Two questions:
1) I know that Mitsubishi hyperheat units maintain full heat capacity down to 5 deg F or something like that. But is there a limit to the temperature differential that they can maintain? For example, assuming you have an appropriate sized unit, would it be able to maintain a room at 74 degrees F even when it is 10 degrees F outside?
My existing, ducted split system was having trouble keeping it above 68 when it was 10 outside (of course, if I allow the system to turn on the aux heat strips, then it has no problems going above 68).
2) Suppose you get the outdoor unit model MXZ-5C42NAHZ that can support 5 indoor units. According to submittal data (http://meus1.mylinkdrive.com/files/MXZ-5C42NAHZ_Submittal.pdf), it can ramp all the way down to 6000 btu cooling, and 7200 btu heating.
Suppose for your indoor units, you have 5 x MSZ-FH12NA (standard wall unit). According to submittal data (http://meus1.mylinkdrive.com/files/MSZ-FH12NA~MUZ-FH12NA_Submittal.pdf), these units can ramp all the way down to 2500 btu cooling and 3700 btu heating.
My question is this: Does the minimum running capacity of the outdoor unit (6000/7200) control the minimum capacity that the indoor units can ramp down to? Or can multiple indoor units be running at below 6000 btu, so long as the total of the running indoor units equals the 6000 btu minimum of the outdoor unit?
In other words, could two indoor units be running at 3000 btu each to reach the minimum 6000 btu of the outdoor unit? Or does the 6000 btu minimum of the outdoor unit dictate that, whenever an indoor unit is running, it must be running at at least 6000 btu?
Thanks in advance!
1) I know that Mitsubishi hyperheat units maintain full heat capacity down to 5 deg F or something like that. But is there a limit to the temperature differential that they can maintain? For example, assuming you have an appropriate sized unit, would it be able to maintain a room at 74 degrees F even when it is 10 degrees F outside?
My existing, ducted split system was having trouble keeping it above 68 when it was 10 outside (of course, if I allow the system to turn on the aux heat strips, then it has no problems going above 68).
2) Suppose you get the outdoor unit model MXZ-5C42NAHZ that can support 5 indoor units. According to submittal data (http://meus1.mylinkdrive.com/files/MXZ-5C42NAHZ_Submittal.pdf), it can ramp all the way down to 6000 btu cooling, and 7200 btu heating.
Suppose for your indoor units, you have 5 x MSZ-FH12NA (standard wall unit). According to submittal data (http://meus1.mylinkdrive.com/files/MSZ-FH12NA~MUZ-FH12NA_Submittal.pdf), these units can ramp all the way down to 2500 btu cooling and 3700 btu heating.
My question is this: Does the minimum running capacity of the outdoor unit (6000/7200) control the minimum capacity that the indoor units can ramp down to? Or can multiple indoor units be running at below 6000 btu, so long as the total of the running indoor units equals the 6000 btu minimum of the outdoor unit?
In other words, could two indoor units be running at 3000 btu each to reach the minimum 6000 btu of the outdoor unit? Or does the 6000 btu minimum of the outdoor unit dictate that, whenever an indoor unit is running, it must be running at at least 6000 btu?
Thanks in advance!