... for four #6 wires. One "source" said 1½". That looks HUGE to me ! Looks like 1" or maybe 1¼".
What do the experts say ?
What do the experts say ?
Gee wiz guys, am trying to make it easy !
Okay, you are correct, there are THREE #6 THHN and ONE #8 THHN. Total area of the wire is (according to Table 15.1.3) is 0.1887 sq in. We are using PVC conduit, assuming Type A.
1.0" PVC Conduit (assuming Type A) allow 0.434 sq in for a 40% fill rate. I don't understand how to use the other charts regarding temperature rise, but assume that the load is 50A CONTINUOUS (hot tub).
If this is running outdoors or in a wet location you'll need THWN.
Almost all THHN is dual rated. (I've never used any thhn-2 that's not.)
Concur ! I never seen any that is not.Almost all THHN is dual rated. (I've never used any thhn-2 that's not.)