Grounding wires inside boxes
bobinyelm
Olympia, WA
I am running #6 wire for a welder using 6-2 w/gnd NMC.
Obviously I will connect the ground wire to the grounding terminal of the 50a receptacle, but what gauge minimum do I have to run to the metal box itself?
It would seem that the box wire doesn't carry current, but is there for "short protection" to blow the breaker, so a lesser gauge would suffice.
Same question for my 30a 220v #10 wire for my compressor...
Thanks
Bob
mm08822
The overcurrent protection for the circuit determines the minimum size of the egc.
The size of the grd wire jumps at various breaker sizes. See table 250.122.
The 6-2 nmb will have a #10 grd wire. Use #10 to pickup the box. A pigtail will work best here.
10-2 nmb will come with a #10 grd wire. Use #10 to pickup the box. A pigtail will work best here.
wyliesdiesels
Modesto, CA
u need #10 for both circuits.
bobinyelm
Olympia, WA
Thanks for the table.
I noticed that the #6 had #10 ground wire, so I guess that they automatically size the ground wire inside cable according to that table, so you're safe using the same for grounding. Makes sense!