Tight Square Turn (90 degree) For EMT Conduit

penright

ALLIANCE MEMBER
Joined
Dec 27, 2016
Messages
618
Location
SW of Mustang, OK
By the way I am running 3/4 EMT.

Here is my obstruction.


I would like to continue along the bottom of the girt and make the corner behind the pole. There is a product that comes close to allowing what I need.
http://www.garvinindustries.com/conduit-fittings-supports/emt-conduit-fittings/pull-elbows/ecs-75

The problem is I don't think I will be able to get to the screws since they are on the inside.

I did do the 2 45 degree last night. The issue was I wanted to put shelves in that corner and **** up against the pole.

Assuming there is nothing that can be done. I can only think of two options.
1. Go overhead, the only down side is losing symmetry of the conduit in the building. (ring around the girt)
2. Hold the back legs of the shelf proud of the wall, then when I cut shelves allow the back to overhang and but back up with the wall.
 
To avoid these ads, REGISTER NOW!
OP
P

penright

ALLIANCE MEMBER
Joined
Dec 27, 2016
Messages
618
Location
SW of Mustang, OK
You could look at an lb or ll condolet.
It would have to be a LL (i think), after laying it in there the cover would have to be pointing down. I could leave the inside screw a little lose, notch the end so it would go around the "inside" screw". I could still get my pull. Will have to look at that.

Your thought got me thinking outside the box or should I say outside the conduit? Will MC make that bend? Do they make MC without wire. I know without wire it would not be a "cable".

Edit: Found it I think. AFC?
http://www.homedepot.com/p/AFC-Cable-Systems-3-4-in-x-25-ft-Flexible-Steel-Conduit-5503-22-AFC/205071931
I wonder how sharp can you bend it?
 
Last edited:

Radix2

Well-known member
Joined
May 28, 2014
Messages
1,853
Location
the thumb!, MI
Not seeing the issue against going inside the pole - place the shelf directly above. Space others from there.
 

LXCam

ALLIANCE MEMBER
Joined
Apr 23, 2013
Messages
19,204
Location
AZ
You could 90 up or down into a 4S box then 90 and kick or offset back into the web too.
 
OP
P

penright

ALLIANCE MEMBER
Joined
Dec 27, 2016
Messages
618
Location
SW of Mustang, OK
What about flex, like BX, or liquidtite?
I am guessing and one of the experts can correct me, let's assuming it can be bent that sharp of a turn, I bet there is code about radius vs size of EMT. As I learned in pulling my service about codes and 90's, sometimes following the code makes your life easier (besides saving it).
I guessing the reason LL and LB are the only options is because they are considered a box and you can restart a pull.

I still curious, how tight can you bend 3/4" flex both physically and code?
 
OP
P

penright

ALLIANCE MEMBER
Joined
Dec 27, 2016
Messages
618
Location
SW of Mustang, OK
Not seeing the issue against going inside the pole - place the shelf directly above. Space others from there.
It was late by time I figured out the 2 45 and I did not take a picture, I will when I get home before I pull it down and post it for future info. I think they call it a compound 90. There was not much in googling. The one thread I found was about 15 different opinions on how to do it. I finally went with the mock it up, join it in the middle, and got close.

The problem is when you look at it the bend starts about 4" to clear the obstruction. So you would have to hold about 4" off either the back or from the pole. Again, a picture will be worth a 1000 words.
 

davetulk

Well-known member
Joined
Feb 2, 2009
Messages
101
Location
Mid Florida
Is there any give in the insulation behind the post? If you picked up a prefab 90 bend from HD can you thread it behind the post? even Slide it in vertical then rotate it horizontal?

I might be totally off base...not that familiar with how the corners attached on steel building.

Also for my education why is that tight 90 not legal? I assume there would be no junction in it. http://www.homedepot.com/p/3-4-in-E...-EMT-Inside-Corner-Pull-Elbow-14607/100210850
 
Last edited:

LXCam

ALLIANCE MEMBER
Joined
Apr 23, 2013
Messages
19,204
Location
AZ
Well since you're really over complicated this transition. Use a LL to a close ****** to a pulling L to a close ****** to a LR. That'll keep everything at hard 90's but assuming that upright is 2"x2" will push the pulling L out maybe 1/2-1" or not a tad more. It all depends on how far or close I should say you can tighten the assembly.
 

DeltaWye

Well-known member
Joined
Sep 26, 2016
Messages
114
Location
Toronto, Canada
If you don't have the space behind the post to do a radiused 90 at the same elevation then your only options are to run on the inside, spot a box or fitting on the outside corner of the building and come back in after the post, or change elevations. I'd change elevations. Like Lxcam suggests in post #8, 90 down with a kick into a box or what I'd do is 90 down into another 90 going along the other wall. 90, offset or spot a box as per your requirements and degrees of bend accumulated before the corner in order to get back up to your height.
 
