I got my in-slab radiant heat system in my garage up and running about 3 weeks ago and have some questions on what would be considered normal operation and on some settings.
The garage is 40X64X16 pole barn. I have 2" Foamular 250 R10 under the slab and along the sides of the slab extending down 8" below the bottom of the insulation under the slab. The slab is 6" thick. I have 8 loops of 1/2" barrier pex tied to the bottom of the rebar with the rebar on 3" stands. The loops are 285 ft on the shortest and 290ft on the longest loop. The loops are on 12 " spacing with the exception of in the center part of the floor they are a little wider. All 8 loops are connected to one manifold for 1 zone through out the build (no offices or rooms). I contacted Hydro-Smart with my build specs and they recommended their HSPS120LT pump panel with a primary and secondary pumps and the the Hydro-Smart 115 micro boiler (LP gas). So that is what I got. The thermostat is an Aube TH114-AF-024T which has the floor sensor. I have tube ran in the floor for the sensor to go into and that is were the sensor is located. The walls are covered in 3"+ of closed cell foam. Ceiling has R50 blow-in. I have 3 overhead doors 2 are 10x10 and 1 is 12x14. All 3 are 2" insulated & bonded commercial doors.
Heating system - I have the thermostat set on floor only, no air temp. I have the temp set a 50'F. It will stay of 50' and sometimes even hit 51' I used my inferred heat gun and the floor temp shows about 54 in the warmest to 50 at the coolest spot which is where the thermostat sensor should be located. The boiler runs what I consider a lot. I have an hour meter connected to the pumps on the panel so I can see how much it did run. It will run for a short while and off for few minutes and back on again. Even with the Thermostat is set on 50 and the temp is 50, I have seen the boiler run when it showed 51 on the thermostat. Is this normal for a radiant system to do that??
Settings - The boiler can be set from 99'F to 122'F. At first I had it set on 120' but after reading different post on the web I backed it down to 100'. Both primary and secondary pumps have 3 settings low, med. hi. I have the primary set on hi, and played around with the secondary pump settings. With the secondary pump on low, I have about .4 gpm flow rate (according to indicators on manifold) and about 28' difference in drop in temperature from inlet to return. Inlet about 80' with return coming back at 52. With secondary on med. I get about a 22' difference between inlet and return temps. Flow is about .6 gpm. Inlet was showing about 76' and return about 54'. With the secondary pump on hi get flow rate of about .8 gpm but don't remember what the temp drop from inlet to return was, but the inlet was a several degrees cooler. Seems like a waste of heating the water up, and mixing cool water with it to go through the loops. Any suggestions on what temp the boiler should be on and pump settings?? Why would it be running with the thermostat set on 50 and temp showing 50' to 51'??
The garage is 40X64X16 pole barn. I have 2" Foamular 250 R10 under the slab and along the sides of the slab extending down 8" below the bottom of the insulation under the slab. The slab is 6" thick. I have 8 loops of 1/2" barrier pex tied to the bottom of the rebar with the rebar on 3" stands. The loops are 285 ft on the shortest and 290ft on the longest loop. The loops are on 12 " spacing with the exception of in the center part of the floor they are a little wider. All 8 loops are connected to one manifold for 1 zone through out the build (no offices or rooms). I contacted Hydro-Smart with my build specs and they recommended their HSPS120LT pump panel with a primary and secondary pumps and the the Hydro-Smart 115 micro boiler (LP gas). So that is what I got. The thermostat is an Aube TH114-AF-024T which has the floor sensor. I have tube ran in the floor for the sensor to go into and that is were the sensor is located. The walls are covered in 3"+ of closed cell foam. Ceiling has R50 blow-in. I have 3 overhead doors 2 are 10x10 and 1 is 12x14. All 3 are 2" insulated & bonded commercial doors.
Heating system - I have the thermostat set on floor only, no air temp. I have the temp set a 50'F. It will stay of 50' and sometimes even hit 51' I used my inferred heat gun and the floor temp shows about 54 in the warmest to 50 at the coolest spot which is where the thermostat sensor should be located. The boiler runs what I consider a lot. I have an hour meter connected to the pumps on the panel so I can see how much it did run. It will run for a short while and off for few minutes and back on again. Even with the Thermostat is set on 50 and the temp is 50, I have seen the boiler run when it showed 51 on the thermostat. Is this normal for a radiant system to do that??
Settings - The boiler can be set from 99'F to 122'F. At first I had it set on 120' but after reading different post on the web I backed it down to 100'. Both primary and secondary pumps have 3 settings low, med. hi. I have the primary set on hi, and played around with the secondary pump settings. With the secondary pump on low, I have about .4 gpm flow rate (according to indicators on manifold) and about 28' difference in drop in temperature from inlet to return. Inlet about 80' with return coming back at 52. With secondary on med. I get about a 22' difference between inlet and return temps. Flow is about .6 gpm. Inlet was showing about 76' and return about 54'. With the secondary pump on hi get flow rate of about .8 gpm but don't remember what the temp drop from inlet to return was, but the inlet was a several degrees cooler. Seems like a waste of heating the water up, and mixing cool water with it to go through the loops. Any suggestions on what temp the boiler should be on and pump settings?? Why would it be running with the thermostat set on 50 and temp showing 50' to 51'??