air compressor whip wiring question

Bellaireroad

Well-known member
Joined
Mar 22, 2013
Messages
636
Location
Fort Worth
Hello, I am wiring a ~2 foot whip from the motor to a relay on my compressor. The motor is a 5 Hp 220 rated at 29.5 amps at full load. Will 10 gauge be enough for this, or go with 8 gauge? thanks
 
To avoid these ads, REGISTER NOW!

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
The difference is pennies, why even consider the lesser wire? Go with the 8 gauge, less heat loss, less chance of voltage loss and just all around better choice. The 10 gauge is probably NEC legal, but I would not do it.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,071
Location
Modesto, CA
Did the compressor not come with it already wired?

What kind of compressor? Usually thats already wired up.

Id like to see what the manufacturer would use.

Technically, the wire should be 125% of NEC FLC which is 28a for 5hp.Yours is 29.5a so it should be #8 but u could probably get away with #10.
 
OP
B

Bellaireroad

Well-known member
Joined
Mar 22, 2013
Messages
636
Location
Fort Worth
Did the compressor not come with it already wired?

What kind of compressor? Usually thats already wired up.

Id like to see what the manufacturer would use.

Technically, the wire should be 125% of NEC FLC which is 28a for 5hp.Yours is 29.5a so it should be #8 but u could probably get away with #10.

Its a Heinz 57 ..started life as a snapon with chinook k30 pump and 7.5 baldor motor. Still has the chinook, now has a Leeson 5 hp 184T frame. the whole thing is getting redone, tank has been sandblasted and powder coated, pump has been honed, new rings and valves........wiring and plumbing is left

http://www.leeson.com/leeson/searchproduct.do?invoke=viewProductDetails&motorNo=131622.00&productType=0
 

Jlarson

Well-known member
Joined
Mar 27, 2015
Messages
738
Location
AZ
10 gauge is compliant. The conductors are sized off the fla listed in the tables not the nameplate. 28x125% is 35 so 10 gauge.
 
To avoid these ads, REGISTER NOW!

TAMPAGT07

Well-known member
Joined
Feb 20, 2008
Messages
11,147
Location
Palm Harbor, Fl
Hey OP, why did you go from a Baldor to a Leeson? I just picked up a Baldor 5hp on Ebay for $350 shipped... For this price I couldn't even get a Northern Tool 5HP Leeson....
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,592
Location
Fullerton, CA
This is the chart used for sizing motors in the NEC

430.248.jpg


#10 would be fine.

Engineer is incorrect
 