Last edited:

checkthisout

Well-known member
Joined
Sep 5, 2008
Messages
5,232
It was late by time I figured out the 2 45 and I did not take a picture, I will when I get home before I pull it down and post it for future info. I think they call it a compound 90. There was not much in googling. The one thread I found was about 15 different opinions on how to do it. I finally went with the mock it up, join it in the middle, and got close.

The problem is when you look at it the bend starts about 4" to clear the obstruction. So you would have to hold about 4" off either the back or from the pole. Again, a picture will be worth a 1000 words.

Hold it out then adjust shelving as needed. Not 100% sure what you have in mind but if a shelf rests almost on top of it then it's not interfering at all.

If you have adjustable metal shelving you can slide the post between the conduit and the post then install your shelving brackets.
 

LXCam

ALLIANCE MEMBER
Joined
Apr 23, 2013
Messages
19,204
Location
AZ
I have one last terrible suggestion (for many reasons) so no blasting from the peanut gallery. Get yourself a telephone 90 and drill your post and insert that in the post. Damn the structural aspect or the difficulty of pulling wire thru it, it would be legal from a code aspect and keep yourself clear of the corner.

800.jpg
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
I bet that would clear the corner, I think they make one with double set screw connectors. I liked the original idea of laying cable in the channel and covering it, so simple.
 
Last edited:
OP
P

penright

ALLIANCE MEMBER
Joined
Dec 27, 2016
Messages
618
Location
SW of Mustang, OK
Hold it out then adjust shelving as needed. Not 100% sure what you have in mind but if a shelf rests almost on top of it then it's not interfering at all. If you have adjustable metal shelving you can slide the post between the conduit and the post then install your shelving brackets.
I will be building them so I could make any adjustments. That is my plan B if the LL/LR doesn't work. The only reason right now I can see is it not working is if I can not get the cover on/off from underneath. As @LXCam said, I am over thinking it. Although overthinking is my personality, I also know if I don't think through it, my OCD will bug me every time I see it.



I liked the original idea of laying cable in the channel and covering it, so simple.
That is definitely starting to look like the better/easier option. But look at all the conduit bending I have learned. I did a compound 90, that I will not use this time and probably never. You know the old saying about education, it always cost time and money.
 

Radix2

Well-known member
Joined
May 28, 2014
Messages
1,853
Location
the thumb!, MI
I will be building them so I could make any adjustments. That is my plan B if the LL/LR doesn't work. The only reason right now I can see is it not working is if I can not get the cover on/off from underneath. As @LXCam said, I am over thinking it. Although overthinking is my personality, I also know if I don't think through it, my OCD will bug me every time I see it.

Now I am really missing your problem - if you are building your own shelves, just do a nice sweep to the inside of the beam and continue down the next wall, clean, nice and simple.

Build your shelf directly on top of the pipe height, space the other shelves from there.

Again, nice and simple...if the 3/4 in of the conduit under the shelf is interfering ..you are building your shelve too close together...

Or maybe I am still not getting what you are trying to do...:willy_nil
 

ard

Well-known member
Joined
Feb 16, 2015
Messages
4,391
Location
Sierra Foothills... California
There is NO WAY I would bury a box or LB or whatever deep in that corner behind a shelf. It defeats the entire concept of conduit- to be able to pull wires.

I would either do the back to back 45s and notch the shelf a little bit... OR... Compress the insulation by about 1/2" and slide a 90 into place.

My 2 cents


Edit: OP, you may not have this perspective- but every other sparky that has come upon someone else's work....they will be looking to add a circuit and will start pulling the wire and find "hey it's stuck"... A day later they will discover that some &$^$^ put an LB behind the post them built shelves over it.... They will post a picture on GJ.

;)
 
Last edited:

checkthisout

Well-known member
Joined
Sep 5, 2008
Messages
5,232
I bet that would clear the corner, I think they make one with double set screw connectors. I liked the original idea of laying cable in the channel and covering it, so simple.

He made the right decision going with the conduit. He's doing a good job too!
 
To avoid these ads, REGISTER NOW!

matt_i

Well-known member
Joined
Mar 14, 2008
Messages
10,752
Location
SE Michigan
Not seeing the issue against going inside the pole - place the shelf directly above. Space others from there.

That would be my take, couple of 45s. Notch the support post for the shelves or simply add spacer blocks to get more clearance to the steel corner.
 

ard

Well-known member
Joined
Feb 16, 2015
Messages
4,391
Location
Sierra Foothills... California
Now I am really missing your problem - if you are building your own shelves, just do a nice sweep to the inside of the beam and continue down the next wall, clean, nice and simple.

Build your shelf directly on top of the pipe height, space the other shelves from there.

Again, nice and simple...if the 3/4 in of the conduit under the shelf is interfering ..you are building your shelve too close together...

Or maybe I am still not getting what you are trying to do...:willy_nil

OP has some (and this isnt judgemental) OCD issues going on with the plane of the shelf sides, fitting right up to the post, no notches, etc, etc (I think)

OP, there are always- ALWAYS- trade offs. In this case it is 'continuous pipe, EMT fully functional and no hidden boxes/fittings' against 'there will be a notch in the side wall of the shelf'.

