277 volt lighting

realvc

Well-known member
Joined
Jan 7, 2011
Messages
394
Location
Lake Norrell, AR
My shop was built with 277 volt, 8 foot, T12 two lamp flouescent fixtures.

There are eighteen fixtures in this 30' x 60' building.

When I moved in I found a stack of these new in the box fixtures and have been replacing the ballast as needed from the stack.

Recently two of the fixtures would only light on one lamp and when I switch the lamps around it still will only burn on the one side so I've replaced the whole fixture using the new ones.

Two other fixtures will light on one lamp and after a time the other will come on.

The lights are wired up 240 volt and seem to work O.K.

I've been here almost 10 years and have gone through around 6 ballasts and 28 lamps plus replace the two complete fixtures.

I've priced new T8 fixtures and lamps would run around $1000.00

I'm trying to decide if I should just rock on with what I got or bite the buttlet and switch everything out to the T8's.

I had planned on doing this before I retired and now that I am retired the $1000.00 looks a whole lot larger than it did.

Thanks in advance for your help.
 
Last edited:
To avoid these ads, REGISTER NOW!

astroracer

Well-known member
Joined
Jun 22, 2005
Messages
3,001
Location
Mid_Michigan
I think biting the "buttlet" would be frowned upon in some circles... :)

How much money have you spent on the "repairs"? It sounds like the only thing it is costing you is time... I would just keep on doing what you are doing if the cost is nothing but time... :)
Mark
 

rockwithjason

Well-known member
Joined
Jan 8, 2006
Messages
2,633
Location
Las Vegas
you may look at replacing the tubes with ballast bypass led units. it's a little more front end cost but you are eliminating a point of failure, reducing energy costs and you may not need as many units because the output is higher.
 
OP
R

realvc

Well-known member
Joined
Jan 7, 2011
Messages
394
Location
Lake Norrell, AR
I think biting the "buttlet" would be frowned upon in some circles... :)

How much money have you spent on the "repairs"? It sounds like the only thing it is costing you is time... I would just keep on doing what you are doing if the cost is nothing but time... :)
Mark

Thanks, all it has cost so far is just my time and the cost of the replacement lamps.
 
OP
R

realvc

Well-known member
Joined
Jan 7, 2011
Messages
394
Location
Lake Norrell, AR
you may look at replacing the tubes with ballast bypass led units. it's a little more front end cost but you are eliminating a point of failure, reducing energy costs and you may not need as many units because the output is higher.

Thanks, I'll check into this.
 

cybrdyke

Well-known member
Joined
Sep 9, 2014
Messages
3,447
Location
USA
Depending on how old the ballasts are....back in the day, ballasts were voltage-specific, but they were also battleships. You could connect a 277v ballast to a 240v supply and it would probably fire the lamps. But, it's not correct. And ballasts back then had no "brains" so they couldn't correct it for you. You're probably not getting optimal performance from the lights, nor are you getting maximum life cycles.
On the other hand, the replacement stuff is free.....
To rewire to 4' T8's :
18 tandem kits with 4 lamp ballasts will cost you about $450. 72 lamps will cost you another $150 - (ish). Plus your time to re-wire them.
Good luck.
CD
 

LS6 Tommy

Well-known member
Joined
Dec 27, 2013
Messages
26,162
Location
Northern NJ
Cybrdyke beat me to it. You're killing the 277 ballasts running them on 240...

Tommy
 
Last edited:

LS6 Tommy

Well-known member
Joined
Dec 27, 2013
Messages
26,162
Location
Northern NJ
I agree, but that is what was here when I came on the scene.

Well, if you have the spares and you're OK with the shortened lifespan, I guess it's no biggie. Biggest concern would be if the switches aren't double pole...

Tommy
 
OP
R

realvc

Well-known member
Joined
Jan 7, 2011
Messages
394
Location
Lake Norrell, AR
Depending on how old the ballasts are....back in the day, ballasts were voltage-specific, but they were also battleships. You could connect a 277v ballast to a 240v supply and it would probably fire the lamps. But, it's not correct. And ballasts back then had no "brains" so they couldn't correct it for you. You're probably not getting optimal performance from the lights, nor are you getting maximum life cycles.
On the other hand, the replacement stuff is free.....
To rewire to 4' T8's :
18 tandem kits with 4 lamp ballasts will cost you about $450. 72 lamps will cost you another $150 - (ish). Plus your time to re-wire them.
Good luck.
CD

You get a better price than I was quoted. It came out like right at $50.00 a fixture including lamps so that would be $900.00 before taxes.

The only thing I've had to buy so far has been the lamps.

I also lowered all the fixtures from off the ceiling rafters. That brought them down from about 14 foot to about 8 foot. I've also installed three additional fixtures bringing to total to 18. The light is way better and way easier to change lamps, ballasts or whole fixtures.
 
OP
R

realvc

Well-known member
Joined
Jan 7, 2011
Messages
394
Location
Lake Norrell, AR
Well, if you have the spares and you're OK with the shortened lifespan, I guess it's no biggie. Biggest concern would be if the switches aren't double pole...

Tommy

The electrician that has been instructing me checks everything I do and he O.K.ed the switches and all the changes so far.

