Upgrading 200amp service to 400 amp

TTMotorsports

Well-known member
Joined
Jan 8, 2019
Messages
1,107
Location
Lucerne Valley, CA
So I'm upgrading my current service from 200 amp to 400amp so I can run 200amp sub panel in my new shop. The electrician that just checked out the job sent me a overpriced quote in my opinion and from what others have quoted over the phone. The existing panel and breakers are all in 100% working order. He said I need The panel, the larger riser , all new breakers/ 2nd 200 amp breaker has to be installed now. As well as all New water /gas bond/ground rods.

Would changing panel to 400 amp service really require changing all water and gas bond as well as new ground rods? That alone was almost $600.

Also current breakers are standard square d so why quoting new breakers at a tune of $400 plus $220 for 200 amp breaker for sub panel


Also why would the 200 amp subpanel breaker need to be installed when the panel is swapped out?

I'm no professional but I've done quite a bit of electrical work before but never a panel upgrade. I'm waiting on 3 more quotes to see what they say as well but they all said they will reuse breakers and existing wiring from meter to panel.
 
To avoid these ads, REGISTER NOW!

Stuart in MN

Well-known member
Joined
Sep 8, 2005
Messages
23,135
Location
Minneapolis
He may be including those things as a liability issue - no electrician wants to have callbacks after the project is done, so by replacing everything now he knows there aren't any old or deteriorated components that may come back to haunt him later.

It's not what you're asking, but are you sure you need a 400 amp service and a 200 amp sub? Have you done a load calculation? I'm not saying you don't need one, just that it's a good idea to make sure before spending a lot of money. Unless you have a lot of high powered equipment that's all running at the same time it may not be necessary.
 
OP
T

TTMotorsports

Well-known member
Joined
Jan 8, 2019
Messages
1,107
Location
Lucerne Valley, CA
2 5 ton ac units. 15hp rotary converter. 10hp compressor. Cnc plasma cutter. 2 lifts. 3 welding stations and a powder coating oven. If I have oven on cnc cutter going. Compressor and ac units I'm at well over 100amps not counting lighting computers etc.

The shop is 4000 sq ft welding and fabrication shop.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,031
Location
Modesto, CA
Is this a one man shop?

Have you checked with your PoCo about that 10HP motor? Many PoCos have limits on motor hp size...
 

gungatim

Well-known member
Joined
Jan 8, 2013
Messages
8,101
Location
west mich
around here it was drastically cheaper to have the poco run a seperate line from the pole to a 2nd meter on the outbuilding to run 200amp. it's an extra monthly bill, and I forget if the rate was cheaper or a little more expensive but saved thousands when we did my FIL's 50x100 shop a few years back.
 
OP
T

TTMotorsports

Well-known member
Joined
Jan 8, 2019
Messages
1,107
Location
Lucerne Valley, CA
I tried to get a second meter but county wont let you have 2 meters on my lot so I'm stuck doing it this way. If I could get a second meter would save me close to 5 grand.

Usually 2 sometime 3 guys working at once.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,031
Location
Modesto, CA
I tried to get a second meter but county wont let you have 2 meters on my lot so I'm stuck doing it this way. If I could get a second meter would save me close to 5 grand.

Usually 2 sometime 3 guys working at once.

It may save you on the front end but meter fees add up over time.
 

analog

Member
Joined
Nov 27, 2017
Messages
21
Location
Central Oregon
I recently did this upgrade at my house. Electrician drove two new ground rods and the inspector checked to ensure they were there, too. I didn't discuss why he did it, though. I can't comment on the rest of your questions, since my service comes in through an outside meter base separate from the house panel. He did not have to touch the house panel.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,643
Location
Richmond, VA
Unless the electrician installed the existing rods, how does he know they meet code? I would expect the quote to include that.

How old are the existing breakers? They don't last forever.
 

dcg9381

Well-known member
Joined
Jun 20, 2018
Messages
11,778
Location
Austin, TX
Around here, there is a 320A option. It'd basically allow you to keep your 200A panel as-is and add a 2nd panel. I did not calculate your electrical load...
 
To avoid these ads, REGISTER NOW!

jbwilkins

Well-known member
Joined
Mar 16, 2016
Messages
310
Location
Nashville Tn
What NEC version is Phoenix on?? The most recent revision (2014) requires arch-fault almost everywhere (none were required in 2000), which the breakers are expensive.....His quote could be including replacing all your standard breakers with Arc Fault on the home. He may be required to by code since it's a 'new' service......
 

oldgoaly

Well-known member
Joined
Apr 3, 2006
Messages
395
Location
Shiloh, Il
We live on a farm, had the electrical updated and upgraded to 400 amp, 500 wire. 2-200 amp boxes, new meter box, weather head, same old meter and power lines from the pole. Have to check with your power company, they don't charge for it, but the guy they send may not have clue! I had a electrician here, when the guy got out of the truck, I looked at him. His wife got him the job at the power company, he has never pulled a wire or bent conduit. After the electrician threw his arms up came back in, he says you know that guy? "nope" just looked at his hands, he is a pencil pusher! I knew all the power companies service guys. But supervisors and engineers are a joke! Worth spending the money to do it right!
 

FTG-05

Well-known member
Joined
Oct 11, 2012
Messages
1,541
Location
TN
I tried to get a second meter but county wont let you have 2 meters on my lot so I'm stuck doing it this way. If I could get a second meter would save me close to 5 grand.

