In my 32x32 what's the preferred method for wiring ceiling lights?Receptacles or junction boxes?This is a pole barn.
Hardwiring. If you use outlets they need GFCI protection.
Can you quote this from the NEC?
My inspector said that if you could not reach them from the ground then no GFCI needed.
In my 32x32 what's the preferred method for wiring ceiling lights?Receptacles or junction boxes?This is a pole barn.
In the engineering shop where I work here in New Zealand we have hi-bay lights in the workshop and they are all plug in and were installed brand new that way. I just recently got a hi-bay light for my home workshop and it's a plug in deal as well. Beats me what the rules are for you guys though.
Most lights I've seen are hard wired but I just wanted to put it out there that in some places plug in is common.
something to consider when saying warehouse/plants use high bay lights that plug in............are they 120v lights?..........................
Generally not. 277v mostly. They use twist-lock plugs and receptacles so that the cords dont fall out.
CD
yup, and the gfci rule only applies to 120v outlets
I know we have 480v 3ph all over the place here at the plant