kd3pc

Well-known member
Joined
Aug 10, 2013
Messages
3,630
Location
Northern Neck
marine shore power transfer switch will do exactly what you want to do.. Check out eBay for Blue Seas or other model
 

u3b3rg33k

Well-known member
Joined
Dec 18, 2017
Messages
4,087
Doing it this way I do not have to buy anything else... To me it gives me more flexibility...

I'm wondering about doing it this way and NEC code...


You'll have to BUY a generator transfer switch though. a grid tie inverter is the right move here, at least if you care about ROI. it doesn't make literal cents to draw down lead acid batteries and recharge them when you have the grid available. keep them in float charge and use the power directly.

or spend nothing and waste money.


anyways code requires you to use a transfer switch that does not allow for the possibility of feeding inverter power back into the grid.
 
Last edited:

u3b3rg33k

Well-known member
Joined
Dec 18, 2017
Messages
4,087
Time to get ticked off then. i'd hardly call that free. operating a solar + lead acid battery system costs more per kWh than grid power.

I already answered question 1. you need a transfer switch that cannot backfeed the grid with your inverter output.

2. yes, you can have multiple power sources feeding different panels - doesn't matter if they're solar/generator/UPS/kid-on-a-bike-power. it sounds like you need to start doing some research.
 

Bretny

Well-known member
Joined
Jul 31, 2017
Messages
3,918
Location
Dutchess county NY
The power you can make at home is always going to cost more than what the power company can provide you. Unless we are talking about a grid tied system and tou get ALOT of sun. Once you go adding batterys to the system and a charge controler your more expensive than the power companys power.

Buy a generator.
 

u3b3rg33k

Well-known member
Joined
Dec 18, 2017
Messages
4,087
dude buy a code book. your AHJ/insurance guy gonna take "u3b3rg33k quoted code so i did what he said" when your garage burns down?
 
To avoid these ads, REGISTER NOW!

HOTFR8

Banned
Joined
Mar 2, 2007
Messages
24,498
Location
Castlemaine, Victoria. The Hot Rod Centre of Austr
I've collected enough parts to build a solar system of sorts. Here's what I'm considering. Using a 1200W solar panel input to charge a bank of batteries, then pull off the bank at 24VDC to power an inverter, coming out of it at 120VAC to power shop lights and 120V small loads. What I want to do is is have it set where I can switch from my solar source to Utility source as needed through a 3 pole relay. I'd switch the Hot, neutral and ground through the relay all at once from each source going out to the load. I'd like to have the load on the common, Utility 120V on the NC contact and Solar 120V on the NO contact and power the coil to energize through either a remote switch or have it set up so when the batteries get to a preset threshold state of discharge, it denergizes the coil and goes back to Utility power source.

What does NEC code say about something like this?

Would be much easier just to have a smart inverter that can connect or disconnect from the grid as I have. Otherwise why not set up the Solar to stand alone separate from your grid power and I have done this as well.
 

American Locomotive

Well-known member
Joined
Jan 8, 2017
Messages
11,185
Location
Rhode Island
You can do whatever you want inside your own garage. Code only matters when its time to sell, you get electrocuted, or your house burns down. If you want dedicated solar-powered circuits, go right ahead and put them in. You could switch your lighting and small loads circuit with a Triple-Pole-Double-Throw contactor/relay. Make sure it's rated for whatever the feeder circuit is capable of delivering.

As to the others saying "generating your own power at home is always more expensive" - that is only true if you're actually generating power from some sort of fuel source. Solar has a fixed one-time investment cost. Provided your batteries last a long time, and you have decent panels that don't degrade fast - it'll make "free" electricity once the initial cost is paid off.

Grid-tie inverters are great if you have constant high-power draws. However if your house usually has low power draw, grid-tie may not be all that great for you during the day, and will not help you at night. Many utilities will not pay (or allow) for grid-returned power, and if they do, its usually at a lower rate than they sell power to you. Additionally, grid-tie inverters are designed to shutdown if the mains loses power.

Battery-tied solar systems allow you to store and use power as you please. If you have low-demand during the day, your batteries will charge up all day. Once night time hits, you can start drawing off the batteries. With a large enough system, it's conceivable you'd never have to use power from the grid at all. However, your limited by the size of your inverter and battery system, and it's also less efficient.

There are pros and cons to each system, and it sounds like the OP has it figured out what he wants from his solar system.
 
Last edited:

u3b3rg33k

Well-known member
Joined
Dec 18, 2017
Messages
4,087
Code is there for safety of you and others. the reason code specifies the narrow blade is hot and the wide blade is neutral isn't just to "be code", it's for appliances that used a neutral bonded metal cabinet - if you flip L and N on an outlet and plug that in, you have a HOT box sitting out! if that circuit gets completed to ground/neutral by anyone/anything, bad things happen. if it happens to someone else because you play with that attitude, you might end up on the hook for whatever happens because of it.

You can do whatever you want inside your own garage. Code only matters when its time to sell, you get electrocuted, or your house burns down. If you want dedicated solar-powered circuits, go right ahead and put them in. You could switch your lighting and small loads circuit with a Triple-Pole-Double-Throw contactor/relay. Make sure it's rated for whatever the feeder circuit is capable of delivering.

As to the others saying "generating your own power at home is always more expensive" - that is only true if you're actually generating power from some sort of fuel source. Solar has a fixed one-time investment cost. Provided your batteries last a long time, and you have decent panels that don't degrade fast - it'll make "free" electricity once the initial cost is paid off.

