Any PROs see a problem with this picture?

maplepuck

Active member
Joined
Feb 15, 2018
Messages
33
Location
Southern Oregon
I am wanting to add a few additional outlets 120s and 240s, and one for a welder in my garage...
I went to determine my service amperage...and noticed no main shut off. (and no more room) so a new load center is in the future methinks.
the other side of the wall, just the meter.

I'm obviously going to have to pull a permit and have the PoCo perform a proper shut off for me to upgrade...
Question: despite my meager knowledge and ability; i would normally be apt to change the box on my own, but given the facts; should I hire a pro? and what can i expect in pitfalls? e.g. additional costs, actions, etc.

thanks for looking
D
 

Attachments

  • breakerbox.jpg
    breakerbox.jpg
    136.4 KB · Views: 557
  • meter.jpg
    meter.jpg
    73.2 KB · Views: 245
To avoid these ads, REGISTER NOW!

oledude1952

Well-known member
Joined
Jan 20, 2019
Messages
69
Location
KY
Really odd how that service passed inspection with no main breaker in the breaker box OR a main disconnect after the meter also....So really a pro needs to access the situation for you and this will need to be fixed. .

The breaker box looks like it is a 24 circuit unit. And the main service conductors feeding it looks in the pic, like they MAY be 2/0 copper conductors.

So you may get away with just changing the breaker box to a 200 amp / 40 circuit box with a main and re-using the service conductors .. MAYBE... .

Good Luck and JMO.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,735
Location
NW Iowa
It's a split buss panel. Top 6 double pole breakers are all mains, third one down on the left turns off the lower "lighting"section of the panel.

Must have quite a few 240V loads in the house already?
 
Last edited:

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,951
Location
NJ
it appears there are some neutrals going to breakers

they are all connected to 2 pole cb's - so 240vac ckts. Old enough where re-identifying whites was not required.

They would be re-identified during service upgrade.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,951
Location
NJ
Really odd how that service passed inspection with no main breaker in the breaker box OR a main disconnect after the meter also....So really a pro needs to access the situation for you and this will need to be fixed. .

The breaker box looks like it is a 24 circuit unit. And the main service conductors feeding it looks in the pic, like they MAY be 2/0 copper conductors.

So you may get away with just changing the breaker box to a 200 amp / 40 circuit box with a main and re-using the service conductors .. MAYBE... .

Good Luck and JMO.

It's a split buss panel as Bert stated. Telling tale is the 2 black conductors from the cb mentioned to the connections on the bottom of bottom panel buss.

6 throws of hand is considered a legal disconnect which the top 3 cb's left and 3 right provide.

Would need to check loads to be sure, but it looks as you thought: change box to 200 amp main / 40 circuit will work.

Probably just needs 2 additional grd rods.
 
OP
M

maplepuck

Active member
Joined
Feb 15, 2018
Messages
33
Location
Southern Oregon
It's a split buss panel. Top 6 double pole breakers are all mains, third one down on the left turns off the lower "lighting"section of the panel.

Must have quite a few 240V loads in the house already?

good eye, and thanks for the straightening out. everything electric in this 1980 bungalow...the only natural gas is from me and the dog...cant get anything to run on that except for the females in the house :)
 

oledude1952

Well-known member
Joined
Jan 20, 2019
Messages
69
Location
KY
You guys have some good some ZOOM on your PC's to see the pics of the breakers that well. :) Good call....
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,180
Location
SE MI
It's a split buss panel. Top 6 double pole breakers are all mains, third one down on the left turns off the lower "lighting"section of the panel.
Why does such a panel even exist ?

Must have quite a few 240V loads in the house already?
There are 7, not including the one that feed the "lighting" section. 2 of them are in the lighting section.
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,180
Location
SE MI
I'm obviously going to have to pull a permit and have the PoCo perform a proper shut off for me to upgrade...
Depends on your location. Does the PoCo require an inspector to sign off ?

Question: despite my meager knowledge and ability; i would normally be apt to change the box on my own, but given the facts; should I hire a pro? and what can i expect in pitfalls? e.g. additional costs, actions, etc.

I think Henry Ford said, "Whether you think you can or think you can't, you are probably right !"

Any new box will require a ground bar and that ground bar will have to be properly connected to a properly installed ground rod. This could be a DIY job, IF YOU ARE COMFORTABLE ! A pro would knock it out in under 4 hours, assuming no problems installed the ground rod(s).

