Subpanel main breaker position
machsnell
Northern Virginia
The electrician wired my subpanel with the feeder and he put the 100 amp breaker at the top. The hot wires are in the way of the neutral bar, not too bad but enough to make wiring the neutrals difficult.
The feeder comes in from the bottom so.....can I shorten the wires and put the 100 amp breaker on the bottom slots or is that a no no and I should just deal with it?
pattenp
Virginia - USA
You can place the main breaker at the bottom. What amp is the feeder breaker in the main panel and feeder wire size?
wyliesdiesels
Modesto, CA
Yes breaker can be moved. Be sure to use the retention screw.
The cables need cable clamps where they enter the enclosure...
Not on that panel you cant.
Yes u can...
brewchief
Is that one of those panels that the buss bar is different next to the main so you can't put breakers there? If so I wouldn't move the main.
pattenp
Virginia - USA
If the bus is made only to have the main where it is then just remove the main while hooking up the neutrals. Also you can shorten the feeder an inch or so to tighten up the bend radius on the feeder a tad to get it off the neutral bar.
machsnell
Northern Virginia
I will check when. I get home.
Great and simple idea to remove the main breaker while installing neutrals. Perfect. And to shorten. Thank you pattenp.
dw1
Ky
Look at the two screws holding the metal plate that holds the bus bar assembly and MB, see if you can take those two screws out and turn the whole inside assembly 180* and reinstall if you cant move only the MB.
malibu101
Walnutport PA
You said an electrician installed this.
Without a clamp on the SE cable? Call somebody else! NOW!!
Did he use oxide inhibiting compound on the aluminum wire?
I'll assume the romex on top without a clamp is just for temporary.
machsnell
Northern Virginia
Yes the electrician said it needed a clamp. It was at the end of the day after we did the new wires from meter and changed out the panel.
I had run the 1/0 and put in sub.
When he saw he said it needed but what you can't see is that there is a 2x4 under the panel that the ser runs through. It 8s smaller than the hole in subpanel. He said not code but he wasn't worried about it because it does hold the wore firm and in the middle of the metal edges.
I was also going to clamp wire.
He did use antiox on all aluminum.
machsnell
Northern Virginia
Virginia. Can do correctly. I waited like 4 months to get this hooked up and we started this past Saturday at 10 and finished at 10 something at night with nary a break.
This was the last location we worked.
malibu101
Walnutport PA
OK. Now we understand.
It's not going to burn the place down or cause a person to be electrocuted tomorrow but you know it's not right and are going to make it proper.
That said. Looks fine as it's a basic install.
And like someone said above, see if the 2 screws holding the breaker buss interior into the box will allow it be be flipped. Since the breaker moves horizontal you can do that where I live.
EDIT- I know it's easy to say on a keyboard, but,,,,,,
It's usually always dollars and time saved to just do it right the first time.
Aceman
Eastern Oregon
I can't believe you waited 4 months for that! I hope you didn't pay professional electrician rates for something that looks like a guy off craigslist wired it.
1. No cable clamps.
2. Using an aluminum bussed panel=junk.
3. A 2x4 mounted tight to the bottom of the panel, how do you install the proper cable clamp now? Remove the 2x4? Does this electrician have any previous experience, at all?
Let me guess, no permit?
machsnell
Northern Virginia
Thanks I will look at buss bar.
I put sub panel in and then ran the ser and didn't think about clamp until after wire was in.
Asphalt guy not smart with electricity.
I don't like to redo but learned the not so hard way. I will fix.
wyliesdiesels
Modesto, CA
The other issue with 2x4 on the bottom is u cant add branch circuit wiring into the bottom of the panel now or down the road.
Do it proper- remove the block and add the clamps...