air compressor whip wiring question
Bellaireroad
Fort Worth
Hello, I am wiring a ~2 foot whip from the motor to a relay on my compressor. The motor is a 5 Hp 220 rated at 29.5 amps at full load. Will 10 gauge be enough for this, or go with 8 gauge? thanks
Charles (in GA)
50 mi south of Atlanta
The difference is pennies, why even consider the lesser wire? Go with the 8 gauge, less heat loss, less chance of voltage loss and just all around better choice. The 10 gauge is probably NEC legal, but I would not do it.
wyliesdiesels
Modesto, CA
Did the compressor not come with it already wired?
What kind of compressor? Usually thats already wired up.
Id like to see what the manufacturer would use.
Technically, the wire should be 125% of NEC FLC which is 28a for 5hp.Yours is 29.5a so it should be #8 but u could probably get away with #10.
Bellaireroad
Fort Worth
Its a Heinz 57 ..started life as a snapon with chinook k30 pump and 7.5 baldor motor. Still has the chinook, now has a Leeson 5 hp 184T frame. the whole thing is getting redone, tank has been sandblasted and powder coated, pump has been honed, new rings and valves........wiring and plumbing is left
http://www.leeson.com/leeson/searchproduct.do?invoke=viewProductDetails&motorNo=131622.00&productType=0
Jlarson
10 gauge is compliant. The conductors are sized off the fla listed in the tables not the nameplate. 28x125% is 35 so 10 gauge.
TAMPAGT07
Palm Harbor, Fl
Hey OP, why did you go from a Baldor to a Leeson? I just picked up a Baldor 5hp on Ebay for $350 shipped... For this price I couldn't even get a Northern Tool 5HP Leeson....
alfredeneuman
Fullerton, CA
This is the chart used for sizing motors in the NEC
#10 would be fine.
Engineer is incorrect