EMT grounding
PoorOwner
CA
Do I need to pull a ground (THHN/THWN) if using EMT if the first metal box is grounded with a green ground screw?
I think I prefer to pull one though. So at each box the ground wire needs to ground the box and receptacle, right?
also, where it is coming in the first box through the garage wall, (romex) is it acceptable to just wrap the ground wire around the ground screw without cutting it before going to wire nut. Saving some space.
wolfhawk73
Eastern North Carolina
Do I need to pull a ground (THHN/THWN) if using EMT if the first metal box is grounded with a green ground screw?.
Yes.
I think I prefer to pull one though. So at each box the ground wire needs to ground the box and receptacle, right?.
Yes.
Yes.
At least that's what I did for years, and I doubt the NEC has back-tracked on those requirements since '03.
Don't quote me. :evil:
sberry
Brethren, Michigan
The first box is bonded with the screw to the service neutral, the second would be bonded thru the conduit provided one didn't use partial knockouts. The second box will need an additional ground bar and if you want run a green or bare wire from service neutral to it. Depending on how many spaces are available in the first box it may save some congestion and ease to add a ground bar to it also, can attach ground rods and grounding conductors it instead of neutral.
mm08822
You're talking about panels. OP is talking about boxes in conduit runs for devices.
wyliesdiesels
Modesto, CA
No.
Code allows EMT to be used as the EGC and therefore no additional conduxtor is needed for an EGC.
If using metal boxes and self grounding outlets then u would only need to ground the box.
Yes u can do that.
Incorrect.
Read first comment above...
P
PoorOwner
CA
So.. basically the common 15 A receptacle is self grounding?
So no ground wire in the second box, but need pigtail from receptacle TO the box.
Even though you says "self grounding", shouldn't mounting the receptacle to the box itself give me the ground?
I will check the ohms after the job, likely there will be a few ohms but it should be grounded well?
For the pigtailing then.. can I use 14 gauge solid on a 20 amp circuit ( with 12 THHN for hot and neutral)
sberry
Brethren, Michigan
You need to use a 12 but, self grounding is for devices screwed in to the box but if it is mounted in the cover needs a tail. I skip it on a few I have mounted in handy boxes, most of my 4x4 is cover mounted so I can change the configuration some if wanted, its pretty much a personal thing though.
wyliesdiesels
Modesto, CA
Yes but check outlet to be sure.
Dont need one in first box either.
No pigtail needed IF conduit is continuous metal, panel to box, box is metal, AND outlet is self grounding.
Yes thats what self grounding means. It grounds itself to the box.
For 15a circuits #14 for EGC, 20a circuits #12 for egc and 30a circuits #10 for egc...
P
PoorOwner
CA
OK.. I got it..
it's NOT directly connected to the panel. In the first box, it has a romex 12/2 coming in. So will ground that with a ground screw. Then the 2 wirenut to THHN.
However.. What if the first box has 2 romex (2 circuits) coming in.. it sounds like just need to tie the 2 grounds together and to the first box then?
ard
Sierra Foothills... California
Not all receptacles ARE 'self grounding'.
When one IS self grounding, and has this feature (usually a spring doohicky at the yoke), then it will self ground- no need to attached it to the ground point in the box.
However many (most?) cheap receptacles are NOT self grounding.
At least that is my recollection
P
PoorOwner
CA
I will run the pigtail
Just one thing though. I just got the motor switch that is in a metal box with knock outs. The inside and outside of the box are both painted. How would i get a good ground out of this if I don't run a ground wire.
The knock out 2 step. is a 1/2 inside a 3/4 so the retaining nut might not fit that well either
It may make a little contact but I think some sanding is needed for best result
P
PoorOwner
CA
I am still not liking the heavily painted , on both side concentric knock outs, apparently you don't need a grounding bushing .. (Lock nut with a clamp for ground wire) until greater than 250V, can anyone confirm.
It doesn't look like for 1/2 KO this is a popular piece either, because who would run 250V+ circuit thru 1/2 KOs. But it seems there is a few pieces available. I would need one on both entrance and exit of the box to get good grounding
wyliesdiesels
Modesto, CA
Just scrape the paint off.
And yes bonding bushings are required for 480v not 240v...
U could certainly use one if u wanted to....
grantw
Bay Area, CA
I added a bonding bushing to my 2" EMT that feeds my 40 space sub-panel. I don't trust lock nuts against a painted surface to catch a 200A fault. For the 3/4 emt out of the sub, I have a ground wire. Overkill for home use, but I sleep easier. I guess in 20-30 years, the new owner will also know exactly where ground is just pulling one outlet..?
wyliesdiesels
Modesto, CA
:+1:
I dont trust good continuity through paint either....even more so if its a concentric knockout with only very minimal contact via the 2 tabs...