Hint, the new box will be longer. You CAN mounted sideways if you want and then the wires will likely reach all of the breakers. If you want it mounted vertical, some of the wires might not be long enough. It is legal to splice on a "pigtail" inside of the box using an appropriate connector !
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,180
Location
SE MI
it appears there are some neutrals going to breakers

Time to get new glasses ! Those are 240V loads so black is L1 and white is L2. Use of a white insulated conductor is allowed if it "Romex" type cable. Not a bad idea to use a red Sharpie or a piece of red tape on those wires for all of us "apprentices" !
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,951
Location
NJ
Depends on your location. Does the PoCo require an inspector to sign off ?



I think Henry Ford said, "Whether you think you can or think you can't, you are probably right !"

Any new box will require a ground bar and that ground bar will have to be properly connected to a properly installed ground rod. This could be a DIY job, IF YOU ARE COMFORTABLE ! A pro would knock it out in under 4 hours, assuming no problems installed the ground rod(s).

Hint, the new box will be longer. You CAN mounted sideways if you want and then the wires will likely reach all of the breakers. If you want it mounted vertical, some of the wires might not be long enough. It is legal to splice on a "pigtail" inside of the box using an appropriate connector !

The main service panel can have grds and neutrals on the neutral bar. A dedicated grd bar not necessary but nothing prohibiting it.

The grounding electrode conductor is to connect the service neutral block to earth.

As long as height of new main cb is below 6'7", panel can be raised up to gain more free conductor length in panel.

Most panels in US can not be mounted horizontally. Breakers must not be able to be turned on in the downward direction.
 

dscheidt

Well-known member
Joined
Apr 26, 2017
Messages
2,894
Why does such a panel even exist ?
.

Split bus panels are no longer made. They were used because a main breaker is expensive, and throwing a few breakers isn't that hard. They're confusing, and don't make much sense given a main breaker is now pretty cheap.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,735
Location
NW Iowa
Why does such a panel even exist ?

Breakers bigger than 60A were much more expensive. A 200A breaker would have more than doubled the price of a panel. A split buss panel really isn't a bad design. Less parts and connections that could fail.

There are 7, not including the one that feed the "lighting" section. 2 of them are in the lighting section.

It's obvious there are (7) double pole breakers. I was wondering if they are all actually being used.
 

ford33

Well-known member
Joined
Feb 26, 2011
Messages
2,118
Location
Chicago, IL. USA
I learned something new today. I never heard of a split bus panel or knew how it would work. Thanks, for sharing.
 
To avoid these ads, REGISTER NOW!

checkthisout

Well-known member
Joined
Sep 5, 2008
Messages
5,232
I am wanting to add a few additional outlets 120s and 240s, and one for a welder in my garage...
I went to determine my service amperage...and noticed no main shut off. (and no more room) so a new load center is in the future methinks.
the other side of the wall, just the meter.

I'm obviously going to have to pull a permit and have the PoCo perform a proper shut off for me to upgrade...
Question: despite my meager knowledge and ability; i would normally be apt to change the box on my own, but given the facts; should I hire a pro? and what can i expect in pitfalls? e.g. additional costs, actions, etc.

thanks for looking
D

You have room. Just convert those breakers on the bottom there that are singles but taking up two spaces into doubles.

The 4 singles on the right can be grouped into two spaces freeing up 2 spaces for a 240V or one 240 and 2 120V.

The two breakers in the lower left can be changed to doubles allowing you to add two 120V circuits or one 240V circuit.
 
Last edited:

Miss the Pontiacs

Well-known member
Joined
Nov 7, 2016
Messages
16,475
Location
Saskatchewan Canada
You have room. Just convert those breakers on the bottom there that are singles but taking up two spaces into doubles.

The 4 singles on the right can be grouped into two spaces freeing up 2 spaces for a 240V or one 240 and 2 120V.

The two breakers in the lower left can be changed to doubles allowing you to add two 120V circuits or one 240V circuit.

Good catch:beer:
At the lake I used some Square D 15 amp single pole double throw breakers. So now I have an abundance of 15 amp standard SD breakers to spare. I don’t know what the OP’s breakers are maybe his manufacturer has a similar option.
 