I do all the work the way he instructs me and then he comes back by to see if I've done it all like he told me.
 

reader2580

Well-known member
Joined
Dec 31, 2014
Messages
14,545
Location
Minneapolis, MN
You could buy ballast bypass LED tubes and just rewire with 120 volts direct to the tubes. You don't need the 277 volt ballasts then. I have seen the LED tubes for $11 each.
 
To avoid these ads, REGISTER NOW!

Wes J

Well-known member
Joined
Mar 13, 2016
Messages
457
Location
Peoria, IL
FYI, 277 volts is used for commercial buildings with 480 volt 3 phase service. In 480 Y configuration, each phase to neutral is 277 volts. They can run these light fixtures at 277 volts single phase with no need for a transformer.
 
OP
R

realvc

Well-known member
Joined
Jan 7, 2011
Messages
394
Location
Lake Norrell, AR
Code does NOT permit anything but 120v lighting in a residential setting.

U should change it all to 120v...

Yes I agree. It's a work in progress and since no permits or inspections are required everyone does what ever they want.

Our home has been brought up to code on the electrical and plumbing but my shop is a work in progress.

We live in a rural community around a lake with all kinds of homes built over the years by the owners.



277v and above is NOT a DIY voltage!

The 277v lights are wired up 240v
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,020
Location
Modesto, CA
U screwed up the quote...

The lights need to be changed to 120v operation. They cannot be ran on 240v 277v or any voltage other than 120v to be code compliant...
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,756
The 277v lights are wired up 240v


Does not matter, residential is limited to 120V maximum, somebody got a deal on worthless 277V fixtures & they were hacked in, because 277V was not available.

Years ago was at a auction of a electrical contractor retiring, folks were snapping up new 8 foot, 2-lamp 277V strips for $10 each, was laughing the whole time while that lot was up for bid. :bounce:

Convert them or replace them, as it is there is a mess.
 
OP
R

realvc

Well-known member
Joined
Jan 7, 2011
Messages
394
Location
Lake Norrell, AR
Does not matter, residential is limited to 120V maximum, somebody got a deal on worthless 277V fixtures & they were hacked in, because 277V was not available.

Years ago was at a auction of a electrical contractor retiring, folks were snapping up new 8 foot, 2-lamp 277V strips for $10 each, was laughing the whole time while that lot was up for bid. :bounce:

Convert them or replace them, as it is, there is a mess.

That is what I figure happened here.

It is not near the mess today as it was when I started. The lights are the last of electrical that I'm redoing.
 
OP
R

realvc

Well-known member
Joined
Jan 7, 2011
Messages
394
Location
Lake Norrell, AR
I've decided to change out all the lighting to the T8, 110 volt units.

The wiring and the lighting has bugged me from the beginning. Like I said before everything has been redone now except the lights and the only reason I stopped is that we had the house remodeled but now that is done I can get back on track with the shop updates.:thumbup:

Thanks for all your replies you have helped me decide to go for the big to me lighting change out.
It is the right and best thing to do even though it is gonna cost me some of that hard to come by money.

I'll have a bunch of the 277v fixtures and lamps to get rid of if any one needs them you can get a real good deal.:D

Thanks again
Vince
 

G_P

Well-known member
Joined
Jul 11, 2010
Messages
7,135
Location
Central CT
Look on Craigslist. The 277v only stuff usually goes for pennies or is given away since there is little demand for it. Multi voltage lighting is more pricey since it can be used at home.

You can probably pick up a whole load of 277v fixtures from a building that upgraded to LED.
 

doctorsouse

Member
Joined
May 4, 2016
Messages
19
Location
Northeastern CT
Out of curiosity, what is the cost of the T8 fixtures you are looking into? I only ask because I wonder in your case how much extra it would cost for you to upgrade to LED fixtures.
 
OP
R

realvc

Well-known member
Joined
Jan 7, 2011
Messages
394
Location
Lake Norrell, AR
Out of curiosity, what is the cost of the T8 fixtures you are looking into? I only ask because I wonder in your case how much extra it would cost for you to upgrade to LED fixtures.

The cost of the T8 fixtures comes to about $50.00 each including lamps.

I'll need 18 so it is real close to $900.00 total before taxes.
 
OP
R

realvc

Well-known member
Joined
Jan 7, 2011
Messages
394
Location
Lake Norrell, AR
I picked up seven of the T8 4 lamp fixtures yesterday and was able to get 6 of them hung.
The other 11 were picked up this morning.

The electrical supply house even honored the quote from Sept of 15 and the gave me a better deal on the lamps since they had gone down in price.

What a huge improvement they are making. :rocker:

Now to get the rest of them hung.
 
OP
R

realvc

Well-known member
Joined
Jan 7, 2011
Messages
394
Location
Lake Norrell, AR
Got all the fixtures switched out to the T8 and wired for 120.

I had lowered all the old 277 volt lights down to 9 foot to get better lighting.
The new T8 lights are so much brighter I had to raise them up to cut out the glare.

Should have done this long ago. The old lights were a problem form the get go.
I never had all of them working at the same time for very long.

I now have light everywhere.

The only thing is that my fm radio does not like the new lights. But I have overcome that moving the external antenna. I may even go to an outside antenna later on.
For now I'm enjoying the lights and the sound.
 