I am back with two more questions that hopefully have simple answers but doing research online I don't seem to come up with a definitive answers.

1. Does code require an exterior electrical receptacle on a detached garage? I did not plan to have one but can't see anywhere that it is required.

2. I saw this quote online today...."If you were to run a neutral to one silver/white screw on the receptacle, then continue with another wire from the other silver/white screw onward to the next receptacle, you could not remove the receptacle and keep the neutral uninterrupted, a violation of the code[. Because of this, you will need to use individual GFCI receptacles at each box."

I wired my receptacles with incoming neutral on one silver screw and outgoing neutral to the other silver screw. I only have one GFCI at the beginning of each receptacle circuit then standard 15 amp TR receptacle after the GFCI. Is this O.K. or would this wiring method require a GFCI for every receptacle? In other words, if you use just one GFCI in the receptacle circuit do you have to wire nut the incoming and outgoing neutral with a single pigtail to one of the silver screws? The above quote really confuses me.
 
To avoid these ads, REGISTER NOW!

oleguy

Well-known member
Joined
Nov 22, 2009
Messages
273
only if you have a multiwire branch ckt.in other words two hots sharing one neutral.also the two hots need to be on separate legs.then the neutrals need to be pigtailed
 
Last edited:
OP
I

impalatom

Active member
Joined
Oct 27, 2015
Messages
30
Location
Iowa
Can anyone help me on question 1. Does code require an exterior electrical receptacle on a detached garage?
 

CNGsaves

Well-known member
Joined
Sep 26, 2012
Messages
13,233
Location
KS and OK
^ ^ ^ Pretty sure that GJ Sparky's have answered that question as NO for required exterior outlet on detached garage.

Still a good idea, even if not required.
 
OP
I

impalatom

Active member
Joined
Oct 27, 2015
Messages
30
Location
Iowa
^ ^ ^ Pretty sure that GJ Sparky's have answered that question as NO for required exterior outlet on detached garage.

Still a good idea, even if not required.

CNGsaves, I am sorry but I do not see a post from GJ Sparky, so I am confused as usual, but if you say a exterior outlet is not required on a detached garage that is what I need to know. Thanks
 

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
Keep in mind there will come a time when you wish you had one. About the 15th time you throw an extension cord out the window or run it under the door.
 

simpler=better

Well-known member
Joined
Oct 6, 2015
Messages
499
Location
Baltimore, Maryland
#2 is debated a lot, but it boils down to this:

It's only a problem if you work on the circuit hot (a no-no) or you uninstall the outlet and leave the wires floating around in lala land.

If you're worried, pigtail at each outlet. If you're not, don't.
 

tfi racing

Well-known member
Joined
Apr 19, 2008
Messages
2,907
Location
Cedar,BC
Keep in mind there will come a time when you wish you had one. About the 15th time you throw an extension cord out the window or run it under the door.

Why wouldn't one put an outdoor receptacle on a garage?Makes no sense not to have one.:dunno:
 

Short Round

Well-known member
Joined
Sep 13, 2014
Messages
92
Location
Upstate NY.
Why wouldn't one put an outdoor receptacle on a garage?Makes no sense not to have one.:dunno:



I plan on having them on the outside. All pretty high above snow line. One between the garage doors and another pair on at least one of the long sides of the garage.

I envision using the shop vac as much outside the door as inside the garage for cleaning vehicles. Then there is car battery chargers and all sorts of un thought of minor work outside. Maybe a small electric pressure washer, etc.
 
Last edited:

Cmreschke

Well-known member
Joined
Feb 15, 2014
Messages
775
Location
North of Detroit
Question 1=NO. Not required.
Question 2= No. Not a violation.
As stated above it is only a violation if it is a neutral on a multi wire branch circuit where the current from 1 circuit is carrying thru the receptacle.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,582
Location
Fullerton, CA
Keep in mind there will come a time when you wish you had one. About the 15th time you throw an extension cord out the window or run it under the door.


Even if it is just once it still is a Code violation (NEC 2011)

Flexible Cords and Cables
400.8 Uses Not Permitted.
(3) Where run through doorways, windows, or similar
openings
 

TractorJeff

Well-known member
Joined
Dec 8, 2013
Messages
3,309
Location
Elkhorn, WI
"Even if it is just once it still is a Code violation (NEC 2011)"
Does anyone really care if it is a Code violation?
Is the knowledge of a Code violation going to stop someone from having a party in the driveway with the stereo playing from an extension cord? Is the guy with a dead battery going to call AAA for a tow truck to jumpstart his car in his driveway because it is a Code violation to put the extension cord out the door to put a battery charger on? Is the threat of a Code violation going to stop a guys wife from hanging Christmas Decorations on the garage?
GET A LIFE!!!!!!!!!!!!!!!!!!!!!!
 
To avoid these ads, REGISTER NOW!

Wirepuller

Banned
Joined
Oct 6, 2014
Messages
305
"Even if it is just once it still is a Code violation (NEC 2011)"

Does anyone really care if it is a Code violation?

