I have my heaters installed, and they have been working perfectly for the past couple months. Today, I decided to wire both heaters into 1 Thermostat....... Well that proved to be a mistake.

- Issue 1: I didn't turn off the power to the heaters. 2 of the thermostat wires touched, and something happened.....

- Put both heater's thermostat wires to the 1 thermostat. Nothing works now.

- I figured I'd reverse it all and go back to 2 thermostats so I don't loose heat for the night...... well NOW NO HEATERS WORK. I have 120V to the heater, but the power light won't come on.

Do you think I fried the internal Transformer? OR?!?!?!

Heaters are Reznor VPT 125


Thanks
Chad
 
Last edited:
To avoid these ads, REGISTER NOW!

manwithtools

ALLIANCE MEMBER
Joined
Aug 24, 2015
Messages
13,968
Location
Lebanon, TN
I looked at the installation manual and I don't see any indication of fusing for the transformer so I suspect the transformer might have shorted and been damaged. If so, you will need a new transformer.

To operate two units from one thermostat I would have the first unit turn on a relay and then wire the contacts from the relay in place of the thermostat for the second unit.
 
OP
C

Cmanz28

New member
Joined
Jan 25, 2015
Messages
4
I just borrowed a Multimeter.... Transformer is fried. Time to overnight a couple!

Thanks!
 
To avoid these ads, REGISTER NOW!

manwithtools

ALLIANCE MEMBER
Joined
Aug 24, 2015
Messages
13,968
Location
Lebanon, TN
I just borrowed a Multimeter.... Transformer is fried. Time to overnight a couple!

Thanks!

Good, glad you got it solved. Two thermostats is not a bad thing, but if it was me I'd set them up in parallel if they're both in the same building / heating space. In other words if either one calls for heat have it turn both heaters on. It will require some small relays but they are not expensive. Probably a bigger hassle to run the wire between them
 
Last edited:

LS6 Tommy

Well-known member
Joined
Dec 27, 2013
Messages
26,162
Location
Northern NJ
I looked at the installation manual and I don't see any indication of fusing for the transformer so I suspect the transformer might have shorted and been damaged. If so, you will need a new transformer.

To operate two units from one thermostat I would have the first unit turn on a relay and then wire the contacts from the relay in place of the thermostat for the second unit.

This.

Can't really run two transformers on one t-stat.