Need help reading breaker schematic

R-mm

Well-known member
Joined
Dec 24, 2013
Messages
420
Hello all I need some assistance reading the schematic on my breaker box. If I want to add a 120/240 circuit for an electric oven can I use any two empty slots on a given side or must I use one of the bottom four? I can not find a legend that explains the symbols on the

Image1494244824.862672.jpg
 
To avoid these ads, REGISTER NOW!
OP
R

R-mm

Well-known member
Joined
Dec 24, 2013
Messages
420
That is confusing because 17-24 are where the existing 240 loads are connected...

Image1494247461.590428.jpg
 
OP
R

R-mm

Well-known member
Joined
Dec 24, 2013
Messages
420
So somebody has done the wrong thing by using slim breakers on number 1?


Sent from my iPhone using Tapatalk
 

Movover

Well-known member
Joined
Jan 14, 2015
Messages
585
Location
Central Maine
So somebody has done the wrong thing by using slim breakers on number 1?


Sent from my iPhone using Tapatalk

Breaker 1 is not a slim it a tandem, 2 breakers built into 1 package (Not to be confided with Double pole). A slim is a half size breaker
 
OP
R

R-mm

Well-known member
Joined
Dec 24, 2013
Messages
420
Ok so... i can either free up space by using more tandems above or adding slims in 17-24. I can put my 120/240 anywhere i make the space? And is it correct that 120/240 ALWAYS takes two slots there is no way to draw from both hots in a single slot?


Sent from my iPhone using Tapatalk
 

Movover

Well-known member
Joined
Jan 14, 2015
Messages
585
Location
Central Maine
I would put the slims in 17-24 move the double poles to where you made room and I believe that will free you up enough. The new tandems have a molded piece that will not let them fit in any slot now because this is "cheating" and most panels are not designed for that extra load on the buss stabs. Of course the GJ way is the same way I fixed the problem and that is to install a larger panel :)

Yes 240V will always be 2 slots that I am aware of. No way to get both phases on 1 slot
 

walta

Well-known member
Joined
Jan 13, 2017
Messages
2,313
Location
Dutzow Missouri
After seeing the photo, I think the diagram is wrong or the breakers are numbered strange order.

Walta
 

brewchief

Well-known member
Joined
Sep 20, 2008
Messages
2,371
Location
Michigan
It looks to me like the bottom two full size slots will fit the half size breakers, there is a two pole breaker that's like two of the half size but IIRC you need to put it on the spot that it can hit both busses. This means a half size single then a two pole slim(same as one of the regular single pole) and then another half size. If you put them in the wrong spot you get both poles on the same bus.

That tandem at the top left is not a GE breaker and shouldn't be there at all.

With some shuffling you can make room, a larger panel or a sub panel will be in your future if you need much more room beyond that.
 
To avoid these ads, REGISTER NOW!

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,055
Location
NJ
After seeing the photo, I think the diagram is wrong or the breakers are numbered strange order.

Walta

The diagram is correct. The numbering is a little odd on the diagram b/c if you are using full size cb's in the bottom 2 slots it is only 2 ckts not 4. E.g. 17A and 17B would be better than 17 & 19.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,055
Location
NJ
I don't think the diagram matches the actual layout, I only count 20 breaker spots

It is correct. Panel has 20 full size breaker slots. But the 2 bottom spaces (L & R) can use 1/2 size cb's and give the total of 24 ckts.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,055
Location
NJ
It looks to me like the bottom two full size slots will fit the half size breakers, there is a two pole breaker that's like two of the half size but IIRC you need to put it on the spot that it can hit both busses. This means a half size single then a two pole slim(same as one of the regular single pole) and then another half size. If you put them in the wrong spot you get both poles on the same bus.

That tandem at the top left is not a GE breaker and shouldn't be there at all.

With some shuffling you can make room, a larger panel or a sub panel will be in your future if you need much more room beyond that.

Agreed, that top left tandem cb should not be in there. New panel should be in the plans.

Op, is this a sub or where is the main cb?
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,770
Top left breaker looks like an Eaton BR.

It should be removed and replaced with a GE...

It's a Siemens breaker, here is a photo of a Gould/ITE which is the original design of what is now Siemens, & the hack done to make them fit a GE.



The hack is required to make a competitive make twin breaker fit a space made for twins in a GE panel.
 

Stuff

Well-known member
Joined
Aug 31, 2013
Messages
572
GE does may a 2 pole / 240v tandem/slim. You can use it in slots 19/21 or 20/22 and then use slim/tandem on either side. Some recommend only using full size breakers for large loads but it does give you another option.
2d534948-3adb-4dc9-9013-06cdc47783f9_1000.jpg

http://www.homedepot.com/p/GE-Q-Line-50-Amp-1-in-Double-Pole-Circuit-Breaker-THQP250/100356520
 
OP
R

R-mm

Well-known member
Joined
Dec 24, 2013
Messages
420
Thanks guys I have a bunch of slims to replace small loads and a full size two pole for the oven.

I cant figure out what type of bushing i need for the armored cable coming out of the oven. Its about .9in outside diameter and I want to get it into a pretty std 4in metal box.

I noted that incorrect breaker too and will remedy.

Image1494440586.338650.jpg
Image1494440599.110465.jpg
 

brewchief

Well-known member
Joined
Sep 20, 2008
Messages
2,371
Location
Michigan
Looks like a fitting for 1/2" greenfield would be right.
The only place the slims will work is the bottom two spaces.

Sent from my XT1254 using Tapatalk
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,778
Location
NW Iowa
I cant figure out what type of bushing i need for the armored cable coming out of the oven. Its about .9in outside diameter and I want to get it into a pretty std 4in metal box.
]

Any standard flex connector will work. I think that would be 1/2 flex, but not sure off the top of my head.
 