clanure
Member
Hello,
Been lurking for quite a while, learning what I can. My shop construction just got finished, but the flooring, lighting, hvac, and electrical are on me. Here's my intro for pics of the shop:
https://www.garagejournal.com/forum/showthread.php?t=370981
Figure I'd start with the electrical, so have been researching what I can. This is what I have planned so far and would like to have all of your input on it.
Here's the meter panel on the house, I'll add a 100 Amp breaker to this panel.
Homeline 100-Amp 2-Pole Double-Pole Circuit Breaker:
https://www.lowes.com/pd/Square-D-Homeline-100-Amp-2-Pole-Double-Pole-Circuit-Breaker/3363896
I'll trench the ~100 feet from the house to the shop. Here's the run:
I'll have to make one small (less than 90 degrees) turn around the house and then straight to the shop:
I'll be using 4 separate #2 THHN through 2" conduit, with 2 90 elbows and that small turn around the house.
I'll enter the shop here, between the window and the end of the building:
I'll use one of these to enter the shop (Above or Below?) the panel:
https://www.lowes.com/pd/CARLON-2-Type-LB-Nonmetallic-Conduit-Body/3127635
I'll use this for the panel:
https://www.lowes.com/pd/Square-D-Homeline-40-Circuit-20-Space-100-Amp-Main-Breaker-Plug-On-Neutral-Load-Center-Value-Pack/50311143
I'll frame out this section here with metal studs and mount the panel:
I had a grounding rod included when the slab was poured, so I'll ground the panel here:
Once I get the panel in, then I'll finally get to the fun stuff of lighting, hvac, and setting up shop.
So, what do you think? Is everything I'm doing making sense? Anything I should change? Should I up-size anything?
Appreciate any comments or suggestions.
Lynn
Been lurking for quite a while, learning what I can. My shop construction just got finished, but the flooring, lighting, hvac, and electrical are on me. Here's my intro for pics of the shop:
https://www.garagejournal.com/forum/showthread.php?t=370981
Figure I'd start with the electrical, so have been researching what I can. This is what I have planned so far and would like to have all of your input on it.
Here's the meter panel on the house, I'll add a 100 Amp breaker to this panel.
Homeline 100-Amp 2-Pole Double-Pole Circuit Breaker:
https://www.lowes.com/pd/Square-D-Homeline-100-Amp-2-Pole-Double-Pole-Circuit-Breaker/3363896
I'll trench the ~100 feet from the house to the shop. Here's the run:
I'll have to make one small (less than 90 degrees) turn around the house and then straight to the shop:
I'll be using 4 separate #2 THHN through 2" conduit, with 2 90 elbows and that small turn around the house.
I'll enter the shop here, between the window and the end of the building:
I'll use one of these to enter the shop (Above or Below?) the panel:
https://www.lowes.com/pd/CARLON-2-Type-LB-Nonmetallic-Conduit-Body/3127635
I'll use this for the panel:
https://www.lowes.com/pd/Square-D-Homeline-40-Circuit-20-Space-100-Amp-Main-Breaker-Plug-On-Neutral-Load-Center-Value-Pack/50311143
I'll frame out this section here with metal studs and mount the panel:
I had a grounding rod included when the slab was poured, so I'll ground the panel here:
Once I get the panel in, then I'll finally get to the fun stuff of lighting, hvac, and setting up shop.
So, what do you think? Is everything I'm doing making sense? Anything I should change? Should I up-size anything?
Appreciate any comments or suggestions.
Lynn