Wow lots of misinformation here....
There is for certain, now. Although it's super late I typed a looooong reply and then it disappeared when I tried to post it.
Some of your corrections are debatable such as the GEC size (250-66 and MANY AHJs and pocos) Repeating your local requirement in no way makes yours a blanket application. My reference to the 'meter can' was clearly being used collectively of the combo panel and you are being disingenuous for picking that particular nit.
yes. this is now your main disconnect.
Largest wire needed to rods is #6 not #4....
[/COLOR] [/COLOR]
U need an insulating bushing on the bottom of the can where the cables enter the panel.
[/COLOR][/COLOR]
NO
your house panel is now a subpanel and rods should not be connected to the neutral bar....
Largest wire required to rods is #6 NOT #4...
[/COLOR][/COLOR]
Look closer.
Always good advice!
That is a combination meter main service panel. The meter section and breaker section are one panel.
So no bonding needed....
[/COLOR]
The house panel is being fed by 4-wire SER so its bonded via the bare aluminum ground wire...
He is correct in needing to separate the neutrals and grounds in his house panel as its now a subpanel.
Neutrals and grounds should only be bonded at the first means of disconnect. After that, neutral bars need to be isolated...
And he will need to add an EGC...
That is incorrect. The the house and barn panels dont need a direct EGC between them.
Where did u come up with that?
Have you read an NEC? I mean SINCE 2005? The four-wire with EGC has been code since *2008(!)*. If this were a previously installed three wire it could be retained and the neutral and ground WOULD be bonded there! 250.32 I think that one is. What purpose do u think that would serve?
if you reference that book I mentioned (NEC) you would find that it serves to provide a rapid path back to the over current device that is designed to trip in response. Relying on *soil* to provide this path to the interrupt device has long proven inadequate and dangerous. NEC2008 (there's that thing again) 'outlawed' the practice. It's not different from the reason that grounded receptacles were implemented decades ago. Before proclaiming that others are spreading misinformation , perhaps you would be well served to trouble yourself to be correct. I'm fully aware that I'm new to this board, having lurked learned and enjoyed it. But I'm not here to pick any fights and will only try to help. Accusing me of being wrong is fine, but at least be right and ready to back it up. I love debate. I'm not keen on accusations.
A meter can is NOT the first means of disconnect. However, in the OPs case, he has a combination meter main with the meter on the left and the main disconnects on the right.
again, I think you're being a bit trite with this differentiation.
The OP should connect the rods to the neutral bar that is in the top left of the disconnect section. This is factory bonded to the panel.
Look closer next time.
[/COLOR][/COLOR]
Again the house panel(not seen) IS bonded via the bare ground from the SER...
[/COLOR][/COLOR]
Yes, he is missing the GEC to the rods and it is surprising that it is missing.
However, I disagree that it is dangerous. This is because rods are for grounding lightning and have no function under normal operation....
not entirely, also serves to stabilize the xformer's secondary voltage and reduce spikes caused by other events
U need to use a bare solid #6 that goes from the upper left neutral bar to the 2 rods....
the real answer is what his local AHJ and poco require...but ridiculously, it appears they don't require.....anything! But MANY require #4
U dont need an EGC direct from inside house panel to barn panel. Im not sure where he came up with that but its incorrect.
Again, on this you are flat wrong. I hope you'll recognize it and correct your clearly outdated position. The source is still NEC 2008; 2011; 2014. Your 4-wire feeders from the disconnect panel to the subpanels is correct.
Make sure the barn panel has 2 rods as well.
Max size required to rods is #6 NOT #4....
Ground rods have nothing to do with bonding panels with EGCs....grounding electrodes are for grounding lightning NOT bonding....