Re-wire/re-motor band saw

G-ManBart

Well-known member
Joined
Jan 24, 2015
Messages
2,059
Location
Michigan
Hey all, I'm getting ready to attempt my first re-motor project and thought it would be smart to get a little expert advice before I start. I'll say up front that I'm no electrician, but I'm familiar enough with Ohm's law to keep from hurting myself :D

I bought a clean Wells horizontal bandsaw that was set up for 3-phase power. I have the correct single-phase replacement motor ready to install, and it currently has the leads set for 240V service. The motor shows a max of 4.4A current draw at 240V.

Since the saw was three-phase it has a magnetic starter switch, which shouldn't be necessary for single-phase, correct? The saw also has an automatic shutoff switch wired to the start/stop control box.

What I was thinking of doing was essentially bypassing the current wiring setup, adding a service disconnect with midget 5amp fuses, and then running a simple heavy duty on/off switch....essentially leave all the old stuff in place other than the wires to the motor and the automatic shutoff relay (guessing it's a relay, but I haven't taken it apart to look).

Am I missing anything obvious, or is this a dumb plan?


I've heard/read that some folks have retained the original wiring and used it to power the replacement single-phase motor, but that seems overly complicated for no reason (unless I'm missing something). This page covers a magnetic starter to a single-phase motor:
http://wiki.vintagemachinery.org/motor starter wiring diagrams.ashx

I'll post a couple of pictures of the current setup for reference.





 
Last edited:
To avoid these ads, REGISTER NOW!

jakemac

Well-known member
Joined
May 21, 2013
Messages
9,035
Location
New England
Can't help with the wiring, but I'm pretty sure that you'll be blowing fuses if you limit yourself to 5a. The 4.4a rating is for the run draw. It doesn't take into account the amps drawn at startup. You might want to use 7 or 10 amp fuses.
 

bmwrd0

Well-known member
Joined
Nov 7, 2010
Messages
5,488
Location
Beaver Fever Oregon
Can't help with the wiring, but I'm pretty sure that you'll be blowing fuses if you limit yourself to 5a. The 4.4a rating is for the run draw. It doesn't take into account the amps drawn at startup. You might want to use 7 or 10 amp fuses.


Yeah, you need to have an idea of LRA before sizing a fuse, its not something I would go to a slow blow fuse on. Certainly no need for a mag starter.

How much HP are you talking?
 

bmwrd0

Well-known member
Joined
Nov 7, 2010
Messages
5,488
Location
Beaver Fever Oregon
Starting Amps are listed (for that motor) as 24.7 under the performance tab. So, the fuse needs to be sized for that AT STARTUP. With just 3/4hp, I would just run it at 115v probably with a slow blow (I was thinking a bigger moter cause 240v) through a common motor starter switch. That way, you can run it off a regular plug if you need to move it around. They list it as 8.4 at 115v, so a 10a slow blow should do it. This should do for a switch: http://www.amazon.com/dp/B00CONEYIA/?tag=atomicindus08-20

But I haven't delt with this since trade school, and would defer to others. Also, call Baldor and get a recomend from them.
 

454ragtop

Well-known member
Joined
Mar 24, 2008
Messages
5,011
Location
Carver, MA
Starting Amps are listed (for that motor) as 24.7 under the performance tab. So, the fuse needs to be sized for that AT STARTUP. With just 3/4hp, I would just run it at 115v probably with a slow blow (I was thinking a bigger moter cause 240v) through a common motor starter switch. That way, you can run it off a regular plug if you need to move it around. They list it as 8.4 at 115v, so a 10a slow blow should do it. This should do for a switch: http://www.amazon.com/dp/B00CONEYIA/?tag=atomicindus08-20

But I haven't delt with this since trade school, and would defer to others. Also, call Baldor and get a recomend from them.

X2, I'd run it on 115 volt as well. If you're going to be the only one running it, I'd just run it off a good quality switch, that's what I do on my own saw. If you'd rather have a protective switch like linked to above, I probably have one in my stash I'd sell a lot more reasonably.
Jim
 
OP
G

G-ManBart

Well-known member
Joined
Jan 24, 2015
Messages
2,059
Location
Michigan
Starting Amps are listed (for that motor) as 24.7 under the performance tab. So, the fuse needs to be sized for that AT STARTUP. With just 3/4hp, I would just run it at 115v probably with a slow blow (I was thinking a bigger moter cause 240v) through a common motor starter switch. That way, you can run it off a regular plug if you need to move it around. They list it as 8.4 at 115v, so a 10a slow blow should do it. This should do for a switch: http://www.amazon.com/dp/B00CONEYIA/?tag=atomicindus08-20

But I haven't delt with this since trade school, and would defer to others. Also, call Baldor and get a recomend from them.

