Big Maxx 50000 install questions
kdt1970
Utah
So my kids got me a heater for my attached garage for Christmas. I can do the install work easily. I am just not so great at the math. I need to figure out the gas line sizing so I can run it. I have 1 inch lines and my meter is 5psi at 250 qfph. I dont know if I need to run 1 inch to the heater or if smaller is good. The distance is approx 22 feet from the tee in my house with approx 4 90 degree corners. I have a gas water heater, furnace, dryer and stove. Any help I can get would be great.
K
kdt1970
Utah
22 feet is all?
Yes, I need 7 feet on way a 90 turn 7 feet out to garage, 90 turn then about 8 feet up the wall to heater. That is from the tee above my house heater. It about 12 to15 feet from the tee to the gas meter.
das_V8
Columbus, OH
Just went through this process myself. Look on your water heater, furnace and dryer labels for BTU input rating and report back. What kind of stove (simple 4 burner, or 6 burner double oven, etc)? What size is your line coming into the house? If you google gas pipe calcs you can find simple tutorials on how to calculate your line sizes and ensure you have adequate capacity.
D45
NW INDIANA
I ran 3/4" for a 70 foot run for my 75k, so could only GUESS that 1/2" would be enough for a 50k
das_V8
Columbus, OH
You sure it is 5psi or 0.5" WC? My understanding is most standard residential meters are 0.5" WC at 250 cubic feet of gas per hour at under 2psi inlet.
At that assumed rate, and per the 2015 IFGC, a 30' run (round up from 22') of 1/2" will allow for 95 cf/h (~97k BTU).
But the real question is if your house can supply enough gas to your other appliances and the heater if you tap into the main line.
K
kdt1970
Utah
My meter says MAOP 5 PSI...250 C.F.H. @ 1/2 DIFF.
My water heater is 40000 BTU
I will need to look at the other appliances tonight.
My Main line coming into the house and up to the point I will Tee it is 1 inch.
das_V8
Columbus, OH
Thanks for confirming, I'm going to duck out of this now as I admit-tingly have no knowledge of what I would presume a "high pressure" setup? I'm curious though so following along.
I would assume you have enough capacity though, I did it with a 1" main line supporting 80k furnace, 75k water heater, 60k stove and my (new) 45k shop heater. I tapped into my 1" line and ran 60' of 3/4" to 1/2". But you should still run your calcs to confirm.
Showkey
"MEMBER EMERITUS"
Wausau WI
The 195,000 BTU tankless NG water heater are where the meter size often becomes an issue.
K
kdt1970
Utah
Ok so first in line stove, 16500 btu, 1/2 inch tee'd from main line (1 inch). Next is house furnace 90000 btu, 1/2 inch tee'd from main line. Next is water heater 40000 btu, 1/2 inch tee'd from main line. Next is dryer 20000 btu, 1/2 inch tee'd from main line. Garage heater will get tee'd in between dryer and water heater.
K
kdt1970
Utah
K
kdt1970
Utah
So with this sizing chart, it is saying minimum 1/2 inch. Would I be ok to run 1 inch for the two 7 foot legs and then 1/2 inch the last 8 feet to the heater? There will be three 90 degree corners in the first 7 feet, as I need to bump out around a header over my stairs.
pbon
I am installing one now. I am pretty sure it’s 1/2 and that is what I am using for about 30’ of piping.
K
kdt1970
Utah
Ya, I decided on 3/4 for the run then I'll reduce to 1/2 were the shut of valve will go the last 1 to 2 feet. I have all my holes drilled and have mounted my super struts to my rafters. Now the hard part of getting the heater in place. The gas and electric will be the easy part. I will most likely hire someone to do the venting through my roof. I just don't feel comfortable doing that part.
D45
NW INDIANA
Looks close to the wall.......
With the draft hood and a 90° angle, going to be pretty close I would guess
K
kdt1970
Utah
It is 18 inches from the back wall. If I have to I can come out another 12 inches for 30 inches away.
pbon
18” probably won’t get you the 5’ you need for vertical vent with the typical stainless vent kit that comes with 1 45 degree.
K
kdt1970
Utah
It is located near the ridge line in my attic. It is an attached garage it actually has a huge attic. It is around 8 to 9 feet high at the ridge.
pbon
You are right. I meant horizontal vent. Horizontal took some trial and error for me to work with the stainless vent kit. Vertical is much easier and cheaper.
D45
NW INDIANA
Ah ok, the draft hood will add length and then depending if you use a elbow or a clean-out T
Draft hood connector with elbow:
D45
NW INDIANA
Don't you need a drip leg before the connection at, near, or around the heater?
K
kdt1970
Utah
After doing some reading, I will be adding the correct sediment trap up on top near the heater shut off valve. Parts are only 10 dollars.
K
kdt1970
Utah
You can do it!!
Here's my trap on my install, and then the vent work.
1 video on heater installs by this dude:
and I was on my way.
From my adapter, to 90 to 5ft piece. it was all easy.
I really want to, really bad. I am just so worried about making my roof leak.
D45
NW INDIANA
Looks great
Install the vent yourself, it's easy
I did it myself and it doesn't leak
D45
NW INDIANA
Connect the draft hood and the elbow or T vent
Hang a plomb from the ceiling to the center of the vent hole opening and mark it
Use a drill bit and then a hole saw
I have a good install thread of my heater install, from start to finish
It's easy for the vent, and I've never done this before
Pruittx2
Points to middle of right palm, Michigan
Super easy,, just like that video shows,, mount unit,, mark roof,, I used a heat gun, to soften the shingles to work with them,, cut, mark,, drill,, jig saw,, Viola!
I used this boot that some questioned, but it's a self sealing, B-vent safe piece that worked good, installed easy, and is leak free.
I searched the codes for all work in my area,, then did it all, Ran gas line, 20a dedicated circuit, safety switch, thermostat, hung unit, and did all vent work.
When the Propane guy came, he complimented my workmanship, then hooked up gas, leak tested all pipes and did first fire up, then adjusted flow rate and pressures.
Saved hundreds on install labor costs, learned a bit,, and have the satisfaction of a job well done.
D45
NW INDIANA
I would say you save more than hundreds
Some people pay $2000-$3500 for the heater and install
I think my total cost was under $800