Hard wire or receptacles for ceiling lights?
mikhett
jackson nj
In my 32x32 what's the preferred method for wiring ceiling lights?Receptacles or junction boxes?This is a pole barn.
Thumper68
Duluth MN
Hardwiring. If you use outlets they need GFCI protection.
Can you quote this from the NEC?
My inspector said that if you could not reach them from the ground then no GFCI needed.
OP I prefer a mix of both, most of the lights in my shop are plugged into switches outlets, makes changes easier, of course most of my lights are hanging as well so to hard wire them I would have had to run BX to them.
alfredeneuman
Fullerton, CA
210.8
Personnel. Ground-fault circuit-interruption for personnel shall be provided as required in 210.8(A) through (C). The ground-fault circuit-interrupter shall be installed in a readily accessible location
(A) Dwelling Units. All 125-volt, single-phase, 15- and 20- ampere receptacles installed in the locations specified in 210.8(A)(1) through (8) shall have ground-fault circuit interrupter protection for personnel.
(2) Garages, and also accessory buildings that have a floor located at or below grade level not intended as habitable rooms and limited to storage areas, work areas, and areas of similar use
The CODE says nothing about whether they can be reached from the ground or not, only that the actual GFCI unit itself shall be installed in a readily accessible location. You could have outlets on the load side of the GFI, and they would still have to be protected
Marctrees
TX/LA border - Toledo Bend
First off, I am a big believer in GFI protection.
That said,
Code or not, whats the hulaballoo?
If they are on the ceiling dedicated for ceiling light purpose, and I wanted cord and plug for whatever reason, I would not worry about GFCI
Well, unless it's being inspected, then I don't know what's current. Marc
cybrdyke
USA
In professional lighting, it would be rare to see receptacles on the ceiling, with the exception of HID lighting in factories and warehouses. First, they would require GFCI protection which is very problematic with electronic ballasts and drivers. Ballasts and drivers both have leakage current which plays havoc on GFCI's, causing them to trip. And when the lights go out, who knows where the reset button is?
It's only in the DIY world, where it's more common to see folks cobbling together their own lighting. You might hear that using receptacles makes moving lights and doing maintenance easier. Personally, I've never seen anyone climbing a ladder to move their lights around. With the advent of uber long life LED's, maintenance is no longer much of an issue.
In my opinion, it's better to get the lighting design right from the start and then you wont have to worry about it.
Good luck
CD
William Payne
Wanganui, New Zealand
In the engineering shop where I work here in New Zealand we have hi-bay lights in the workshop and they are all plug in and were installed brand new that way. I just recently got a hi-bay light for my home workshop and it's a plug in deal as well. Beats me what the rules are for you guys though.
Most lights I've seen are hard wired but I just wanted to put it out there that in some places plug in is common.
cybrdyke
USA
Pretty much the same over here. Industrial high bays, whether they're HID or LED, are hung on hooks and then plugged into boxes connected by conduit. It's done mostly so that a maintenance worker can work on them easier.
Kia Ora
CD
marklc
I like hardwiring them just for aesthetics reasons. I don't like all that rubber cord dangling all over the ceiling. And again then no GFCI needed. Although in my area if they are up high out of reach inspectors don't care if they are GFCI or not.
cybrdyke
USA
something to consider when saying warehouse/plants use high bay lights that plug in............are they 120v lights?..........................
Generally not. 277v mostly. They use twist-lock plugs and receptacles so that the cords dont fall out.
CD
alfredeneuman
Fullerton, CA
yup, and the gfci rule only applies to 120v outlets
I know we have 480v 3ph all over the place here at the plant
You're talking Apples and Oranges here.
The GFCI rules are quite different when it comes to Commercial/Industrial vs Residential.
Lighting outlets, even if they're 120 Volts, aren't required in anything other than a Residential garage application.