Hey fellas!
I'm going to pick up an A/C unit for the garage.. think i found the one I want:
https://www.appliancesconnection.com/lg-lw1816er.html?ref=TRJC
Electrical Requirements
Volts: 230/208 Volts
Frequency: 60 Hz.
Amps: 15 Amps
Rated Amps: 7.5 Amps
I currently have an unused 240 line in the garage with a 20A breaker (2 pole) which I planned on using for the A/C unit. Will this be alright? I'm not too sure on the "Amps vs. Rated amps" specs above. Are they listing "Amps" as Full Load Amps?
What size breaker do you guys suggest? Seeing as it's 20A in there currently, I assume the wiring is 12 awg.
Here's a pic of the breaker - I have no idea where all those labels are from, lol
Thanks in advance!