Well-known member
Hi all. Trying to do some long term planning before I put in some garage heaters here in NW Ohio.
Space is a 24x24x8 with hip roof. Partial lofts.
Currently completely uninsulated.
I have already 1 240V/20A circut with plug for my lift or whatever else I need to run for now. Wired with 12-2. The 240
I am looking to add:
-Heaters (2x 5kw)
-Insulation
-Larger Welder/Plasma
Current situation:
Garage Wiring (CURRENT)
240V @ 20A
12-2 Wire
Garage 240 (CURRENT)
240V @20A
12-2 Wire
Usage:
Lift
240v
15A peak draw
Heaters
2x @ 5kW
21.6Amp Draw
Constant - Full time winter
Welder
240V @ 40A
Heaters will most likely run in conjunction with welder or lift for 4/mos of the year.
Based on this I am thinking I will need to set up my 240v on 60A breakers with either 6-3 or 8-3 wire correct?