What wire would be suggested to go from compressor to a load center? Compressor has 12/3 going from pressure switch to motor, so would 10/3 be ok? Manual suggests a 40 amp breaker though and says 23 amps at full load.
 
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Based on 23A the #10 is okay, but under the NEC the HP of the motor determines the circuit size. Also 10/3 is not needed, use 10/2. A neutral is not required. With amps at 23 the motor HP is over 3HP and should be hardwired.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
I am a code believer but this is one if the fine lines doesn't cause me sleep loss. These are wired all the time 10 cable 30 breaker, never seen one trip it.
 
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,758
Use EMT & pull 10 AWG THHN conductors and it will be fine.
 

RickP

Well-known member
Joined
Jan 15, 2013
Messages
1,549
Location
Annapolis, MD
It says 5 hp. I was planning on mounting a disconnect near the compressor with a 40 amp breaker. What wire would be suggest for just the 5 or 6 feet to the compressor?

I wired my compressor with this whip from Home Depot:
01a1d729-b499-4286-b399-5263f8c074c0_400_compressed.jpg


It's wired with stranded 10 THHN, and it's only about $9.
 