Grounding wires inside boxes

bobinyelm

Well-known member
Joined
Nov 5, 2016
Messages
152
Location
Olympia, WA
I am running #6 wire for a welder using 6-2 w/gnd NMC.

Obviously I will connect the ground wire to the grounding terminal of the 50a receptacle, but what gauge minimum do I have to run to the metal box itself?

It would seem that the box wire doesn't carry current, but is there for "short protection" to blow the breaker, so a lesser gauge would suffice.

Same question for my 30a 220v #10 wire for my compressor...

Thanks

Bob
 
To avoid these ads, REGISTER NOW!

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,051
Location
NJ
The overcurrent protection for the circuit determines the minimum size of the egc.
The size of the grd wire jumps at various breaker sizes. See table 250.122.

The 6-2 nmb will have a #10 grd wire. Use #10 to pickup the box. A pigtail will work best here.

10-2 nmb will come with a #10 grd wire. Use #10 to pickup the box. A pigtail will work best here.
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,073
Location
Modesto, CA
u need #10 for both circuits.

QID86_large.jpg
 
OP
B

bobinyelm

Well-known member
Joined
Nov 5, 2016
Messages
152
Location
Olympia, WA
The overcurrent protection for the circuit determines the minimum size of the egc.
The size of the grd wire jumps at various breaker sizes. See table 250.122.

The 6-2 nmb will have a #10 grd wire. Use #10 to pickup the box. A pigtail will work best here.

10-2 nmb will come with a #10 grd wire. Use #10 to pickup the box. A pigtail will work best here.

Thanks for the table.

I noticed that the #6 had #10 ground wire, so I guess that they automatically size the ground wire inside cable according to that table, so you're safe using the same for grounding. Makes sense!
 