Modine Hot Dawg won't fire up
Beeffajitas
Southern NH
So, going through the pre-cold rituals. Had propane delivered today. Tried to fire up the Modine in the shop. It's not making all the relay/solenoid clicking that it usually does. In the past I have had to cycle the starting sequence to purge air from the propane line, but with no clicking I don't think I've even got to that point. Distribution blower fan will turn on.
Things I've tested so far..
- transformer is producing 24V to the board
- Honeywell control valve LED does light green (it's getting 24V) (no blinking)
- 120V is NOT going to the exhaust fan, after call for heat
Any thoughts?
Specracer
Have you killed power to the unit (causing a reboot)? And there are not any fault codes blinking?
D45
NW INDIANA
Try checking the blade fuse inside, my friend had one bad from factory
$2 later it worked perfectly
Check for fault codes
What size unit?
Beeffajitas
Southern NH
It's a HD-45AH
I'm not seeing a very complicated control board. I think all the controls happen inside the Honeywell control valve. It's P/N 5H76383.
Looks like this:
https://controlscentral.com/eCatalog/tabid/63/Category/Heating-Gas-Control-Valves/ProductID/506368/PageIndex/14/ViewType/2/Default.aspx
There's one LED on the Honeywell, no blinking. There is a sticker in the unit to identify codes.
This is the only board I see:
https://www.qcsupply.com/20886-modine-terminal-board-with-time-delay-relay.html
I did shut power off a couple of times.
I'm thinking this board is supposed to send a signal to the control valve to start the sequence, but I'm not sure how to test that.
JeepJohn62
Alaska
Any thoughts?
Is the unit firing up?, but the fan will not function, so it shuts off? I might be able to help. Just fixed mine this week.
Sent from my SM-A102U using The Garage Journal mobile app