240V Wiring Questions - Wire Gauge
countrybumpkin
Cherry Valley IL
Hi all. Trying to do some long term planning before I put in some garage heaters here in NW Ohio.
Space is a 24x24x8 with hip roof. Partial lofts.
Currently completely uninsulated.
I have already 1 240V/20A circut with plug for my lift or whatever else I need to run for now. Wired with 12-2. The 240
I am looking to add:
-Heaters (2x 5kw)
-Insulation
-Larger Welder/Plasma
Current situation:
Garage Wiring (CURRENT)
240V @ 20A
12-2 Wire
Garage 240 (CURRENT)
240V @20A
12-2 Wire
Usage:
Lift
240v
15A peak draw
Heaters
2x @ 5kW
21.6Amp Draw
Constant - Full time winter
Welder
240V @ 40A
Heaters will most likely run in conjunction with welder or lift for 4/mos of the year.
Based on this I am thinking I will need to set up my 240v on 60A breakers with either 6-3 or 8-3 wire correct?
C
countrybumpkin
Cherry Valley IL
pattenp - Yes.
wyliesdiesels - Detached.
The garage sub panel is routed with ~15ft or wiring from the main panel in the house.
Both the house and the sub are using 20A 12g.
I will have to upgrade both.
dcg9381
Austin, TX
6/3 copper @ 60A would get it done.
Might look at 2/2/2/4 AL wire, probably costs less/same - capable of 90A.
Main difference is pain-in-the-*** to pull, so it depends on your conduit size.
6/3 can be pulled thru as small as 3/4" (1" recommended).
2/2/2/4, 1 1/4" or larger.
6/3 as in UF-b? good luck pulling that through 3/4"... :lol:
pattenp
Virginia - USA
I believe it will take 1" or even 1.25" conduit to meet the fill requirement for a single cable of 6/3 UF-b.
Edit: After looking a the wide dimension of 6/3 UF it may take 1.5" conduit.
Im not gonna even bother calcing that.
It would be foolish to pull such cable through conduit when there are easier materials to do so.
strutaeng
Dallas, TX
I would just pull a larger wire. 6 gauge seems light for running the heaters and welder or plasma. What most here recommend is Al wiring with a subpanel.
Also, you didn't include an air compressor. Plasma cutters need something like 5-6 CFM, so throw a another decent load to the mix.
#2 Al in conduit will get you plenty of juice.
dogdog
why would op needed to put UF-b inside a conduit, if he already have conduit, regular THHN or THWN would fit fine... I think I fit 4 or was it 3 #6 THHN inside a 1" emt not an issue at all