I want to run (9) 8' T5HO fixtures (216w each). Will my 14awg, 15-amp circuit handle this load? I asked the electrician to run all 20 amp circuits in my shop, and discovered today that I have one, 15-amp circuit dedicated to my light circuit.
what is the ballast current rating? you dont go off the light bulb wattage but the ballast current
Thank you...what I figured. I have it switched on 3 switches, 3 banks of 3 lights each, but he only ran 1 home run, 14awg.
Thank you all. Just got off the phone with Lithonia regarding the ballast current...it is 2.1 amps per fixture. These are the 4-bulb, 8' T5HO fixtures available through Home Depot.
Man, I'm not happy about the wiring. Really ticks me off. I installed a 42 space, 200 amp panel, and he pulls only one 14-2 for ceiling lighting. Insulation and drywall are done.
What about running them 240v? The fixtures have a multi-volt ballast.
Those who were curious about shop size: 40x30 with 14' ceilings
Man, I'm not happy about the wiring. Really ticks me off. I installed a 42 space, 200 amp panel, and he pulls only one 14-2 for ceiling lighting. Insulation and drywall are done.
I have it switched on 3 switches, 3 banks of 3 lights each, but he only ran 1 home run, 14awg.
I did like the other person said I have mine on 240v, and split into two groups so if I do not need them all at once I have the option. In my auto shop I split them in to three areas, in that part I used 22 400w HID.