To avoid these ads, REGISTER NOW!

Absorbed Power

bczygan

Well-known member
Joined
Nov 4, 2009
Messages
22,002
Location
DETROIT! Arsenal of Scrappers
I have a 230VAC 1PH welder with a listing of 5.4 kilowatts of absorbed power.

How does this relate to the required circuit size and breaker in amps, and wiring, both cord and circuit portions?

Bill
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,074
Location
Modesto, CA
What model welder?

What does the manufacturer call for?

What kind of cord and plug does the welder have?

Welder circuits are wired based on duty cycle and type of welder (transformer or motor driven)....

Without any of that info we would just be guessing...
 
OP
B

bczygan

Well-known member
Joined
Nov 4, 2009
Messages
22,002
Location
DETROIT! Arsenal of Scrappers
What model welder?

What does the manufacturer call for?

What kind of cord and plug does the welder have?

Welder circuits are wired based on duty cycle and type of welder (transformer or motor driven)....

Without any of that info we would just be guessing...

Doesn't call for anything.

#14, no plug.

HF #44568:

https://www.google.com/url?sa=t&rct=j&q=&esrc=s&source=web&cd=2&ved=0CCYQFjABahUKEwjj-uPU_-_GAhWBHR4KHbf0AG4&url=http%3A%2F%2Fpdfstream.manualsonline.com%2F5%2F52e92f38-6fd7-43cc-9fb2-92937e3fd196.pdf&ei=YjWwVePBKYG7eLfpg_AG&usg=AFQjCNH9vDv6Uasxabb6WASVSaHXC_Kg2w&sig2=xlqKXF6MRj7td3oq8kSZDQ

Transformer type, I think.
AC/DC
10%@130AC 15%@100DC

Bill
 
To avoid these ads, REGISTER NOW!

Alchymist

Well-known member
Joined
Mar 1, 2009
Messages
4,423
Location
Central PA
To be "technically correct" absorbed power is true power in a reactive circuit as opposed to reactive power. Power factor is calculated thus:

PF = real power divided by apparent power.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
If it has a 14 wire the breaker needs to be limited to 30A. Use a 12 or better for the circuit.
As a general rule for estimation. The supply wire should be a size larger than the cord on the appliance, there are probably some exceptions but its hard to burn the place down that way.
 
Last edited:

DSMR

Active member
Joined
May 24, 2015
Messages
42
To be "technically correct" absorbed power is true power in a reactive circuit as opposed to reactive power. Power factor is calculated thus:

PF = real power divided by apparent power.

=cos(theta) :)
 
To avoid these ads, REGISTER NOW!