Planning electrical service for my garage that I'm currently building. Planning to run 1/0-1/0-1/0-4 Aluminum MHF fed from my main panel inside house. Total run is about 150'. About 10' of that will be inside my house, so obviously I cant run the MHF inside. Is it possible to transition from the MHF to SER inside a 2'' LB? Will it physically fit? Split bolts? Polaris connectors?
Other option I have considered is a dual lug meter base so I don't have to enter the house at all, but Im having trouble locating a 200 amp base with an extra set of lugs?