Y2KFirehawk
Active member
Almighty garage warriors! I come to you to draw upon of your great garage building electrical knowledge.
Long story short, I am building a 24x28 detached two car garage about 15' from my house. From an electrical load perspective, I am looking at...
So the rub... The house currently has 200A service that is pretty well utilized after we finished our basement.
In speaking to a field technician from my local power provider (PPL) they mentioned about adding a second meter socket to the house, utilizing the existing underground feeder. (Permitting my proposed additional amperage load is acceptable and not needing to increase the wire size of the feeder)
For 100A service, does that make sense to you or would adding a 100A breaker to the existing 200A panel make sense?
Thank you in advance!
Long story short, I am building a 24x28 detached two car garage about 15' from my house. From an electrical load perspective, I am looking at...
- Two 15A lighting circuits
- Two 20A wall outlet circuits
- One 240VAC 22A circuit for Air Compressor
- One 220VAC 25A for 2-post lift
- One 240VAC 30A for welder
So the rub... The house currently has 200A service that is pretty well utilized after we finished our basement.
In speaking to a field technician from my local power provider (PPL) they mentioned about adding a second meter socket to the house, utilizing the existing underground feeder. (Permitting my proposed additional amperage load is acceptable and not needing to increase the wire size of the feeder)
For 100A service, does that make sense to you or would adding a 100A breaker to the existing 200A panel make sense?
Thank you in advance!