Grid-tie inverters are great if you have constant high-power draws. However if your house usually has low power draw, grid-tie may not be all that great for you during the day, and will not help you at night. Many utilities will not pay (or allow) for grid-returned power, and if they do, its usually at a lower rate than they sell power to you. Additionally, grid-tie inverters are designed to shutdown if the mains loses power.

Battery-tied solar systems allow you to store and use power as you please. If you have low-demand during the day, your batteries will charge up all day. Once night time hits, you can start drawing off the batteries. With a large enough system, it's conceivable you'd never have to use power from the grid at all. However, your limited by the size of your inverter and battery system, and it's also less efficient.

There are pros and cons to each system, and it sounds like the OP has it figured out what he wants from his solar system.

It's always more expensive, even for solar, just by factoring in the cycle count and capital cost of the batteries.

about $0.28/kWh for flooded lead acid. grid power costs half that. the only way it's cheaper than grid power is if you get your batteries for free.

http://webs.wichita.edu/depttools/d...Hour to Store Electricity final published.pdf

Mind you if you're factoring in the cost of having power lines run to your house because you're building where they won't hook you up for a marginal cost, then that's different.
Either way li-ion has a better cost/kWh than lead acid due to the short lifespan of lead acid when used beyond 50% DoD. Failing to fully charge lead acid on a daily basis causes additional wear.

if you're comparing solar+batteries to a generator, then you might come out ahead, or not. a standby generator with a full fuel tank won't degrade much if well protected from the weather (both the fuel and the generator). possibly longer than the standby lifetime of a set of lead acid batteries.

The only way to see actual return on investment with batteries is to do a grid-tie with battery backup. this keeps the batteries charged for maximum lifespan, and you sell any surplus generation back to the grid. this gets you UPS grade backup power if done with modern equipment (double-online or standby style), and if you live in a place that does time-of-use or event priced power, you can switch to battery for load shaving whenever the price point makes sense.

Long-term testing of solar panels shows them to have 80% or better output after 20+ years of use. that seems pretty solid.
 
Last edited:

American Locomotive

Well-known member
Joined
Jan 8, 2017
Messages
11,185
Location
Rhode Island
It's always more expensive, even for solar, just by factoring in the cycle count and capital cost of the batteries.

about $0.28/kWh for flooded lead acid. grid power costs half that. the only way it's cheaper than grid power is if you get your batteries for free.
Your figure is pretending that no power will be used from the grid during the day, and that the battery is only going to last the minimum amount of time, and that the battery is going to be fully discharged every single time. A good deep cycle lead acid battery will last thousands of cycles if only partially discharged - up to 5,000 cycles or more for certain gel-cell type batteries.
 

u3b3rg33k

Well-known member
Joined
Dec 18, 2017
Messages
4,087
Your figure is pretending that no power will be used from the grid during the day, and that the battery is only going to last the minimum amount of time, and that the battery is going to be fully discharged every single time. A good deep cycle lead acid battery will last thousands of cycles if only partially discharged - up to 5,000 cycles or more for certain gel-cell type batteries.

If you want to cherry-pick data, then the 10,000+ short-cycle life of NiCd would be the real kicker. having a pack big enough to do useful work running a shop while lasting 5k cycles is one hell of a battery pack. Even the people I know who are off-grid and have banks made of trojan forklift batteries only have a few days of power in the winter at most - if they conserve. you can equalize a bank of forklift batteries easily and not suffer thanks to being able to water them - you have to take apart your battery bank and charge cell by cell to equalize a gel pack. it's not at all practical for this sort of use.

most people don't have a battery pack big enough to draw down power at the 20 hour rate - the 4 hour rate is more likely, and that gives you 80% discharge efficiency added on to the 80% charge efficiency. assuming for the sake of argument you charge from a 1200W array, your net available power from the array is effectively reduced to about 750W. if you were charging from the grid, you'd be paying 40% extra for power.


if you want a battery bank of AGM or gel batteries big enough to get a 5k cycle life out like you can out of an x kWh li-ion pack, you need to limit DoD to 70%, and then upsize the lead acid pack to 2.5x kWh for the same usable storage. wanting 10kWh of stored power but having to buy 25kWh of storage to get it is not economically viable.
http://www.batterypoweronline.com/wp-content/uploads/2012/07/Lead-acid-white-paper.pdf
attachment.php
 

Attachments

  • complife.jpg
    complife.jpg
    18.9 KB · Views: 43

u3b3rg33k

Well-known member
Joined
Dec 18, 2017
Messages
4,087
Actually 6-8000 times if only discharged 20%, a solid 3-4000 times at 30% discharge at least the ones we use in the light towers...They use AGM batteries,.

BTW, my batteries are just about free...

Free batteries turns the numbers on their heads. makes things way more economical. Btw those Li-ion prices are out of date in the article i linked above - numbers are from 2010 or older. they're much cheaper per kWh now.
 

HOTFR8

Banned
Joined
Mar 2, 2007
Messages
24,498
Location
Castlemaine, Victoria. The Hot Rod Centre of Austr
I'd be switching from one source to the other at times when I exceed capacity for an extended time...

Not if you designed it to carry the load you require. For example my small stand alone system has two 80 watt panels two 6 volt batteries and an invertor.
It runs my computer (includes printer, scanner, router and modem), phones, fax, answer machine and also has a few lights on the system as well. To back it up I have a battery tender plugged into the mains power. I have a power inlet on the wall with a short lead from the invertor to that plug and the office has its own power points all on the dedicated system. To do it properly in any way you need to spend some money so it works as it should.

The risk you have with the switch would be cooking batteries when the power is not being used from them and it is isolated.

I had no idea this thread would go so far off...If the MOD would, please delete it before I get banned.
I see no reason for you to be banned.
 
Last edited: