250. 148a refers you back to 110. They are not listed differently. Splicing is splicing. The wirenut or crimp sleeve or wagon or split bolt if you want does not have to be listed for grounding.
Equipment grounding conductors must be spliced together with a device listed for the purpose [110.14(B) and 250.148(A). Listed is the key word. If the wire connector you used is Listed for UL 467 prove it to the inspector.When an installer uses something the inspector knows nothing about and is unfamiliar, the burden of compliance now is on the INSTALLER and NOT the inspector.
They didn't give me any paper, just told me to call back after I fixed it for a reinspection of the electrical.
LOL. Sounds like a real professional inspection agency there....
Wire nuts are without question, 100% compliant for tying grounds together. Call the agency and ask for the lead inspector and ask what code you violated.
And, don't pay any reinspection fees!
A Splice Coming Apart Is Due To Poor workmanship and no wirenut is going to prevent that. Some crimps won't prevent poor work.
Just go down to the office and have his boss explain to you what is required.I agree with this.
Call the agency and ask them to tell you what code you violated. Don't question them about why the inspector failed your grounds, or that you think the way you did it is to code and you think that you are the one that is right.
Just ask them to tell you the code that has been violated, and then check for yourself to see if it is really a violation or not.
If you do it that way, it makes you look like you want to learn from them. If on the other hand, the code they quote you does not prohibit the use of regular wire nuts to make your grounds, call them back and say that you can not find anywhere in the code they provided you where it says you can't do what you did.
You want them to show you, in writing, why they failed you and not just tell you they think you are wrong. If they can't do that, then you will have some recourse in not changing what you have done if you can show them that nowhere in the code they gave you says what you did is a violation.
I know it sounds stupid, but if these are the people who you will have to deal with in the future for other inspections, if you piss them off now, they will find every little stupid thing that might possibly be a violation and make you change all kinds of stuff just to piss you off instead.
Jim
.
I know it sounds stupid, but if these are the people who you will have to deal with in the future for other inspections, if you piss them off now, they will find every little stupid thing that might possibly be a violation and make you change all kinds of stuff just to piss you off instead.
Jim
Here's an example of what he claimed was a violation - https://goo.gl/photos/H25p8ZZFv2htQXLHA (GFCI using Line in and Load terminal to add 2nd outlet) and https://goo.gl/photos/4UfiXjk6GXmfb4Tt8 (two separate circuits)
These are the wire nuts - https://goo.gl/photos/cpE4oZWxkudnWSfDA and https://goo.gl/photos/WkzxzQzhUDGgKuDF9 and https://goo.gl/photos/2kD4aqFLvy5VJXsJ8
I'm going to give them a call on Monday and ask for some clarification.
Wires look short to me anyway,Is that a gfi feeding a decorator recept next to it?
Not trying to derail here, but is twisting my grounds together with no wire nuts not an acceptable practice according to code?

Not trying to derail here, but is twisting my grounds together with no wire nuts not an acceptable practice according to code?
If you twisted then soldered it would actually be OK

Nope
It is around here anyway,its considered a mechanical connection as long as theyre twisted 1st before soldering.
I usually wrap the end with tape though.![]()


It doesnt take much time when youve done it that way since the early 70s,its all about practice.You would never see that done in a production environment. The amount of time and materials to first twist, solder, than apply electrical tape over the joint?!?!
Versus twist with linesman's pliers - then affix the wire nut / marrette, done.![]()
If circuit conductors are spliced or terminated on devices or equipment in a box, any equipment grounding conductors installed with the circuit are required to be connected to the box by listed devices. Such devices for attaching an equipment grounding conductor to a box include listed grounding screws, listed grounding clips, and other listed devices. Grounding connections are not permitted to be solely dependent on solder.

NO! Do NOT do that.Do what he wants and call it a day. If you call him on his knowledge it may go bad for you in the future inspections.
JMOTake a piece of 1/2" plywood 2ft. x2 ft. square and screw four or five plastic wall boxes on it like you are using at home where the inspector failed your work. ...
Put some 12-2 NMG in them and make all the grounds up in the boxes .....using all the different ways that have been posted on here and take it to the inspector's office. Make him pick the grounds connection that he wants you to do. You get your answer and he knows that you don't just roll over.JMO
Take a piece of 1/2" plywood 2ft. x2 ft. square and screw four or five plastic wall boxes on it like you are using at home where the inspector failed your work. ...
Put some 12-2 NMG in them and make all the grounds up in the boxes .....using all the different ways that have been posted on here and take it to the inspector's office. Make him pick the grounds connection that he wants you to do. You get your answer and he knows that you don't just roll over.JMO







Did you notice the twist first part? I also do the rest of the wires in the box the same way,wrap them with super 33/then rubber then super 33 again.
Ive only had 1 inspector complain about it,but he was a young kid who didnt even have a journeymans license but the city of cb saw fit to make a residential inspector out of him.
So anyway the chief inspector told him it was fine.![]()
Take a piece of 1/2" plywood 2ft. x2 ft. square and screw four or five plastic wall boxes on it like you are using at home where the inspector failed your work. ...
Put some 12-2 NMG in them and make all the grounds up in the boxes .....using all the different ways that have been posted on here and take it to the inspector's office. Make him pick the grounds connection that he wants you to do. You get your answer and he knows that you don't just roll over.JMO