Thanks...I looked at the performance tab and totally missed the starting amperage.

I think running it 115 makes a lot of sense, and it's easy enough to change the pre-wired configuration.
 
OP
G

G-ManBart

Well-known member
Joined
Jan 24, 2015
Messages
2,059
Location
Michigan
X2, I'd run it on 115 volt as well. If you're going to be the only one running it, I'd just run it off a good quality switch, that's what I do on my own saw. If you'd rather have a protective switch like linked to above, I probably have one in my stash I'd sell a lot more reasonably.
Jim

I'll be the only one using it, so that part makes things easier. I was thinking maybe a protective might be a bit of overkill, but figured it was worth asking the question.
 

foghorn1966

Well-known member
Joined
Aug 18, 2012
Messages
228
Location
N. Alberta
Myself, looking at your starter pic. I would leave your motor wired for 240V, change the primary taps on the control transformer to 240/250 Volts, and buy two properly sized overload heaters for your starter. You would only use two phases on the contactor. Your existing control switches should work fine.
 
Last edited:
OP
G

G-ManBart

Well-known member
Joined
Jan 24, 2015
Messages
2,059
Location
Michigan
Myself, looking at your starter pic. I would leave your motor wired for 240V, change the primary taps on the control transformer to 240/250 Volts, and buy two properly sized overload heaters for your starter. You would only use two phases on the contactor. Your existing control switches should work fine.

Okay, I think I'm tracking with you, but just to be sure, I've got a couple of questions.

First, going off the markings on the control transformer all I would need to do would be to jumper H2 to H4, right? That way H2 and H4 would look the same as H1 and H3 do now?

Does it matter which phase/leg I leave off of the contactor? I'm guessing just leave off L3, but I'd rather not guess :)
 
To avoid these ads, REGISTER NOW!

ddawg16

Well-known member
Joined
Jul 11, 2008
Messages
21,005
Location
S. California
Can you post a pic of the motor name plate?

I'm inclined to agree with going the 120Vac route. Just assume it's going to be running off one of your 20A wall ckts. There should be enough time delay in your breaker for it to start up. No extra fusing needed.

I'd pull the contactor and transformer and sell them on Ebay.
 

Doug Arthurs

Well-known member
Joined
Dec 1, 2012
Messages
1,137
Location
Ontario
I would use the original wiring and as mentioned set the transformer to 240v and run the motor from 240v. This leaves all the controls as original. You will have a blade that stops at the end of the cut and a safe magnetic motor starter. Plus you won't have to replace anything except for fuses and the overload heater.
 
OP
G

G-ManBart

Well-known member
Joined
Jan 24, 2015
Messages
2,059
Location
Michigan
I would use the original wiring and as mentioned set the transformer to 240v and run the motor from 240v. This leaves all the controls as original. You will have a blade that stops at the end of the cut and a safe magnetic motor starter. Plus you won't have to replace anything except for fuses and the overload heater.

Does it matter which leg gets left off?
 

foghorn1966

Well-known member
Joined
Aug 18, 2012
Messages
228
Location
N. Alberta
It looks like the control transformer is wired for 240V input right now & the primary is on L1 & L2. So leave L3 off. Remove the fuse on the secondary on the control transformer & measure the voltage across the open fuse holder. If you get aprox 120 V you are good to go once you replace the fuse. Post back the voltage reading.
 
Last edited:

foghorn1966

Well-known member
Joined
Aug 18, 2012
Messages
228
Location
N. Alberta
Also check the full load amps at 240 V on your motor nameplate along with the service factor number. Then consult the chart on the inside of the electrical cabinet door. I suspect even the overload heaters will be close to the required size. You might have to wire it up like the diagram in your original vintage machinery link if that overload block needs to sense current in the three legs. ( I forgot about that possibility.)
 
Last edited:
OP
G

G-ManBart

Well-known member
Joined
Jan 24, 2015
Messages
2,059
Location
Michigan
It looks like the control transformer is wired for 240V input right now & the primary is on L1 & L2. So leave L3 off. Remove the fuse on the secondary on the control transformer & measure the voltage across the open fuse holder. If you get aprox 120 V you are good to go once you replace the fuse. Post back the voltage reading.

You were right....got 126V across the open fuse holder which is what I routinely see in my barn and house (off the same transformer). At that point I wired the motor according to the diagram and it works like a charm! I still have to check the heaters, but that's an easy fix if they need to be swapped out. I made one test cut on a piece of 2.5" angle and it ran smooth, and the motor didn't even get warm. The switches all work and the automatic cutoff functions properly, so that's a bonus.

I tried to make a quick video, but had technical difficulties....pushed the button at the wrong time! I'll redo that just because everybody loves videos.

You guys ROCK! :bowdown:
 