You can hide this notch by placing the shelf height just above the level of the notch. The notch will not be seen unless you get down an look for it.

HTH

GL

Agree looks good so far
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,770
Bend the EMT w/ 2-45's on the outside of the post, conduit bodies in a semi-concealed space ****.
 

ard

Well-known member
Joined
Feb 16, 2015
Messages
4,391
Location
Sierra Foothills... California
This is silly, but there is another way- keeps it all in two planes, perfect corner:


Adds 3 extra 90s, and would visually be much older than the other solutiuons. But, thought about it.

You could do it with two 90s, but then one piece would leave the corner at a differnet level (i.e. Not at the purlin). If each bend is a 6" radius, then one would be 12" at least offset
 

Attachments

  • image.jpg
    image.jpg
    8 KB · Views: 55

teamextreme

Well-known member
Joined
Aug 10, 2013
Messages
867
Location
Lakewood, CO
Bend the EMT w/ 2-45's on the outside of the post, conduit bodies in a semi-concealed space ****.

28 posts and only one person got it right! The ONLY appropriate solution is 2 45's. Quick, easy, still only 90 degrees of total bend, and no hidden or hard to get at conduit bodies.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,053
Location
NJ
B/c the 4" sq post is in the corner and not contained within the plane of the walls, nothing will ever fit tightly into that corner from both directions without a custom build. So it's really a moot point whether it is 1 or 2 sides that aren't tight into the corner.
I read the OP's problem as the vertical of the shelf being held away from the face of the 4" sq tubing. Nothing to do with the individual horizontal shelves or bracing.
Since shelving rarely moves once assembled (IMO), bend 2 45's with enough clearance between the conduit and tubing where the vertical leg can fit next to the 4" tubing and behind the conduit. Use a coupling in the center of the 45s.
And when the day comes where he is actually putting up the shelving, pull the wires out of the conduit, separate the conduits at the coupling between the 45's and put the entire shelf (leg) into desired position and re-assemble conduit/wires.
 

zmaxmotorsports

Well-known member
Joined
Jan 11, 2013
Messages
11,948
Location
South of omaha
This is silly, but there is another way- keeps it all in two planes, perfect corner:


Adds 3 extra 90s, and would visually be much older than the other solutiuons. But, thought about it.

You could do it with two 90s, but then one piece would leave the corner at a differnet level (i.e. Not at the purlin). If each bend is a 6" radius, then one would be 12" at least offset
:wtf::wtf::wtf::wtf:
How in the world would you ever pull wire through that?
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,053
Location
NJ
28 posts and only one person got it right! The ONLY appropriate solution is 2 45's. Quick, easy, still only 90 degrees of total bend, and no hidden or hard to get at conduit bodies.

Read post #1 again.
OP said he didn't like that method so he is looking for alternatives b/c going tight to the column keeps the shelves away from the corner/wall.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,053
Location
NJ
Well, there's that too.

:thumbup:

(And on the 'two 45s' comment above...its been here since post 1.) That comment has already been said also.

On running a 90, those outer walls that look like insulation MAY have some compression- it won't take much to get a 6" bend to make it

Time for arts & crafts for you -
draw this out to scale. If that channel is 1" or even 1.5", you are not getting a 3/4 emt 90 around that post in that small of a gap.
 

checkthisout

Well-known member
Joined
Sep 5, 2008
Messages
5,232
Try the 90 but if it doesn't work I.E. it might hit the post and want to pull the rest of the run outward toward the insulation, you'll need to make your bend like this. Sorry I **** at paint.

View media item 67470
Can't tell you exactly where to start the bends but you'll make an offset bend, then a 90 bend then another offset bend. This will allow the 90 radius to fit better without it's inner radius hitting the post and wanting to pull the straight portion of the run outwards towards the siding.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
This isn't the real problem. It's really amateur advice in a way. It comes from an absolute compulsion and fear that some day at some point he will need to pull several new circuits in to start a power plant fab shop in the corner of this garage.
Out of the 100's of times I have done this I can't recall having to go back in and pull extra wires for something new. In fact when it's all over could remove 1/2 of the ones I have and not lose a thing.
The logic is lost right up front, "if he wants to put more welders in the corner" etc . This is a small 2 car garage at that.
I add things and even remodel but never needed to break back in to a general to "add for welders and saws" in the same pipe.
My neighbor has this, 2 120v circuits for tools, lathe, mill, about 6 or 8 wood saws, 2 for 240, 1 for a welder and 1 for a comp and the only wire mod done since was to tap for a new gas heater. same for my buds auto shop, 1 mod once right at the panel for AC. 30 yrs 2 men work there.
It's nice work but it's a waste of time and money other than it's cheaper than sitting in the bar, there isn't a deal breaker here but doing this in 1/2 would have done the same thing but the group pile on really does a disservice and does it for the rest want to learn.
No spec builder would do this,, the most he would ever add is a small run out of the panel which is great it's there with extra spaces.
This is not a hospital, a casino or machine shop in which 99 percent of the time a new pipe is run anyway.
This would have been easy and neat in 1/2.
 