Square D QO 30/40 panel and tandem breakers

75gmck25

Well-known member
Joined
Jul 21, 2014
Messages
1,349
Location
Alexandria, VA
I have a Square D QO 30/40 200 amp panel that was installed about 3 years ago by an electrician. It was permitted and inspected as a 200 amp "heavy up" from my old 150 amp panel. I assume the box came from one of the local electrical supply stores. The panel is now full (30 circuits) after they finished our kitchen remodel, but I now want to add a double breaker to feed a garage sub-panel.

I want to move four of the existing circuits to two new tandem breakers, which will then open up two slots. Those slots will be used for a 60 amp breaker to feed the garage sub-panel.

Are there certain positions where the 10 tandem breakers can be installed, or would they work in any position? There is so much wire in the way in the box that its hard to read any of the labels on the inside of the panel itself, if the labels explain which positions are for tandem breakers. The panel cover has nothing about the location for tandem breakers.

Thanks,

Bruce
 
To avoid these ads, REGISTER NOW!

RoadBeater

Well-known member
Joined
Feb 16, 2009
Messages
442
Location
South Central, Ohio
Yup, bottom of panel. My house had a Square D HOM 30 space panel, that didn't allow for tandem breakers. Hope yours is different, had to swap mine out for a 40 space panel.
 

Gokart

Well-known member
Joined
May 22, 2010
Messages
177
It sounds like you have a QO13040M200, which accepts 10 tandem circuits.

It this is the case you should be able to install a QOTxxxx in the bottom 5 spaces.
 
To avoid these ads, REGISTER NOW!

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,596
Location
Fullerton, CA
That particular panel can be mounted either with the main breaker at the top, or at the bottom.

Depending on which way it is oriented, the tandems will fit only at the bottom or the TOP of the panel :D
 
OP
7

75gmck25

Well-known member
Joined
Jul 21, 2014
Messages
1,349
Location
Alexandria, VA
Thanks for all the feedback. There are no stickers on the bottom of the panel, but there is a large sticker on the inside of the right side (main lug is at the top).

There is a Note 5 on the sticker (with diagram) that apparently describes where the tandem breakers are, but I cannot find a "5" anywhere on the diagram. The note says:
"5. Tandem breakers may only be used in plug on spaces provided with mounting rail openings at this end of the interior."

Maybe I'll shut off the main breaker tomorrow and pull a few of the lower breakers loose to see if they have the notch in the mounting rail. Its sounds like that is the most likely setup, since the main breaker is at the top.

Thanks again.