed power is true power in a reactive circuit as opposed to reactive power. Power factor is calculated thus:
PF = real power divided by apparent power.
sberry
Brethren, Michigan
If it has a 14 wire the breaker needs to be limited to 30A. Use a 12 or better for the circuit.
As a general rule for estimation. The supply wire should be a size larger than the cord on the appliance, there are probably some exceptions but its hard to burn the place down that way.
DSMR
=cos(theta) :)