I have two four foot flourescent light fixtures. In both of them only one bulb works.
The bulb is ok. If i switch the bulbs in the fixtures, same result.
Now if i take the cover off, there is only one ballast. Is it possible for the ballast to go half bad?
Den,
Since these are T12, I'll give you these thoughts....
There are many different kinds of T12 ballasts. Most of them are 2 lamp rapid start magnetic ballasts. These ballasts have the lamps wired in series, which is a circular circuit. This means that it's nearly impossible for one lamp to come on full brightness and the other to be out, because the dead lamp would break the circle.
Cheap "shoplights" used a different kind of ballast. You would often find that they would use 2 choke ballasts. These are smaller, cheaper, and less efficient than the other types. The key word in that sentence was "cheaper". Typical shoplights will have a choke ballast in each end of the fixture, each running one lamp. If one of them went bad, it would explain your situation.
If you have a 2 lamp magnetic ballast, there are a few connections you should check. Obviously, check the connections at the sockets at each end of the dead lamp. One end will be yellow wires, and the other end will be either red or blue wires.
The yellow wires are common to all the lamps and they jump from socket to socket to socket. You should check ALL of the yellow wire connections. You also need to check the connections at socket adjacent to the dead lamp sockets. This adjacent socket "feeds" your dead lamp sockets, so the bad connection could be there. If your dead lamp sockets have a red wire, find the nearest adjacent red wire socket and check it. If your dead lamp sockets have a blue wire, then check the nearest adjacent blue wire socket.
Good luck.
CD