Usually 2 sometime 3 guys working at once.

Why not a common meter for both?

My house uses a 200 amp panel. Power comes off the power pole with it's transformer. Meter used to be on the outside of the garage wall.

When my shop was added in 2006, they took a separate power line from the pole direct to the shop. They then installed a meter for both the house and the shop on the power pole and deactivated the house meter.

200 amp service panel in the shop. I'm currently only using about a third of them right now.

In the pic below, you can see my power pole between my house and shop in the background. What you can't see: Two separate power lines, one to each building and the meter near the base of the pole. You can just barely see the transformer.

Good luck.


VOOEqhK.jpg
 

gregs

Well-known member
Joined
Mar 16, 2007
Messages
1,602
I did something similar about 10 years ago. Had a standard 200a overhead service to the power meter on the side of the house but wanted 2-200a services (1-house 1-new shop). Worked it out with the poco to go underground with a pad mounted transformer. They supplied a new 400a meter base for $20. I built a new 400a distribution panel for the side of the house. All it was is the new 400a meter base with a separate 200a disconnect mounted on each side. I removed the existing 200a meter base and replaced it with the panel I built. I did have to rewire the existing house panel so that the grounds and neutrals where separated back to the disconnect, but that was about it. Then I had the new connection point to run to the shop.
 

Swiftlegend

Active member
Joined
Mar 1, 2013
Messages
26
Like post #20 said. I just installed 200amp at an outbuilding(soon will start my thread here) and ran power from pole to it underground. Took meter off house , and the put pedestal out at pad by transformer pad. IT is a rare thing apparently and even PoCo guys were all confused, I even took out a permit when I didn't need one which was a mess in itself because it was an existing structure.

So yeah, go that route. I "could" later do to meters at pedestal if I wanted to meter building as a business in my area supposedly.
 

slow

Well-known member
Joined
Feb 26, 2006
Messages
2,596
Location
near Orlando
I did something similar about 10 years ago. Had a standard 200a overhead service to the power meter on the side of the house but wanted 2-200a services (1-house 1-new shop). Worked it out with the poco to go underground with a pad mounted transformer. They supplied a new 400a meter base for $20. I built a new 400a distribution panel for the side of the house. All it was is the new 400a meter base with a separate 200a disconnect mounted on each side. I removed the existing 200a meter base and replaced it with the panel I built. I did have to rewire the existing house panel so that the grounds and neutrals where separated back to the disconnect, but that was about it. Then I had the new connection point to run to the shop.

That's exactly how I would do it if possible, but do a generator manual transfer switch at the 200 or 400 amp dosconnect depending on possible future needs.
 
OP
T

TTMotorsports

Well-known member
Joined
Jan 8, 2019
Messages
1,107
Location
Lucerne Valley, CA

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,031
Location
Modesto, CA
Ok so going to just run 125 amp to the shop now as load calculators show that's all I could use.

Now what's the difference between these breakers. 4 pole vs 2 pole. And can I just connect the neutral to neutral bar in existing panel and other end to new panel?

https://www.homedepot.com/p/Murray-...GowL-KJjoaIDDjPCawR-Zwqhr-oXRLdEaAvoXEALw_wcB

https://www.homedepot.com/p/Murray-125-Amp-Double-Pole-Type-MP-T-Circuit-Breaker-MP2125P/203512572

The first breaker is a replacement for the factory main that would come in a meter main combo panel.

go with the second breaker.
 

12husky

Well-known member
Joined
Feb 23, 2014
Messages
91
I upgraded from 200 amp to 380 amps to run 200 out to my shop. The power company said the under ground wire to my house was fine and upgraded my meter to a 380 amp with 2 outputs. We put two 200 amp disconnects on the back of the house. One goes to the new shop and the other goes to the house panel. We didn’t have to touch anything on the house panel: just take the wire that previously went from it to the meter and move it to the disconnect instead.


Sent from my iPhone using Tapatalk
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,031
Location
Modesto, CA
I upgraded from 200 amp to 380 amps to run 200 out to my shop. The power company said the under ground wire to my house was fine and upgraded my meter to a 380 amp with 2 outputs. We put two 200 amp disconnects on the back of the house. One goes to the new shop and the other goes to the house panel. We didn’t have to touch anything on the house panel: just take the wire that previously went from it to the meter and move it to the disconnect instead.


Sent from my iPhone using Tapatalk

there isnt 380a service. Its 400/320a.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,763
What NEC version is Phoenix on?? The most recent revision (2014) requires arch-fault almost everywhere (none were required in 2000), which the breakers are expensive.....His quote could be including replacing all your standard breakers with Arc Fault on the home. He may be required to by code since it's a 'new' service......

The NEC does not require AFCI's (snake oil) just because of a service change. There are things that can trigger AFCI requirements but a simple service change does not.

When you want to know what NEC edition a state is on, try this link.

https://mikeholt.com/technical-nec-menu.php

But in the case of Arizona they do not adopt a statewide code. Each municipality is free to adopt and amend the NEC.
 

gregs

Well-known member
Joined
Mar 16, 2007
Messages
1,602
I had to separate the grounds and neutrals back to the new disconnect. Code required them to be separated at the first disconnect / break for potential issues. It wasnt overly difficult, just took good planning and communication with the poco and county. The actual change over took me a day with the poco disconnecting service in the morning and the county inspecting it in the afternoon. While I was doing my work the poco set the new transformer and pulled cable.
 