A friend needs some help tracing a circuit from a receptacle to the breaker panel. The receptacle has no power and none of the the breaker are tripped, how should we proceed?
A friend needs some help tracing a circuit from a receptacle to the breaker panel. The receptacle has no power and none of the the breaker are tripped, how should we proceed?
+1 the circuit tracer I have is inaccurate also. I get false readings (multiple breakers hit on the trace) or no readings all the time in a panel..
Ok, will try that. Even with the main off?
We turned all the circuit off and the main, then turned each one on and checked for continuity. Only one toned with the mm. I then removed the circuit breaker and tested it, it was bad and now it works? I replaced the breaker and still no power to the plug, all the neutrals and grounds are on the same grounding bar.
To check the ground and neutral wire I'd need to remove all the wires from the ground bar and check one at a time?
--> I do it that way since I wanted to identify which neutral is for which circuit...
............
Capped the old circuit and ran a new one, everything works now.