What wire would be suggested to go from compressor to a load center? Compressor has 12/3 going from pressure switch to motor, so would 10/3 be ok? Manual suggests a 40 amp breaker though and says 23 amps at full load.
Use EMT & pull 10 AWG THHN conductors and it will be fine.
It says 5 hp. I was planning on mounting a disconnect near the compressor with a 40 amp breaker. What wire would be suggest for just the 5 or 6 feet to the compressor?