Attachments

  • C7F4C310-3F94-4A26-87A4-170CCFB30F02.jpeg
    C7F4C310-3F94-4A26-87A4-170CCFB30F02.jpeg
    17.5 KB · Views: 12
OP
M

maplepuck

Active member
Joined
Feb 15, 2018
Messages
33
Location
Southern Oregon
Good catch:beer:
At the lake I used some Square D 15 amp single pole double throw breakers. So now I have an abundance of 15 amp standard SD breakers to spare. I don’t know what the OP’s breakers are maybe his manufacturer has a similar option.

the box is a bryant; haven't pulled the breakers yet. i will look into compatible single pole double throw breakers.
thank you
 

TRWham

Well-known member
Joined
Aug 11, 2017
Messages
1,961
Location
East Cobb County, Georgia
Cutler-Hammer BR breakers are classified for use in at least some Bryant panels. I would check into that. Be careful adding loads down in the lighting section. You might push the limit of the breaker and conductors feeding it.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,735
Location
NW Iowa
Be careful adding loads down in the lighting section. You might push the limit of the breaker and conductors feeding it.

This^
The lighting section is probably fed with a 60A breaker. Large loads should be in the "main" section. No tandems are allowed up there though since you can have no more than 6 breakers up there.

Looks like someone already ran a 50a circuit from the lighting section, not that great...
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,951
Location
NJ
Op, need a good picture of the panel label. It shows accessories details, # circuit permitted, wire sizes, etc.

This panel may or may not be able to use twins or only a certain qty in specific positions.

Personally, I would change it out to have more space available for future, 1 main cb, no worry of overloading lighting buss/breaker.
 

Jim greengo

Well-known member
Joined
Sep 3, 2018
Messages
7,415
Location
Behind my house
Really odd how that service passed inspection with no main breaker in the breaker box OR a main disconnect after the meter also....So really a pro needs to access the situation for you and this will need to be fixed. .

The breaker box looks like it is a 24 circuit unit. And the main service conductors feeding it looks in the pic, like they MAY be 2/0 copper conductors.

So you may get away with just changing the breaker box to a 200 amp / 40 circuit box with a main and re-using the service conductors .. MAYBE... .

Good Luck and JMO.

Looks like split buss.
 

Jim greengo

Well-known member
Joined
Sep 3, 2018
Messages
7,415
Location
Behind my house
Depends on your location. Does the PoCo require an inspector to sign off ?



I think Henry Ford said, "Whether you think you can or think you can't, you are probably right !"

Any new box will require a ground bar and that ground bar will have to be properly connected to a properly installed ground rod. This could be a DIY job, IF YOU ARE COMFORTABLE ! A pro would knock it out in under 4 hours, assuming no problems installed the ground rod(s).

Hint, the new box will be longer. You CAN mounted sideways if you want and then the wires will likely reach all of the breakers. If you want it mounted vertical, some of the wires might not be long enough. It is legal to splice on a "pigtail" inside of the box using an appropriate connector !

You're thinking of a sub panel
 

rburke65

Well-known member
Joined
Nov 10, 2007
Messages
12,349
Location
Canfield, Ohio
When I was rowing houses, there was no code to tape up the 240v two conductor Rome’s with black tape so this my have been an older install.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,759
Depends on your location. Does the PoCo require an inspector to sign off ?



I think Henry Ford said, "Whether you think you can or think you can't, you are probably right !"

Any new box will require a ground bar and that ground bar will have to be properly connected to a properly installed ground rod. This could be a DIY job, IF YOU ARE COMFORTABLE ! A pro would knock it out in under 4 hours, assuming no problems installed the ground rod(s).

Hint, the new box will be longer. You CAN mounted sideways if you want and then the wires will likely reach all of the breakers. If you want it mounted vertical, some of the wires might not be long enough. It is legal to splice on a "pigtail" inside of the box using an appropriate connector !


It is not code compliant under the NEC to mount a panel horizontally as when a breaker is mounted vertically, ON must be up, a horizontal panel will have 1 row with ON being down, it is allowed in Canada though. See NEC Art. 240.81.
 

Jim greengo

Well-known member
Joined
Sep 3, 2018
Messages
7,415
Location
Behind my house
The main service panel can have grds and neutrals on the neutral bar. A dedicated grd bar not necessary but nothing prohibiting it.

The grounding electrode conductor is to connect the service neutral block to earth.

As long as height of new main cb is below 6'7", panel can be raised up to gain more free conductor length in panel.

Most panels in US can not be mounted horizontally. Breakers must not be able to be turned on in the downward direction.

Not all factory installed main breakers break/reset horizontally.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,735
Location
NW Iowa
If a breaker is vertical, then off must be down. If the breaker is horizontal then it does not matter. This applies to all breakers, not just the main.
 