Is the knowledge of a Code violation going to stop someone from having a party in the driveway with the stereo playing from an extension cord? Is the guy with a dead battery going to call AAA for a tow truck to jumpstart his car in his driveway because it is a Code violation to put the extension cord out the door to put a battery charger on? Is the threat of a Code violation going to stop a guys wife from hanging Christmas Decorations on the garage?

GET A LIFE!!!!!!!!!!!!!!!!!!!!!!


[emoji106] There is a special place in hell for these types.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,582
Location
Fullerton, CA
"Even if it is just once it still is a Code violation (NEC 2011)"
Does anyone really care if it is a Code violation?
GET A LIFE!!!!!!!!!!!!!!!!!!!!!!


The OP may care ;) It is just information..... No need to get offended

Only a fool would knowingly violate the rules in the planning stages of the project.
:lol_hitti
 
Last edited:

Shiftless

Well-known member
Joined
Mar 9, 2014
Messages
14,553
Location
East Bay SFO
I'm at a loss as to why you wouldn't want an outlet on the outside.

I suppose if somebody was worried about vandals or pranksters an easily accessible outdoor receptacle would be a liability. I guess in that case you could put a kill switch inside.
 
OP
I

impalatom

Active member
Joined
Oct 27, 2015
Messages
30
Location
Iowa
OP here, just as a follow up to all the concern about not having an exterior outlet on my detached garage, I just don't see the need for it. This is my third detached garage that I have owned and none of them ever had an exterior outlet and it has never been a problem. Besides, I could always add one later on if I needed one. I don't plan on insulating and lining the garage for a couple of years so I have a lot of time to decide if one is needed.
 

Shiftless

Well-known member
Joined
Mar 9, 2014
Messages
14,553
Location
East Bay SFO
OP here, just as a follow up to all the concern about not having an exterior outlet on my detached garage, I just don't see the need for it. This is my third detached garage that I have owned and none of them ever had an exterior outlet and it has never been a problem. Besides, I could always add one later on if I needed one. I don't plan on insulating and lining the garage for a couple of years so I have a lot of time to decide if one is needed.

This is a good example of the fact that different guys have different needs for the different kinds and amount of work they do in and around the garage. I use my nearby garage door outlet at least once a week. impalatom has had 3 garages over the course of I'm sure many years and hasn't seen the need for a place to plug in by the garage door. To each his own! :beer:
 

Alchymist

Well-known member
Joined
Mar 1, 2009
Messages
4,423
Location
Central PA
I suppose if somebody was worried about vandals or pranksters an easily accessible outdoor receptacle would be a liability. I guess in that case you could put a kill switch inside.

Rewired part of our 3 car garage - it was pretty ratty to start with. Anyway, put a GFCI outlet on the inside wall between 2 overhead doors, and an exterior waterproof outlet on the outside, back to back. With the outside outlet fed from the inside GFCI, it's a simple matter to trip the GFCI and shut off the outside outlet as needed.
 

CNGsaves

Well-known member
Joined
Sep 26, 2012
Messages
13,233
Location
KS and OK
^ ^ ^ That's great idea Alchymist. :thumbup:

Found out hard way that my 1955 house with outdoor outlet on front porch wasn't wired so well . . . . . . tripped the breaker and all the outlets in 2 bedrooms weren't working. :sad: This took down my computer, cable modem, router, etc.

Plan to re-wire that with direct 20A circuit of it's own likely with GFCI breaker when I get new main panel in the basement.

When I get more juice to garage by trenching over with a subpanel, I'll steal your idea for garage's outdoor outlets !
 

Alchymist

Well-known member
Joined
Mar 1, 2009
Messages
4,423
Location
Central PA
^ ^ ^ That's great idea Alchymist. :thumbup:

Found out hard way that my 1955 house with outdoor outlet on front porch wasn't wired so well . . . . . . tripped the breaker and all the outlets in 2 bedrooms weren't working. :sad: This took down my computer, cable modem, router, etc.

Plan to re-wire that with direct 20A circuit of it's own likely with GFCI breaker when I get new main panel in the basement.

When I get more juice to garage by trenching over with a subpanel, I'll steal your idea for garage's outdoor outlets !

Don't have to steal it - it's free! :bounce:
 

ddawg16

Well-known member
Joined
Jul 11, 2008
Messages
21,005
Location
S. California
Rewired part of our 3 car garage - it was pretty ratty to start with. Anyway, put a GFCI outlet on the inside wall between 2 overhead doors, and an exterior waterproof outlet on the outside, back to back. With the outside outlet fed from the inside GFCI, it's a simple matter to trip the GFCI and shut off the outside outlet as needed.

That is more or less how mine are done.

Everything in the garage (except lights) are on GFCI's. The outside outlet is pigtailed off one of the inside outlets.

I use that outside one all the time.

And I've never had an issue with anyone stealing my electrical....I don't have those kind of neighbors.
 