... for four #6 wires. One "source" said 1½". That looks HUGE to me ! Looks like 1" or maybe 1¼".

What do the experts say ?
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,279
Location
Modesto, CA
Agree with sberry-

Why 4 #6s?

If one is an EGC, it most likely can be reduced.

But that all depends on size of breaker and whether unhrounded conductors were upsized.
 

teamextreme

Well-known member
Joined
Aug 10, 2013
Messages
867
Location
Lakewood, CO
But if you really do need 4 #6's, then PoorOwner is correct, 3/4" will fit it. If it's a long run, and/or close to 360 deg of bend, you might consider upsizing to 1".
 

ichabod

Well-known member
Joined
Oct 18, 2013
Messages
444
Location
minnesota
the type of conduit and type of wire used will have a say in proper sizing.

chapter 9 tables will give the minimum size conduit for wire size and type of conduit.
 
OP
T

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,670
Location
SE MI
Gee wiz guys, am trying to make it easy !

Okay, you are correct, there are THREE #6 THHN and ONE #8 THHN. Total area of the wire is (according to Table 15.1.3) is 0.1887 sq in. We are using PVC conduit, assuming Type A.

1.0" PVC Conduit (assuming Type A) allow 0.434 sq in for a 40% fill rate. I don't understand how to use the other charts regarding temperature rise, but assume that the load is 50A CONTINUOUS (hot tub).
 
To avoid these ads, REGISTER NOW!

TRWham

Well-known member
Joined
Aug 11, 2017
Messages
2,021
Location
East Cobb County, Georgia
Gee wiz guys, am trying to make it easy !

Okay, you are correct, there are THREE #6 THHN and ONE #8 THHN. Total area of the wire is (according to Table 15.1.3) is 0.1887 sq in. We are using PVC conduit, assuming Type A.

1.0" PVC Conduit (assuming Type A) allow 0.434 sq in for a 40% fill rate. I don't understand how to use the other charts regarding temperature rise, but assume that the load is 50A CONTINUOUS (hot tub).

If this is running outdoors or in a wet location you'll need THWN.
 

ichabod

Well-known member
Joined
Oct 18, 2013
Messages
444
Location
minnesota
according to chapter 9 table c.12 you can run 5 #6 THHN / THWN in a 3/4 ridged PVC conduit.

if it is underground or outdoors it will be required to be THWN, but most THHN is dual rated for THWN as mentioned above post.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,596
Location
Fullerton, CA
If the circuit is 60 Amps or less you can run a #10 ground instead of #8.
(Edit: unless your talking aluminum rather than copper)
 